My HVAC system tries to come on. The coil heats up, but then the fan doesn't come on. The only capacitors (two) are outside with the heat pump. The circuit board c800796p01 has a solid green light.

1 Answer

J Rosado

Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

  • Heating & Co... Master 1,202 Answers
  • Posted on Feb 22, 2020
J Rosado
Heating & Co... Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Joined: Oct 13, 2011
Answers
1202
Questions
1
Helped
500541
Points
3432

A capacitor to a motor, outdoor unit has two motors, a fan and compressor motors. Indoor unit has a fan motor and a capacitor for it. Check the wiring diagrams.
Coil heats up? meaning contactor solenoid coil gets power? or, compressor starts up and radiator coil temp. heats up?
of the three motors, two outside and one inside, does one motor not work? if so, will need to check for power at motor leads and capacitor

5 Related Answers

Anonymous

  • 290 Answers
  • Posted on Nov 20, 2007

SOURCE: Ruud heat pump outside unit trips circuit breaker

Check your wiring between the contactor and compressor for a short to ground, or check the compressor windings for short to ground.
With the Tstat off, the contactor should be open so the only way for the compressor to be trying to do anything is if the 110 volts from the unbroken side are traveling through the compressor to ground. Since 110v is not enough to run it, the overload is kicking it out, cooling off, and repeating the cycle. When you kick on the Tstat, the contactor is supplying voltage directly to ground without going through the resistence of the compressor windings and kicking the breaker.
Post back and let me know what you find.

Ad

Anonymous

  • 540 Answers
  • Posted on Aug 23, 2008

SOURCE: KELVINATOR KSR20C

One might think so, YES! look on one of the door panels that you can remove! Thank-you-very-much!

Anonymous

  • 1 Answer
  • Posted on Nov 22, 2008

SOURCE: Heat pump trips circuit breaker

i want to know the size of breaker to use.we are using a 30,30,30,30but it is kicking off.would a 40,40,40,40or higher be better if they sell them.

Anonymous

  • 1515 Answers
  • Posted on Jan 13, 2010

SOURCE: when the unit is in heat mode is the fan on the

Hi, and the outdoor condenser fan should not be on at all in the heat mode unless this is a heat-pump!! So, I can see that this is a 3-ton Carrier split system and I haven't pulled up any information on it, only if I need to. But if the indoor unit runs on natural gas/propane, this would not be a heat-pump and the outdoor fan would run only in the cooling cycle. So, if it is not gas fired it is a heat-pump, and yes the outdoor unit should be up and running all year around. On a heat-pump you will have what is called a reversing valve in the refrigerant system that directs the flow of freon in the right direction for the season you are in. Most all heat-pumps will have a heat strip package installed in unit for emergency and aux. heat if compressor lets say fails. You're thermostat will have on it a selector switch, you will see on it these labels, Aux., emergency heat, auto/on/off/heat/cool. You will know from what I have just went through with you what you have. Forgive me for such a long explanation as I like my customers to understand more about there units in question. I could have just said yes or no and thanks? Doesn't work like that for me. I hope this has helped you out. One thing, If you determine this is a heat-pump and the fan is not on when in heat, you may have lost this condenser fan motor? You say both run caps. were replaced, and normally when you loose a run cap for a motor they will open internally, leak, buldge ect. So if this is taking place, if you can yourself take a look at the run cap. Also, make sure you have 220 volts to condensing unit. If not, check breaker probably a 30 amp double pole to see if it has tripped. You will have a disconnect box at the unit and inside there will also be 2 fuses. If you see only a pull out square connect, the fuses are still there but in behind the cover. If you have power and can hear the compressor come on but fan does not, I am positive you will have A faulty run cap, or faulty motor. Kill power to unit and try and slide a metal coat hanger down to prop or blade to see if it spins freely. If it is hard to turn bearings are froze up. If the capacitor seems to look ok, and the motor does spin free, It still may have open windings. Do these checks I have asked of you on power to the outdoor unit. If all is good, Stand in front of the unit and have someone turn the stat on for what season you are in. Lower or raise temp a ways above or below room temp. You should her the contactor close and compressor will start along with the condenser motor.If compressor starts and motor does not, then I would say it has failed and or cap again. When a motor is replaced, the run cap must always be replaced to!! Please get back to me and keep me posted. I will wait to hear what has happened. Good Luck.
Sincerely,
Shastalaker7

Bill Long

  • 606 Answers
  • Posted on Feb 10, 2010

SOURCE: Gold Star mini split heat pump 24,000

On a heat pump the difference from heat to cool is the reversing valve.
In cooling or heating the Y1 terminal will always be energized, this is the contactor.
Depending on brand the reversing valve will either be energized in Heat or Cool. At the outdoor unit check to see if the reversing valve is getting 24 volts in cool, if not check to see if it is getting 24 volts in heating. The easiest way to check if the reversing valve is shifting, is to feel the big copper tube, (it is not the suction line on a heat pump) this is a refrigerant vapor line. It will be cold in cooling and hot in heating.
Check your thermostat installation instructions and heat pump installation instructions to determine the proper terminal designations for your heat pump and thermostat. There are some brands out there that use the B terminal as common to the 24 volt circuit, so you have to check the wiring and make sure this is not common.
If it is energized in Cool then the Y1 and O terminal will be energized. You will have 24 volts from common usually the C terminal to Y1 and O.
If it’s energized in Heat then the Y1 and B terminal should be energized. You will have 24 volts from common usually the C terminal to Y1 and B.
If you get heat when you’re calling for cooling or vice versa then switch the wire between the B and O terminals.

Ad

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1helpful
2answers

On a Rheem A/C the outside fan runs a few minutes then shuts off?

Question edited for clarity and spelling of 'capacitor'..
Question moved from Televisions to Rheem A/C.

When a start/run capacitor fails, the fan doesn't turn at all, it will just hum.

Try a full reset of the system. Disconnect the power at the breaker for at LEAST 2 hours, or preferably overnight. It resets the logic board and resets all the relays. If that doesn't work, you need an A/C Service Technician.
0helpful
1answer

Trane XR15 not starting. Has power. There is a contact switch that when engaged the system fires up but coil gets cold but not circulating through the air handler. Could it be capacitor related?

So the contactor pulls in outside, the fan and compressor both start?? Then you say the coil gets cold... what coil is getting cold and is this a heat pump and are you trying to cool the house???

If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79

0helpful
2answers

Brand New 2 weeks old 4 ton Trane compressor leaks a lot of water onto pad

If the unit is running in cold weather than there is ice building up on the coils located outside. This is normal in that the unit is running in heat pump mode heating inside and cooling outside, After the unit detects the ice build up it briefly reverses the cycle heating the outside coils melting(defrosting) the ice which you observe as water on the pad.

The video gives you an example of the defrost cycle!
2012 Trane XL15i Heat Pump Defrost Cycle Steam Show
0helpful
1answer

How do I fix my Trane air handler to keep it from turning off about 20 seconds after being commanded to turn on?

Some units require both a start and a run capacitor. It's possible the wrong capacitor was replaced. It's also possible to add a run capacitor to a system to keep the fan running. There is an outside chance the bearings in the fan motor are worn to the point it's time to replace the motor.
1helpful
1answer

To continue from my last Question, to do with HVAC Evaporator/Condenser Cycles, how often should the System go into Heat Standby, Heat Defrost, and Heat Modes? What are Heat Standby and Heat Defrost?

In this type of system (heat pump), the evap and condenser swap functions by means of a reversing valve, according to the mode selected. Evaps throw off cool air, condensers, warm air. In heat mode, the condenser is the indoor coil and it throws off heat from the outside air. Vice versa for the cooling mode. Heat Standby would be whenever the temperature thermistor has reached set point by the user and shuts down the system. Heat defrost is the cycle that reverses refrigerant flow and defrosts the outdoor coil by sending warm refrigerant liquid to that coil. In heat mode, the outdoor coil builds frost and ice on its surface.
0helpful
3answers

American standard heat pump will only work on emergency heat with fan turned on not auto but only works a little while then quits i can turn it off for about 20 min. and back on emergency heat with fan on...

How old is the unit? Heat pumps don't work when it's real cold, you know it's limits. If it's not real cold outside, then it may be low on gas or such and need a service call.
0helpful
1answer

Brand New Heat Pump Compressor fan turns on then off after only seconds.

What is the model number of the outdoor unit?

If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79

0helpful
2answers

I have a Rheem heat pump/air handler; it draws 2.9amps with only the fan running, 13amps when the heat pump is running and 38amps with the heat strips on. My question is why the unit draws that many amps...

Sounds like it must be about a 2.5- 3 ton system. The 13amps has to be the compressor draw -normal. and 38 on the strips- normal. 2.9 fan -normal.

You may want to check your wiring to see where the outside unit gets its power. Theres nothing inside that can draw 13 amps. That almost has to be the compressor power wire.
1helpful
1answer

Amana Cooling Condensing Unit fan stops spinning after 15 mins

Capacitor, dirty condencer coil causing the motor amps to run too high. But most likely worn bearing on blade side of motor causing it to pull to one side causing it to over heat and shut down. Sleve bearings should have no side play.
Not finding what you are looking for?

121 views

Ask a Question

Usually answered in minutes!

Top Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

john h

Level 3 Expert

29494 Answers

Brad Brown

Level 3 Expert

19187 Answers

Are you a Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...