I have a Rheem AC with Heat Pump model RPKA-036JAZ yr1996 outside and a Rheem RCBA-3765GG17 yr2006 inside. Outside fan was not turning on. Noticed my contactor was not making a connection and replaced today. Now outside fan will not turn off at thermostat, even when removed from the wall. Only can shut off at the breaker. Also noticed the thermostat states AUX HEAT and it is only 50% outside right now. Any suggestions will be greatly appreciated!
Let's start out by your statement that the fan would not run, then you changed the contactor, not it won't stop running.
I believe, based on your info, here's what you need to do. Kill power to the unit. The 2 wires bringing power to the outdoor unit should be on the top 2 terminals. The 2 fan wires should be on the bottom 2 terminals. This is providing that the contactor is mounted Vertical. The could be an outside chance that the unit has a short in it and you are getting voltage feedback somewhere.
Take another look.
Thanks for the response. The fan runs even when the contactor is up and not making contact. Tried switching the wires with the same results.
You switched the wires on the contactor.Most residential contactors only have 1 set of contact points. You need to be sure that the wires for the fan are not on the same terminals as the incoming power. They should be on the opposite side so when the contactor is energized, it makes circuit and fan runs. Check this out and let me know if I can be of any help.