Question about Electrical Supplies
50 amp breaker will not reset ( no. Snap ) and no run or lights!
Posted by david berg on
seanyboy
    Habit-Forming:
    Scholar:
  • 109 Answers
There’s a Direct short in the cicuit. Check all appliances or recent additions for a short.
Posted on Oct 11, 2020
J Rosado
  • 1,201 Answers
Breakers when bad or going out do that, they won't turn on. Due to dirt, grit, dryness, and build up internaly. Try exercising the breaker, on-off-of-off... and if youre lucky it latches to on but, intermitently, so a replacement is called for.
Posted on Sep 23, 2020
Carl Rock
  • Electrical S... Master
  • 2,624 Answers
Assumong this is a generator... disconnect all loads (all cords). Move breaker to OFF position first then to ON.
Make and model?
Posted on Sep 18, 2020
How do I know if the 50 amp manual reset circuit breaker needs to be reset? there is a small yellow lever with reset printed on the top
If the breaker handle is in the middle position, it needs to be reset. you reset it by pushing it to the OFF position and then to the ON position
Oct 29, 2014 | Bryant 50 Amp 2 Pole Br250 Type Br Ni...
Why does my motor guide 50 trolling motor fuse
It depends on how much current the trolling motor is supposed to draw when set to 5. If it's more than 40 amps, then you need a larger breaker. If it isn't more than 40 amps, then your current 40 amp breaker is weak and needs to be replaced.
May 13, 2014 | MotorGuide Electrical Supplies
5000 watt inverter schematics circuit
If you have (90) 50w lamps = 4500 watts total. Assuming a 120/240 panel, if you put 1/2 on one "side" of the panel and the other 1/2 on the other "side" of the panel, that would be 2250 watts on each half. The generator should be rated *at least* 125% of the load; 4500w x 1.25 = 5625W. Using a 4500W generator on this load will cause it to overheat and shorten its life as it is running at 100% of capacity all the time..
One half of the panel is 120V to neutral, and the other is 120V to neutral - or 240V between both circuit breaker terminals. Ohms law for DC circuits and purely resistive AC circuits says Volts x Amps = Watts; or Watts / Volts = Amps. So, 2250W / 120V = 18.75A on each pole of a 2 pole circuit breaker that feeds the sub panel. A #12 copper wire is rated for 20 amps; but as per National Electrical Code - must be de-rated to 80% of rating which means it is good up to 16 amps maximum. A #10 copper wire is rated for 30 amps, but it too must be derated to 80%, making it good for 24 amps maximum. So, if you are going to feed a sub panel supplying (90) 50watt lamps, you will need to run a #10/3 copper cable from a two pole 30 amp circuit breaker at the generator to a 120/240 volt "main lug only" sub panel rated for at least 30 amps.
Divide your load evenly across the sub panel - (4) 15 amps circuits via (2) two pole 15 amp circuit breakers on each "side" of the panel if you run (2) 14/3 cables out to the lights - or (4) single pole 15 amp circuit breakers if you run (4) 14/2 cables out to the lights. No circuit breaker terminal should have more than 23 lamps that means you have (2) w/ 22 lamps and (2) with 23 lamps. The circuit w/ 23 lamps will draw 23 lamps x 50w = 1150W. 1150W / 120V = 9.6A. The 22 lamp load will be 22 x 50w = 1100W. 110W / 120V = 9.2A. Which is well within the 12A maximum allowed (after derating as required by code) by a #14 copper wire rated for 15A.
Mar 10, 2014 | Electrical Supplies
My lights went out and now the stove doesn't work. How do I reset it.
Check your circuit breaker box for a 40 or 50 amp double breaker flip it off then back on should reset
Nov 05, 2013 | GE Adora JBP77SMSS Stainless Steel Kitchen...
My hot tub has been running perfectly until a few nights ago when the GFCI breaker tripped and now it wont reset
Either you have a ground fault or the GFCI is toasted. Turn off the power to the GFCI, open the box the GFCI is in and disconnect the output wires, close up the box, re-energize, and try to reset it again. This will tell you which problem you have.
Jun 04, 2012 | Cutler Hammer CH250 2 pole 50 amp
I HAVE A 3 PHASE 480V. 50 AMP TED134050 BREAKER WHICH FEEDS A 45 K.W. TRANSFORMER.WHICH TRIPS OCCASIONALLY, NOT OFTEN. IT RESETS O.K. WHAT DO YOU SUGGEST?
I would get an amp metetr on it and see what the load is.... if it is running continually at over 40 amp. then you are overloading it...and need to shed some load...
If it is not then the breaker is going bad and needs to be replaced...
heatman101
Nov 16, 2010 | Electric General Ted134050 50a 480v...
15 amp breaker will not reset with all load off.
They are sensitive little ****, I know they won't work on a florescent fixture, no lights should be on it anyway, but just in case, and the slightest thing wrong, one wire off, one ground undone, it will snap off. And they do go bad, so don't tear the house down to find the trouble when the breaker might be bad. Hook the wire into an existing 15 amp breaker and see if it snaps that off. Then you will know it is not the breaker but something in the wall. Check it out.
Jul 30, 2010 | Eaton ARC FAULT CIRC BREAKER
I have a 25gal 5.5hp Craftsman compressor. it is
The only thing I can think it might be is something else is running on that breaker. But for it to snap a 30 amp, whoa. The 5.5 hp motor probably draws 18 amps on start up if not more. But then runs on 12 or 13, so for it to snap a 30 amp, I don't know. The capacitors, you have 2, could be drawing too much. One thing, what is the 30 amp breaker for? Is it 220 volts? Is your comp 220 volts? Check this stuff out. I'm not sure how you test the capacitor, but don't go messing with it, it holds a charge. Hope this helps.
May 19, 2010 | Craftsman Air Tools & Compressors
Electric Furnace Trips Breakers
it is normal for a breaker that is run right on the edge (50 amp and your furnance to use 45) to get weak after a while . the first thing you should do is change the breaker with the same type and amp rateing . it should take care if it
Jan 16, 2009 | Heating & Cooling
Circuit breaker
I was able to get a replacement 5 amp MB-1 push to reset circuit breaker for my Flowtron LE-900 directly from Snap Action http://snapaction.net/ for no replacement cost and no shipping/handling cost. No one at Snap Action enquired as to what it was for, age, warranty, etc. (their MB1 product description indicates it to have a lifetime guarantee). I just had to mail them the defective original breaker - took about 2 weeks to receive the replacement.
Brett
Oct 16, 2008 | Flowtron LE-900 Leaf-Eater Mulcher
Electrical Supplies Logo
15 people viewed this question
Top Electrical Supplies Experts
Gene Haynes
Marvin
Marvin
Are you an Electrical Supply Expert? Answer questions, earn points and help others