The red lick is blinking 3 times. The blower fan

The red lick is blinking 3 times. The blower fan will not kick on. Can't get furnace to kick on. Just cleaned everything. Been having problems with central air too. Been a build up of ice around the pipes and seems like we have to let it thaw before we can get the system running again.

1 Answer

Anonymous

Level 2:

An expert who has achieved level 2 by getting 100 points

MVP:

An expert that got 5 achievements.

Governor:

An expert whose answer got voted for 20 times.

Hot-Shot:

An expert who has answered 20 questions.

  • Expert 80 Answers
  • Posted on Oct 07, 2009
Anonymous
Expert
Level 2:

An expert who has achieved level 2 by getting 100 points

MVP:

An expert that got 5 achievements.

Governor:

An expert whose answer got voted for 20 times.

Hot-Shot:

An expert who has answered 20 questions.

Joined: Oct 03, 2009
Answers
80
Questions
0
Helped
36679
Points
149

These are two unrelated problems. The flash code you are getting is an induced draft problem. The pressure switch is not proving airflow. Make sure that the inducer motor (the motor in the middle of the top door) is running when calling for heat. If so, make sure that the flue in not obstructed. Bird nests, rodents, ice, and snow can plug the flue to the point that not enough air is being moved to allow for ignition.

As for the "ice around the pipes" can be a couple of issues. Check to make sure that your filter has been replaced. If the indoor blower cannot move enough air, the coil will freeze. If that is not dirty, then you most likely have a refrigerant leak and need to have it recharged.

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

My electric furnace constantly runs.. no cold or hot air blowing through the vents.. red LED light blinks 4 times saying limit switch open.. how do I fix the problem?

You'll need to replace the fan limit switch. This little switch is what tells your blower when to kick on and when to shut off. It's stuck open.
1helpful
2answers

1999 Goodman down draft natural gas furnace. It starts as normal, the burners fire and it warms up, but the blower doesn't start, after a couple minutes the burners shut down and the blower immediently...

IT SOUNDS LIKE THE FAN CYCLE RELAY OR BOARD IS NOT MAKING THE FAN COME ON WHEN IT SHOULD THE BURNER SHUTS OFF PROBABLY BECAUSE IT REACHES THE HIGH LIMIT.
0helpful
1answer

Goodman furnace GMP075-3 The thermostat was in the off position over night and sometime during the night, the induced blower and blower motor came on. The trouble light on board blinks 5 times. I checked...

Need your model # to check the codes but, this coming back on after turning the t-stat off is rare. You may have been in a lockout and the furnace re-started. Some furnaces try to start three times , then lock out. Time out, then re-start. The codes should be on your furnace blower door. Write back with this info and i could help.
0helpful
1answer

Have a gmp125-4 furance blower runs all the time checked themostat wires error code 1 blink then 2 then 3 then 5 furance works if you turn power off turn back on when heat kickes off blower comes on gives...

Sounds like limit switch issue. Furnace heats up, high temp limit switch opens, fan will stay on. GMP model is older and do not have the codes.
May be over fired, have airflow problem, to cause the limit to open.
Next time before shutting off power, try to find the limit, it has two wires that connect to a 1.5 x 2 inch card mount to the furnace fire wall. tap on it and see if the blower stops. If so replace the limit.
0helpful
1answer

My furnace the burners light and come on and heat up the unit. But the fan never kicks on and blows. The fan itself works because I can turn it on manually so I know it's not that. The trouble code...

The manual selection on the thermostat bypasses the fan relay. When in Auto, the fan relay turns on the blower. You are probably looking at replacing the circuit board. As far as the three blinks, on the reverse side of the front panel there is a wiring diagram and error code chart. It will give you a starting point where to look for a problem. The three blinks could indicate an open limit because the blower is not operating. Keep the blower on manual and let the furnace run normally until you can figure out what the problem is.
0helpful
1answer

The red light won't stay solid and blinks. the furnace won't cycle more than once or twice before it just won't go and it is not warming up to what the thermostat is set on. we have to flip the actual...

if it is three blinks then it should be the pressure switch, you can blow through the tube(both ways) and it should work. here is a thread I found:

http://en.allexperts.com/q/Heating-Air-Conditioning-696/furnace-working-3.htm

here is a best site:

http://arnoldservice.com/Troubleshooting_Heating_Problems.htm

hopefully this will help you out, Good Luck Tim
0helpful
1answer

My furnace blower kicks on and the flame lights for about 5 seconds then kicks off. I replaced the igniter recently. The service trouble light blinks continuously.

Your furnace may be kicking out on high limit. Its possible your circ. or blower fan needs to be cleaned. If you don't get enough air moving across you heat exchanger it will kick off on high limit.
0helpful
1answer

Furnace kicks off and right back on

If this is a newer furnace, an indication of an error is that the room air blower stays on. Get in front of the furnace and see if you can see any blinking lights. Try not to remove any panels as you will erase any error codes. There should ba a small viewing port that you can look through. Once you count the blinks, look at the wiring diagram for the error code chart. It may give you a starting point. Can you tell us a make and model number of the system?
0helpful
2answers
0helpful
1answer

I have a Goodman furnace GMPN080-4 REV B. I had the blower motor take a dive, so I replaced it with another equivalent 115 VAC 60 Hz 1/2 HP motor. I replaced the 10.0 MFD +10% -5% capacitor with a 7.5 MFD...

limit switch is on the heat exchanger black plastic about 1and1/2 in. by 2 in. with 2 wires going to it , it has 2 screws holding it in take it out and check it with an ohm meter and you should not have a reading if it is good
Not finding what you are looking for?

202 views

Ask a Question

Usually answered in minutes!

Top Goodman Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

Mike Cairns
Mike Cairns

Level 3 Expert

3054 Answers

Jay Finke
Jay Finke

Level 3 Expert

1397 Answers

Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...