Oil trap for 2 ton split unit

2 TON SPLT UNIT MITSUBISHI MODEL NO MU24AV
THAILAND /
Building hight is about 16 meters, condensing unit at roof,
in installation manual hight is 15 metes with 30 meters pipe run and pipe size is 5/8", and it is not mention that there will be any oil retrun problem
1.Do we need to fix a p oil trap at riser or no need?
2. Do we need to change suction line size or keep same size?
3 if same size of piping and with out oil trap will system works without any problem?

2 Answers

Anonymous

Level 1:

An expert who has achieved level 1.

  • Contributor 1 Answer
  • Posted on Jul 26, 2008
Anonymous
Contributor
Level 1:

An expert who has achieved level 1.

Joined: Jul 26, 2008
Answers
1
Questions
0
Helped
838
Points
1

After installing the system would I advice to measure pressures. By the lenght of pipes and hight difference of the units will there be a pressure drop. Be aware if more pipe lenght as the original is used, oil should be added to the system (oil is sticking in the pipes, the more lenght and traps, the more oil will be in the pipes instead of in the compressor).

Anonymous

Level 2:

An expert who has achieved level 2 by getting 100 points

MVP:

An expert that got 5 achievements.

Governor:

An expert whose answer got voted for 20 times.

Scholar:

An expert who has written 20 answers of more than 400 characters.

  • Expert 104 Answers
  • Posted on Jun 15, 2008
Anonymous
Expert
Level 2:

An expert who has achieved level 2 by getting 100 points

MVP:

An expert that got 5 achievements.

Governor:

An expert whose answer got voted for 20 times.

Scholar:

An expert who has written 20 answers of more than 400 characters.

Joined: Jun 12, 2008
Answers
104
Questions
0
Helped
43225
Points
177

Pipe size is okay, not that I know any better than the manufacturer, but I would recommend at least two and possibly even three oil traps in the vapor line on the way back up.

Ad

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

NEED TO KNOW THE TONNAGE ON THIS UNIT

2 1/2 ton. home is about 1200-1400 square feet ?
0helpful
1answer

Purchased Rheem 4 ton 16 seer AC installer just left

Ask your installing company for the AHRI number. If installed with a
matching furnace and coil as listed in the certification then you will get 16 seer rating. If they installed something different than what is listed in the certificate then demand all parts listed or a refund.
0helpful
1answer

Aircondition builds ice on coil

Either lack of refrigerant, stopped up metering device or capillary tube/s, or lack of air flow (due to bad blower motor, or dirty indoor coil) Good luck.
3helpful
1answer

I have a Ruud Model # UACC-036JAS. Any idea on

Hi, yes the number you are showing me 036 indicates its a 3 ton unit. For every ton of cooling, you will have 12,000 btu's of cooling. 36 divided by 12=3 ton unit. Its showing me also its a Ruud Handler 2.0 ton which would be a Model# UACC-024JAS? If your mobel number is the one you gave me, UACC-036JAS, this is a 3 ton unit, absolutely no questions. I hope I have been of help to you. I am a licensed air conditioning / Refrigeration /Heating Contractor. Let me know if I have been of help.
Sincerely,
Shastalaker7
PS If this is a split system with the indoor air handler and condenser outdoors, both coils must be the same tonnage for it to work for you properly. You can't have a 2 ton indoor evaporator coil with a 3 ton condensing unit.
1helpful
1answer

I just serviced a carrier split dual condensers on the roof and cooling unit in the building, i shut the breaker off on the roof connected to the condensing unit, but it goes on and off what is wrong?

I would look a faulty breaker. If you're replaced the breaker and the problem persists, I'd look for either a floating neutral or open ground. A neutral/ground problem is doesn't have to be near the equipment but closer to the feeder panel.
0helpful
1answer

MR. SLIM

that is not the correct m/n normally it wouls be like pu24 36. for every 1 ton the is 12,ooo btus son a PU 24 IS A 2 TON A 36 IS 3 TON A 42 IS A 3.5 TON ETC
3helpful
2answers

Carrier air handler tonnage?

That is a fairly large difference. It is usually ok to have the inside evap. coil and blower up to 1 ton larger than the outside condenser. That will make the unit slightly more efficient as well as less likely to freeze up on low airflow situations. It is not recommended to install a new condenser on an old evap coil. There has been a lot of changes to the design of the coils in the last little while. For example a 10 year old 2 ton coil may only have 3 cubic feet of volume but a new 2 ton coil may have 4 cubit feet of volume.

There are many factors that may have infulenced the decision on what size condenser to install. Many of which can only be done by visiting the home and doing alot of work, checking the duct sizing bioth supply and return, inspecting the insulation and windows of the home etc. etc. Most of the time that never gets done. You can blame the contractor for not doing a complete check, but at the same time you can blame the customer because many contractors that are that good loose the job to a cheaper bid that did not no any of the research. It is a catch 22 for everyone involved.

There is ALOT more to sizing equipment that many people think, sadly that also includes many HVAC contractors. Way too many people use "rule of thumbs" or flat out "guess".

Sorry for the rant but your queston can only be answered by a good well educated HVAC contractor visiting your home. That type of a contractor is getting hard to find these days in such a price competetive world.
0helpful
1answer

Oil Leak

This would indicate a leak somewhere in the condenser sheet coil. I hate to be the bearer of bad news but you should call a service tech in to fix this problem.
Not finding what you are looking for?

848 views

Ask a Question

Usually answered in minutes!

Top Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

john h

Level 3 Expert

29494 Answers

Brad Brown

Level 3 Expert

19187 Answers

Are you a Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...