Question about Carrier XHB123D X/Y Series Heat/Cool Air Conditioner
I have a Carrier Weathermaker 8000 VS furnace that intermittently has frozen up (the inducer blower stops spinning). Do I need to replace the blower or is there something else that can be done? What is the estimated cost for the part?
Posted by travan_jaspe on
Chandler Ede
  • 1,420 Answers
If you can get to the shaft of the motor, oil it using electric motor oil. If the motor spins freely, you just may need to replace the start capacitor, however if it is binding; you will need to replace the inducer as an assembly.
Posted on Jan 18, 2010
  • trogfield Dec 06, 2010
    does this work?
    old question, for mine, the stupid low resistance resistors destroyed their solder. they heat up alot and are 330 ohms. i just needed to add solder.
Weathermaker 8000 not enough heat
Are the tips of the flame blue? You might need to adjust the air mixture sleeve on the burner.
Feb 05, 2013 | Carrier Weathermaker 8000 Gas Furnace 125k...
Will not ignite. LED Code 31
Could well be the inducer motor Google carrier 31fault code there are 3 video's on this on u tube
Jan 15, 2018 | Carrier Weathermaker 8000 Gas Furnace 125k...
Furnace gas valve is not opening
YOUR FURNACE IS IN LOCKOUT MODE DUE TO A SAFETY FEATURE OF UNIT. USUALLY THE HIGH LIMIT HAS BEEN TRIPPED, OR YOU PRESSURE SWITCH FROM DRAFT INDUCER MOTOR FAULTY OR PLUGGED. IT WILL CONTINUE LOCKOUT MODE UNTIL THIS IS FIXED.
Dec 23, 2012 | Carrier Weathermaker 8000 Gas Furnace 125k...
Flame sensor dirty
Sandpaper lightly scrubbed over the sensor tip to remove any contamination.
Sometimes cleaning is not enough and the sensor must be replaced.
Jan 30, 2010 | Carrier XHB123D X/Y Series Heat/Cool Air...
Weathermaker 8000 furnance flashing code 31 blower comes on for 90 sec .. then shuts off .. then other fan goes on.. don't see any flames or lighting goin on can you help?
31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than five minutes,
inducer shuts off for 15 minutes before retry. Check for: - Excessive wind
- Proper vent sizing - Defective inducer motor
- Low inducer voltage (115VAC) - Defective pressure switch
- Inadequate combustion air supply - Disconnected or obstructed pressure tubing
- Low inlet gas pressure (if LGPS used) - Restricted vent
If it opens during blower on-delay period, blower will come on for the selected blower
off-delay.
33 LIMIT CIRCUIT FAULT - Indicates
Nov 04, 2009 | Carrier XHB123D X/Y Series Heat/Cool Air...
Carrier XHB123D X/Y Series Heat/Cool Air Conditioner Logo
822 people viewed this question
Top Carrier Heating & Cooling Experts
Dennis Boxerman
jdthefixer
Marvin
Marvin
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others