HELP!! New install of GMUH75-E3A - Main blower starts immediately on power up/ thermostat turn on. Burner never turns on/ignites. AC power is wired correctly and gas supply is connected. Switch is in the ON position.
Posted by gallingd on
Anonymous
    Scholar:
  • 77 Answers
You need to find out if the problem is in the T-stat, T-stat wire or in the furnace you can do this in a few easy steps
Step 1- Unwire the low voltage from the furnace. Then turn the power back on and see if the blower comes on if it does then the problem is in the furnace and you will need to troubleshoot the furnace (see bottom of page for troubleshooting furnace) if it does not then proceed to step 2
Step 2- Wire the low voltage back up to the furnace (follow the wiring diagram below). And unwire the T-stat, make sure that no wires are touching each other, then turn the power back on to the furnace, if the blower starts then you have a short in the T-stat wire and you will need to pull a new wire. If it does not then proceed to step 3
Step 3- Turn the power back off at the furnace and wire the T-stat back up (follow the wiring diagram below). Turn the T-stat to auto heat 90 if the heat does not start but the blower just runs then you need to replace the T-stat.
http://www.hvac-for-beginners.com/furnace-troubleshooting.html
wiring diagram
Posted on Nov 24, 2010
I have an older Carrier furnace type 58ss. The main burner will not ignite. Operating look ~ thermostat set @ 78 deg, switch furnace on, inducer fan running, pilot light clicks and ignites, inducer still...
power to gas valve ok .. Replace gas valve after checking gas valve coil for continuity/resistance... with valve removed ...and power to valve ... try blowing thru valve from supply side ... stuck valve.... replace...
Nov 01, 2013 | Heating & Cooling
We have a Bradford White Hydrojet Gas Water Heater. Model# MITW5016CX12. The blower comes on and stays on and the the igniter flame does not light. We are afraid that the blower will get too hot when we...
here's what Bradford White lists....
Burner Will Not Ignite
REASON REMEDY Excess primary air Adjust air shutter to reduce air supply -- if supplied No gas Check with utility Dirt in main burner orifice Clean orifice -- check for source of dirt and eliminate Dirt in gas lines Notify utility -- install dirt trap in gas line Venturi clogged Clean -- check for source of trouble and correct Pilot line clogged Clean -- check for source of trouble and correct Main burner line clogged Clean -- check for source of trouble and correct Defective thermocouple lead Replace with new thermocouple lead Defective thermostat Replace Defective magnetic valve Replace entire control Thermostat set too low Turn temperature knob to desired temperature Heater installed in confined space Provide ventilation by use of louvers in wall or door time for a service tech.
Mar 05, 2018 | Fasco Bradford White Hot Water Heater...
No flame
Several steps here to check...
turn power off unit and back on
set thermostat to heat
watch for pilot to ignite..igniter should glow orange or cherry red or spark if its a spark type ignitor
Did you see a pilot light ignite?
If not you probably have a bad igniter.
If pilot lit....in a little bit you hear a click of the gas valve opening..then the main burners will ignite
If you see the pilot and the main burner lights but goes out in a few minutes or immediately you may have an issue of the "high limit" switch tripping.
Is the blower fan turning that blows air out of your vents?
are all your vents open in your house? too many times i see homes with almost all vents shut.
Jan 08, 2011 | Goodman GMS90703BXA Heater
When I turn my furnace on, the purge blower starts as normal, then after 15 seconds the ignitor starts to glow but when the gas valve should turn on it only turns on for a split second and then you can...
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Nov 19, 2009 | Goodman GMS90703BXA Heater
Heater Burner ignites but main blower motor will not turn on.
it sound like the blower motor may be seizing up. try spining the blade by hand to see if it feels free or not. the motor could be trying to turn but can then tripping itself out on overload. (most motors have built in safety overloads which will trip during an overcurrant event. aka too many amps.) you may have to replace blower motor
Mar 16, 2009 | Mr. Heater Natural Gas Garage Heater -...
Ruud silhouette #UHDG-07EAUER won't heat house
Cleaning the flame sensor has nothing to do with blower motor not turning on. You either one of the following problems 1 bad cap for motor. 2 bad motor. 3 bad limit on blower housing or 4 a bad board. You will need a volt meter to check for these problems. Try seeing if the fans runs with unit of and fan switch turned to on. Also does motor hummmm. Is motor cage free ( can check by manually turning) If motor doesnt humm and the cage is free wheeling then you will need to find out if you have power going to the motor. If you find out that you do then you will need to change blower motor. If you do not have power then you will need to check limit with continuity tester on volt meter. If that checks fine only 1 thing can be wrong and that is the board.
Feb 14, 2009 | Ruud UBHC Air Conditioner
Coleman presidential II furnace blower on and off
Sounds like the flame sensor. But it could be the thermostat. Is the furnace standing pilot or electronic spark or hot surface ignition. I would start by checking thermostat. Turn power off to furnace take thermostat off wall and take wires marked r & w and connect them together. Turn power back on if furnace works then change out thermostat.Most eclectronic ignition Furnaces have a flam sensor, You could take flame sensor out and clean it up with steel wool or wire brush. If you need anymore help just reply back .
Jan 17, 2009 | Coleman Propane Forced Air Heater...
Coleman Presidential II mobile home furnace. When burner lights the blower cycles on and off instead of blowing constant through burner cycle.
Is this furnace standing pilot or electronic ignition. If standing pilot i would check furnace filter then the thermastat. To test themostat first turn power off to furnace. Take thermostat off wall and take wires labled R & W and connect them together. If you have electronic ignition I would start with cleaning the flame sensor with steel wool or wire brush.If you have and more questions i will be glad to help.
Carrier Weathermaker SX model 58SX060-CC Blower runs all the time
Remove all power from the furnace, it is likely the brain in the furnace is need of being reset, from the battery replacement, why did you change the battery, was there an indicator telling you to change it?
Many times just removing all the power to the furnace will do the trick with a reset, if not let me know and we will go from there, but it sounds like the main brain is confused or bad, more likely confused, so try the power removed first.
Than let me know [email protected]
Oct 22, 2008 | Carrier XHB123D X/Y Series Heat/Cool Air...
Heating & Cooling Logo
657 people viewed this question
Top Comfort-Aire Heating & Cooling Experts
Marvin
Marvin
Lawrence Oravetz
Arnie Burke
Arnie Burke