Model #GMPN100-4 Goodman furnace. Vent fan continues to run and does not always allow to recycle so no flame.

1 Answer

Anonymous

Level 3:

An expert who has achieved level 3 by getting 1000 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

President:

An expert whose answer got voted for 500 times.

  • Master 1,214 Answers
  • Posted on Dec 17, 2009
Anonymous
Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

President:

An expert whose answer got voted for 500 times.

Joined: Jan 14, 2009
Answers
1214
Questions
0
Helped
566194
Points
3697

The sequence of events for furnace operation is -

Fan purge for 30-45 seconds. During this time, a pressure switch is actuated by the running of the purge fan, proving the control board the purge fan is running.

After purge and purge prove, the hot surface ignition and or spark begins. After a few second delay, the gas valve will open. The control board then monitors for flame prove through another sensor located near the burners. If there is no flame within 3-5 seconds, the gas valve closes. It will repeat this process, usually 3 times, before it shuts the system down, which requires a power down of the system to reset.

I have seen trash get into the hose between the purge blower and the purge switch. But you could be having other problems.

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

Goodman furnace a36-20 fan runs non stop

is green wire from thermostat or from outdoor. retrace and change as needed. If not Goodman has a tech support number you can call while looking at unit.
0helpful
1answer

After one heat cycle, the blower motor keeps running, even after cool down is complete. The furnace will not refire until i turn off the power and wait about 20 minutes for a reset.

your limit switch is opening up, that causes constant fan. Check for flashing codes after flame shuts off and fan continues. Check airflow, filters, lack on return air for possible hi temp limit problems.
0helpful
2answers

Hello. I have a Goodman furnace model no. GDS80453AMA. The furnace indicator light is blinking 3 times, which according to the schematic, is "pressure switch stuck open". Previously I've had the furnace...

The pressure switch requires a negative pressure (vacuum) to close the contacts. It is measuring the pressure in the inducer and indirectly ensure there is good combustion airflow throught the heat exchanger. Check for a small vacuum, in the neighborhood of 1" water column. Usually the vacuum required to close the switch is stamped on the vacuum switch. Check the vent pipe for obstructions and correct size and installation.
If the pressure aka vacuum switch does not close the furnace will not continue with ignition, for safety reasons.
1helpful
1answer

Goodman GS9 propane furnace inducer motor runs continuously

it sounds like the low temp limit switch, the one that cools the furnace down with the burner off and the thermostat open, when it cools to a point the fan stops, the other switch in burner area turns burner off/on, hope this helps
0helpful
1answer

Furnace will not shut off after the setting is reached. have changed thermostat. Temperature reading goes down on thermostat, furnace still runs. Model : Goodman furnace,gmh95/gch9

Check if your thermostat is set on 'o fan' setting.
If it is, trey to set it on 'Auto-fan' instead.
since it seem as if the heating does go off,only the fan may be running continuously.
this is possible if the thermostat is incorrectly set or installed.
good luck.
0helpful
1answer

Will not turn on when set to automatic. when switched to on position no hot air comes out of vent.

If you are talking about the switch on your thermostat, "On" and "Automatic" refer to the fan. In the "Auto" setting, the fan only runs when the furnace is running, in "on" setting, it runs the fan constantly. Your furnace is not firing for some other reason, the on/Auto switch is working properly.
1helpful
1answer

I have outside Goodman-Janitrol furnace and air unit and

two things to try first to get you pointed in the right direction. First disconnect the R or RH wire from the T-Stat. If the furnace turns off (Stops firing w/ fan to turn offabout 90 sec. later) then you more than likely have a bad Thermistat. If it continues to run Pull the R wire from the Furnace circuit board. put door back on furnace if it stops you have a short in the wire. Still Running? Most likely a bad curcuit board. Hope this helps.
1helpful
1answer

Goodman forced air gas furnace not firing

if your power vent moter is not running you should not have have glowing ignitor.Frist the vent moter must close an air prove switch in series with the idnitor .seems you have a stuck air prove switch.Its the one with a hose attached
2helpful
2answers

Goodman a/c blower fan will not shut off

Unhook the thermostat wires on the furnace. If the blower shuts off then your problem is either the thermostat or the thermostat wires. If it contiues to run check you high limit switches next. If all else fails you most likely have a bad blower relay. On most modern furnaces the blower relay is part of the circuit board.
Good luck
0helpful
1answer

Furnace start buts shuts off

It sounds like you have an obstruction in the exhaust vent. Thats why when you bybass the pressure switch it runs ok. Steve
Not finding what you are looking for?

746 views

Ask a Question

Usually answered in minutes!

Top Goodman Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

Mike Cairns
Mike Cairns

Level 3 Expert

3054 Answers

Jay Finke
Jay Finke

Level 3 Expert

1397 Answers

Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...