Kitchen Appliances - Others Logo
Posted on Aug 22, 2008
120 volt folorescent light sign with a photocell
Coming from power source is a black,white, green wire coming from the light is a white, red, green wire coming from the photo is a red, black ,white wire . i need help uncrossing these wires, keep tripping the breaker
Anonymous
Level 1:
  • Contributor 38 Answers
  • Posted on Aug 22, 2008
Anonymous
Contributor
Level 1:
Answers
38
Questions
Helped
28736
Points
55
Based on what you've written, it should be black to red, white to white, and green to green. If you still have trouble, post a picture so I can have a better look of this photo-cell.
Hope this helps,
Kermit
I have a new heater with diferant terminals from the old one so not sure how to atach the wires
There is no need to rewire the internal of the heater!
Just bring in the electrical supply to the heater, it can be either 120 or 240 volts.
If the heater you have is like the picture associated with your post, then all then have to do is change the supplied plug from 240 to 120. It comes pre set for 240. That plug is inside the cabinet.
If any other brand, then you need to change the wires at the transformer of the heater. All heaters need to be supplied with primary voltage: 120 or 240. Then the control system is supplied with secondary voltage out of the transformer. The secondary voltage is no more than 28 volts. and these wires are normally colored as blue or yellow.
Secondary power is already wired within the heater. NO need to change where they are. You will only need to deal with the Primary wiring.
There are many varieties of transformers that transform high primary voltage to a low secondary voltage of 28 volts. and these transformers have many wires: primary & secondary.
I will try to make this easy to understand.
If you have a Gas Heater Transformer with these colors:
  • Red
  • Black
  • White
  • Green
Or...
  • Red
  • White with Red Stripe
  • Black
  • White with Black Stripe
  • Green
These are Dual Voltage Transformers, you can bring in either 120 Volts or 240 Volts
If you bring in only 120 Volts...
1st example:
The Red wire will not be used! Hot wire to the Black, and the Neutral/Common, to the white wire. Green to ground.
2nd example:
Connect the Red wire with the White with Red Stripe together and connect these to the incoming Neutral/Common wire, normally White.
Connect the Black Wire with the White with Black Stripe to your incoming Hot Wire, which is normally Black.
Green to ground
If you bring in 240 Volts...
1st example.
1 Hot wire to the Red, the Other Hot wire to the Black, and White wire is not used. Green to ground
2nd Example:
Wire nut the two Striped wires together. then one incoming Hot wire to the Black, the other incoming Hot wire to Red.
Green to ground
Or This is only a Low voltage - 120 Volts Only
  • Black
  • White
  • Green
Or either any of these combinations...
  • 2 Blacks w/Green
  • 2 Reds w/Green
  • 1 Black, 1 Red w/green
This type will only be a high voltage, 240 volts only
Picture below is what a transformer looks like and it is where your incoming supply wires go. The smaller leads with the spade connections will go to a specific location & is the 'Secondary" .
Good Luck
Mar 14, 2015 • Pool & Spa
tip
How to wire Intermatic T103 and T104 timers
VERY IMPORTANT: Understand that in US residential wiring the WHITE wire is _NOT_ ALWAYS_ the neutral wire. Additionally, prior to 1999 the National Electric Code (NEC) did not require that these white wires be re-identified with black tape or similar means when used for purposes other than neutral. The white wire is sometimes used as a hot, especially when wiring Intermatic T103 and T104 timers.
Also understand that the WHITE neutral wire and the bare (or green) equipment grounding wire are connected together ONLY at the main electric power panel and must _never_be connected together _again_. Once those two wires leave the main electric panel, the WHITE neutral wire must _always_ remain insulated from the bare or green equipment grounding wire. This is very important for safety considerations.
If your wiring is very old and does not have a bare equipment grounding conductor, you _must_ protect the circuit with a GFCI (Ground Fault Circuit Interupter). GFCI wiring is not difficult but is beyond the scope of this post.
DETERMINE WHAT CABLE YOU HAVE:
Usually one will find one of the three following scenarios for the incoming supply cables when wiring a T103 or T104 Intermatic timer:
1...A 120 volt cable with 3 wires: black, white, and bare. The black is LINE (hot), white is neutral and bare is equipment grounding. Black to white is 120 volts. This scenario can be used with the T103, but not the T104.
2...A 240 volt cable with 3 wires: black, white, and bare. The black is LINE(hot), the WHITE is LINE (HOT), and the bare is equipment grounding. Black to white is 240 volts. This scenario is used with the T104 ONLY.
3...A 120/240 volt cable with 4 wires: Black, red, white, and bare. The black and red are (LINE) hot, white is neutral and bare is equipment grounding. Black to red is 240 volts. Black to white is 120 volts. Red to white is 120 volts. This scenario can be used with either the T103 or the T104.
The only difference between the T103 and the T104 is the timer motor voltage rating. The T103 uses a 120 volt timer motor and the T104 uses a 240 volt timer motor. The T103 timer motor is connected to terminal "A" and terminal #3 during manufacturing. The T104 timer motor is connected to terminal #1 and terminal 3# at the factory.
Also, when connecting the bare or green wires to the "GR" terminal, it is best to wirenut the wires together with a pigtail, then connect the pigtail to the "GR" (GRound) terminal, WHICH IS THE GREEN SCREW ON THE LOWER PART OF THE CASE.
WIRING THE TIMER:
The wiring diagram for the T103 is here:
http://www.progressive-growth.com/wiring/T103.pdf
___________________________________________________________________
WIRING THE T103 USING AN INCOMING 120/240 VOLT CABLE WITH 4 WIRES (scenario #3):
Incoming (LINE) wires from 240 volt circuit breaker:
Connect the black (LINE)(hot) wire to terminal #1. Connect the red (LINE) (hot) wire to terminal #3. Connect the white (neutral in this case) wire to terminal "A".
Connect the bare equipment grounding wire to the "GR" terminal, which is the green screw on the case.
Outgoing wires to 240 volt load:
Connect one (hot) wire to terminal #2 and the other (hot) wire to terminal #4. The bare or green wire goes to the "GR" terminal.
WIRING THE T103 USING AN INCOMING _120_ VOLT CABLE WITH 3 WIRES (scenario #1):
Incoming wires from 120 volt breaker or source:
Black (LINE) to terminal #3. White (neutral) to terminal "A". Bare to the "GR" terminal.
Terminals #1 and #2 are NOT used in this case.
Outgoing wires to 120 volt load(s):
Black(hot) to terminal #4. White(neutral) to terminal "A". Bare to the "GR" terminal.
The wiring diagram for the T104 is here:
http://www.progressive-growth.com/wiring/T104.pdf
WIRING THE T104 USING AN INCOMING 240 VOLT CABLE WITH 3 WIRES (scenario #2):
Incoming (LINE) wires from breaker:
Connect the black (LINE) (hot) wire to terminal #1. Connect the white (LINE) (hot in this case) to terminal #3. Connect the bare wire to the "GR" terminal.
The "A" terminal is _NOT_ used.
Outgoing wires to load:
Connect one (hot) wire to terminal #2 and the other (hot) wire to terminal #4. Connect the bare or green wire to terminal "GR".
WIRING THE T104 USING AN INCOMING 240 VOLT CABLE WITH 4 WIRES:
Same as above, except the white wire is not used. Just tape or wirenut it off.
Comment by gotgeek2, posted on Jan 08, 2010ckuzkuz, I'm a licensed master electrician in 2 states with 30 years in the trade. I've installed a lot of Intermatic timers over the years. I wrote this tip because I saw that a lot of folks were having problems wiring them.
on Mar 07, 2010 • Garden
tip
These instructions are for USA residential wiring only.
WIRING THE TIMER:
3helpful
I would like a wiring diagram for an outdoor receptacle controlled by a photocell. Photo cell has 1 each black wire, red wire and white wire.
If I understand correctly, you want to add a photocell to existing receptacle.
Start by looking at receptacle:
Receptacle has 3 different colored screws.
Green screw for bare ground wire
Brass screws with black Hot wire connected.
Silver screws with white Neutral wire.
How to wire photocell to receptacle.
Remove black Hot wire off of brass screw and connect black wire to photocell-black wire. This will power the photocell switch.
Connect photocell-red wire to brass screw on receptacle. This will turn receptacle on-off whenever photocell switch turns on-off.
Connect photocell-white wire to silver screw, and this will complete circuit to photocell switch so the switch is able to operate.
All white Neutral wires are connected to silver screws.
Add a comment for more free help.
Also take advantage of fixya phone service.
For a price, expert speaks with you over phone while you work on circuit or any do-it-yourself project.
Fixya is always less expensive than a service call.
1helpful
Wireing diagram do not no were thay go three wires
K4221C photo cell page at Intermatic:
http://www.intermatic.com/products/photo%20controls/commercial%20%20industrial/stem%20%20swivel%20mount%20-%20thermal%20type.aspx
Photocell has black, white and red wires on photocell.
Black goes to Hot from breaker.
White goes to Neutral from breaker box
Red goes to Load (light)
Electricians don't guess, they test.
You should have one wire coming from breaker box, and another set of wires going to light.
Separate wires for testing.
Since you are outdoors, stand on dry boards and tape tester leads to wood sticks to keep hands away from power.
Turn power ON
Test each wire to bare ground wire.
Tester lights up on hot wire. This wire should be black.
Hot wire connects to photocell black
Hot is identified.
Test Hot wire to all wires except bare ground.
Tester lights up on neutral. This wire should be white.
Neutral wire connects to photocell white
Now the other cable goes to Load. This cable has a black and white wire.
Connect photocell red to black Load wire
Connect white Load wire to Neutral, along with photocell white.
Ground wires are twisted together.
For a price, expert speaks with you over phone while you work on any do-it-yourself project.
I have a dusk to dawn pole light trips the breaker when the photcel is wired in. The wires going to the photocel shows a test light lit with black to either red or white. Can this be a short or simply a...
first when installing a photocell there should be a black wire a red wire and a white wire, black goes to power coming from house, red is connected to black wire in post to light, white goes to the neutral wire coming from home, if you have any other wires you wired it wrong
Jun 19, 2010 • Solar Home
13helpful
5answers
Photoelectric Control (Photo Eye), dawn to dusk, install
Connectthe SUPPLY wire (Black) to the Photoelectric Black. ALL of the white wires - to lights and from supply and on PE - connect together
Redfrom PE goes to all light fixture black lines
Wiring hook up in the back for whirpool dryer
assuming you are referring to the power hookup,there is no positive negative, (it's not D.C.) red and black are the hot lines(240 volt between them) white is neutral and green is equipment ground.voltage reading should be 120 volts from red or black to white as well as green, 240 volts from red to black, 0 volts from white to green
Top Kitchen Appliances - Others Experts
john h
Are you a Kitchen Appliances - Other Expert? Answer questions, earn points and help others