You either have a bad fan relay or a bad tstat. Remove the t stat from the wall (as long as its not mercury), just the cover plate and see if the fan shuts off. If so, bad t stat. If not, bad relay
A heat pump on the optimal heating day (about 50 degrees ambient) will only deliver approximately 85 degree air as compared to 125 degree air from a fossil fueled furnace. The colder the outdoor air is the less heat there is available to be transferred to the living space. At 30 degrees, the heat transfer capability is getting close to negligible meaning the run cycles will be approaching continuous and eventually as the heat pump along cannot maintain setpoint, the outdoor stat or stats will bring on auxilliary heat in the air handler.
If your ambient temp is below the 'balance point' of the heat pump, the house temp will drop a little lower and most times energize the heat strips through the outdoor t-stat. Your outdoor stat could be set too low for the heat pump to carry the structure all the way down to the balance point so when you turn it off and back on, the lower indoor temp automatically brings on the heat pump plus a heat strip or two, thus the warmer air. Second stage on the stat satisfies due to the heat strip, drops them out of the circuit and the heat pump is left running on first stage heat delivering the perceived cold air.
Your outdoor stat could also be not functioning correctly and not allowing the heaters to come on until the system is turned back on reestablishing the two stage call for heat.
Tons of possibilities and not enough room to list....
The "R" terminal on the back of the stat should be 24 volt supply to the stat. For a heat pump, when the stat calls for heat, the "W" terminal goes hot (24 V) and should actuate the reversing valve and start the outside unit for heat. when the stat calls for cooling, The "Y" terminal goes hot and starts the outside unit without the reversing valve. The heat strip is used to temper the air while the outside coil is defrosting when in heating. You need an OHM meter to test for a short in the heat strip. A lot of installers are wiring it to heat all the time when in the heating mode if the heat output is too low on really cold days. Try jumping "R" to "Y" and the outside unit should start. Disconnect the heat strip from power while testing. This is really brief, its a big subject. Good luck.
Your coils on the outside unit may need cleaning.When they get dirty, air cannot flow through them to remove heat from the refrigerant. When this happens pressure increases until it trips a safety and shuts the unit down. It won't run again until the pressure drops to a safe level. Also check your drain line..Make sure it's dripping.If not it's clogged and that will trip the safety switch not allowing water to back up
Dont know what equipment you have but yes of course there is a fix. Turn power off to air handler. cycle power to heat pump and be sure the board is configured properly to match your outdoor unit. Then turn power on to indoor unit and likely go through system setup once again. provide model numbers of all communicating components if more problems.
The furnace has a fault check the furnace compartment for a flash code and check it with the code chart on the furnace door. Turning the power off to the furnace and turning it back on will reset the fault but it may happen again till you verify the fault and fix it.
There may be pins on the circuit board inside the air handler that you can adjust. First turn off the breaker then look inside at the board. They may say 30-45-60-90 etc. Put the pin on a lower number. Do you have a digital or programmable T-stat? There may be a setting in the T-stat setup program that allows for blower delay also. consult you installation instructions. Last if the blower isn't turning off at all then the relay on the circuit board is stuck closed and should be replaced.
It sounds like you have the fan turned on. If you go to the stat, you should see an auto button, or switch for the fan. If you just switch it to auto, the fan will stop, and only start when the unit calls for it, hope that helps