Question about Refrigerators
Sauna trips ground Fault
Gfi trips when power switch is depressed
Posted by [email protected] on
5 Related Answers
Fahr Quad
  • 774 Answers
SOURCE: Ground Fault circuit Breaker trips each time a load is applied
The most likely causes in their order of probability are: 1) water somewhere in the circuit causing the hot wire to ground; 2) a legitimate trip caused by a defect in a device plugged into the circuit; and 3) a defective GFCI breaker. In the first case, wait until it has been dry for about a week and see if it trips. In the second case, make sure there is nothing plugged into the circuit and try resetting. In the third case go ahead and put the regular breaker in, then put a GFCI outlet into the first box downstream from the breaker. If installed according to the directions, that outlet should protect all of the outlets downstream.
Posted on Feb 27, 2009
co7196
Ned C Cook
  • 3433 Answers
SOURCE: GFI on cord trips out.
Probable cause is a single pole gfi opposed to a double pole gfi.
* Do not use a single pole GFCI ON A MULTI WIRE CIRCUIT, IT WILL NUISANCE TRIP IMMEDIATELY
Use a two pole GFCI circuit breaker on such circuits.
Posted on May 20, 2009
protek480
Craig Butler
  • 1730 Answers
SOURCE: swimming pool light on a gfi breaker
It won't take much to trip the GFI. Have you tried to dry the fixture out completely? Use a blow dryer and remove any moisture. Also, remove the light and cap the wires and try it if you can, it might be the wire.
If you need further help, I’m available over the phone at https://www.6ya.com/expert/craig_3fa289bf857b1a3c
Posted on Jul 23, 2009
logcabinsam
  • 7 Answers
SOURCE: ground fault interrupt (GFI)
I have a Whirlpool Model AD$)DSR1 Dehumidifier, with similar issues. When plugged in where it was operating for three years with no problems, it would trip the gfci within 10 minutes. I have it out in the garage right now with all the covers off, and I've had it running on a heavy duty outlet for about a half hour now. The compressor is too hot to touch (ouch!), and the condenser coils are only cool, when they should be quite cold. I am ready to judge that one of two things has happened: Either the compressor is bad, or the refrigerant has leaked out of the system.
Posted on Aug 27, 2009
Anonymous
SOURCE: trips ground fault on plugging into receptacle
I just opened one of the machines with this issue and found that the heating element is entirely ripped open (over the length of the coiled heating element) and the water contaminated with brownish stuff from within the element.
Was wondering if that part can be replaced.
Posted on Nov 30, 2009
Sta-rite heater is about a year old. It worked well up until a week ago. It now trips the gfi breaker. I swapped out the breaker and it trips that too. If I disconnect the exhaust fan, the heater powe
Something in the electrical system supplied by the GFI breaker has a ground fault. The current to ground required to trip a GFI is very little such that dampness on any electrical connection can trip it. This is especially true with motors that have a lot of fine wires in the windings and are open to allow cooling.
Hard water and pool chemicals all are worse than condensation from the air because of their ionic nature.
If the same GFI powers the pump it is what I would suspect first. Your question got cut off before the result of the fan disconnect which if disconnected didn't trip the GFI, is probably the problem. But you should open whatever you can access containing electrical components and make sure everything is dry
Feb 07, 2015 | Sta Rite Pool & Spa
What would cause intermitant pop of ground fault. only thing on the line. ground fault has been replaced
Refrigerators are not recommended to be plugged into a GFI outlet. Depending on the age of the fridge there will be spikes in the current the fridge uses at certain times causing the GFI to trip. A GFI outlet is much more sensitive to current than a non GFI outlet that is tied back to the the regular breaker in the electrical panel. Pleazer Appliance...
May 06, 2014 | Whirlpool Refrigerators
Our 7788F keeps going into a ground fault condition. Need help troubleshooting. John
Ground Fault ???
Troubleshooting Ground Fault
Troubleshooting a ground fault circuit interrupt, or GFI, breaker is pretty straightforward. Troubleshooting the circuit itself can be quite time-consuming.
The GFI breaker is designed with a test button incorporated into the breaker itself.
Pushing the test button should trip the breaker.
On GFI-style breakers the neutral wire going into the house's outlets is connected to the breaker's neutral connector, the white neutral that comes out of the breaker is connected to the neutral bus in the panel, isolating the neutral bus from the neutral wire going into the house.
The test button actually shorts the neutral wire feeding the circuit to the neutral bus in the electrical panel creating a ground fault that should trip the breaker.
It is considered a ground fault because the neutral bus in the main electrical panel is actually connected to the ground bus through the panel's metal casing. What to do if the test button isn't tripping the breaker
Push the test button on the GFI breaker.
The breaker should trip.
If the breaker does not trip, then it may be that the breaker has already tripped and just looks like it's on.
The position of the switch may only move slightly from the on position towards the off position when tripped.
Push the switch on the GFI breaker all of the way toward the off position.
It may take some force to get the breaker to reset.
Turn the breaker back to the on position.
When the breaker has been reset properly you should feel some resistance when pushing the switch back on.
3 Push the test button again and the breaker should trip.
If the breaker still doesn't trip then you should test for power at the screw connections inside of the electrical panel.
Remove the screw that holds the dead front covering the breaker's connections.
Remove the dead front cover.
Test for power with your voltmeter set on AC volts on the highest scale.
For a single pole GFI breaker, touch the black lead from the tester to the silver screw on the GFI breaker and touch the red lead from the tester to the brass screw on the GFI breaker.
You should see 110 volts on the tester. If voltage is seen but the test button won't trip the breaker, then the breaker is bad and should be replaced.
5
Test for power on a two pole breaker by touching the red voltmeter lead to one of screws with a black or red wire connected to it.
Touch the black lead to the other screw with a black or red wire connected to it.
You should read 220 volts or close to it on your voltmeter.
If you read voltage and the test button won't trip, the breaker is bad and needs to be replaced.
What to do if the breaker won't reset and keeps tripping when turned on
6
Unplug everything that is plugged into any of the outlets on the circuit in question.
Try resetting the breaker again by pushing the switch all the way to the off position and then turning it back to the on position.
If it won't reset and trips when the breaker's switch hits the on position, it could be a bad breaker or a problem in the circuit itself.
7
Use your straight-tipped screwdriver to loosen the brass connection screw or screws on the GFI breaker.
Pull the black hot wire, or wires, out of the breaker's connectors.
Loosen the silver screw the white wire is connected to and remove it from the GFI breaker.
8
Push the switch all the way to the off position.
Turn the switch back to the on position.
If the breaker still won't reset, then the problem is the breaker itself and it should be replaced with a new one of the same size, brand and model.
If the breaker resets normally and the test button trips the breaker when pushed, the problem is in the circuit itself and an electrician should be called to find your ground fault.
9
Reconnect the black wire, or wires, to the brass screws on the GFI breaker.
Reconnect the white wire to the silver screw on the GFI breaker.
10
Replace the dead front cover into the breaker panel.
Install the screw or screws that hold the dead front in place.
http://www.hilo-electric.com/blank?pageid=63
Aug 14, 2013 | Computers & Internet
What's youI just wired in my J-300 Jacuzzi hot tub. The GFI trips every time I reset it. I took the GFI out of the equation and the tub runs fine, does not trip the breaker at the main breaker box
#1. DO NOT GET INTO TUB FULL OF WATER WITH A GROUND FAULT.
2. There is a short. You need to get multimeter and start checking each part for current running to ground wire.
3) Power is ON. Connect power without GFCI.
4) Tape tester leads to wood sticks to keep hands away from power.
5) Do not touch anything directly or you will become the ground rod.
6) Ground wire must be present, and bonded back to main panel box.
7) Do not sit or touch directly on cement or bare ground. Do not touch or lean into anything made of metal.
8) Body and parts must be on sheet of plywood, or similar non-conductive dry surface.
9) Test each part with spa, but also test electric line coming from main box.
10) GFCI will also trip with any fault detected on line. So the wire coming to spa may have the fault.
11) Add a new dedicated line from main box to spa.
http://waterheatertimer.org/How-to-wire-GFCI.html
http://waterheatertimer.org/See-inside-main-breaker-box.html
If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7
Oct 02, 2012 | Electrical Supplies
My Sylvania - ground fault 15 amp breaker (32740) is tripping with minutes of reseting. It is for 3 washrooms & hallway & is 30 years old .....does or can it loose its life span? What is the cost...
A circuit breaker can go bad, but usually not in the way that you describe. That's not to say that it can't happen, but just not typical. GTE Sylvania breakers were once popular - I installed quite a few GTE / Sylvania electrical panels in homes in the late 80's. You may have trouble finding replacements; do not put an breaker that "fits" into the panel, unless the breaker is designed for use in the panel you have.
The first thing to do is determine the source of the problem. The breaker will trip, but not indicate if it was the result of a heavy electrical load or a ground fault condition. A 15 amp circuit breaker is designed to carry up to 12 amps continuously. The greater the load, the more quickly it will trip. it may carry a 14.5 amp load for several minutes to an hour before tripping, and a 20 amp load may be carried a second or two. GFI breakers are designed to carry 5 thousandths (.005) of an amp (or 5 milliamps) to ground, or the 12+ amps to neutral before they trip.
The way I would attack the problem is to install a new GFI outlet in front of the old wiring, by "inserting it" between the panel and the other plugs and lights, switches, etc on that circuit. The GFI outlet will provide the same GFI protection that the circuit breaker provided at a fraction of the cost.
Turn off the old GFI breaker, and remove it completely. Install a new, standard (non-GFI) single pole 15 amp circuit breaker in its place. Completely remove from the panel the cable that the old GFI breaker fed. Buy a new electrical outlet box (surface or flush mount as desired) that is large enough and deep enough for a GFI plug and 2 cables (if surface mount, use a 4" square deep box and appropriate cover - or if flush mounting use a deep plastic / fiber single gang box). It will be installed in a place close to the panel, but where the old cable will be able to reach inside. Bring the old cable removed from the panel into the new box. Run a new cable that has the same number and size wires from the panel into the new box, too. Connect the circuit neutral and circuit ground to the neutral and ground bars in the panel (they are probably the same bar) and the hot wire to the circuit breaker. make sure that the circuit breaker is OFF. Twist the two ground wires together and combine an 8 inch length of bare or green insulated wire with them in a wirenut.
Next, wire a new GFI plug in the new box. Connect the green wire from the wirenut to the green terminal of the GFI outlet.
Connect the plug's LINE terminals to the neutral and hot wires in the cable that you ran from the panel to the outlet box.
Now, connect the GFI plug's LOAD terminals to the neutral and hot wires in the cable that you removed from the panel and reinstalled into the new outlet box.
Secure the GFI outlet into the box and install the cover. Cover the electrical panel.
Power up and test. if the GFI trips, there's a ground fault in the circuit. If the circuit breaker trips, the circuit is overloaded.
Jun 13, 2011 | Your One Source Qo Single Pole Ground...
Hi, I have a Kenmore top freezer refrigerator model number 363.79567990. The freezer stopped working and I found out that I had to press the "Reset" button on the outlet while it was unplugged...
It sounds like you've plugged your fridge into a GFI (ground fault interrupter) outlet.
The National Electrical Code (NEC) article 210.8 A (6) says in dwelling units, only those outlets in a kitchen (I'm assuming your fridge is in the kitchen - right?) "where the receptacles are installed to serve the countertop surfaces" must be provide ground fault protection aka "GFI outlet". Unless your town, city, county or state has laws that supersede the NEC, you should have the outlet changed to a standard, grounded outlet to prevent the nuisance tripping you are experiencing when the cooling compressor is trying to start. A refrigerator is not a counter surface appliance, and therefore does not require GFI protection.
The other outlets are fed from this outlet, so when you connect the fridge to another outlet on the circuit, the same GFI plug trips again. When you replace the GFI plug with a "regular one, the GFI plug should be installed in another outlet to provide the GFI protection needed in the kitchen - as described in the NEC above. If you are not familiar with how to do this, please, call a licensed electrician to do this very important job for you. Be safe & be smart.
I hope this helps!
Nov 01, 2010 | Kenmore 55612 / 55614 / 5561 / 655619 Side...
Pump plugged in to grounded receptacle trips the
If by "trips the breaker" you mean the GFI then you are leaking current to ground, GFI's trip when there is an imbalance between the current going to the motor on the HOT side and returning from the motor on the NEUTRAL side, if it is tripping the GFI it is likely the sign of a failing motor.
May 27, 2010 | Little Giant WGP-65-PW 1/8 HP, 1900 GPH...
Gfi installed yesterday on washer 120 v outlet. washer is maytag 3 years old and gfi began tripping during washcycle. can it be washer 3 pronged cord is not grounded at connection in rear of washer?...
The ground not being connected does not tirp thr gfi. The gfi senses the current between the two legs it will trip when the current returning to ground (neutral) exceeds 5mili amps. This is for personal protection. If you have a gfi circuit breaker disconnect the black wire from the breaker, if it does not trip you likely have a groung fault in the washer. If you have a dryer or other metal object that is grounded (Bonded) you may get a shock from it, also standing (barefoot) on a concrete floor may cause the same. ( bonded is a gronded conductor that attaches all metal parts of a electrical curcuit together) a hot lead goes to ground is a dead short and will trip any breaker.
Jul 11, 2009 | Maytag Neptune MAH5500B Front Load Washer
Kenmore 417.40412700 tripping GFI circuit breaker
Unfortunatly washing machines are too sensitive for GFI outlet.only way to fix is too take it off the GFI.
Mar 19, 2009 | Whirlpool Ultimate Care II LSQ9549L Top...
Refrigerators Logo
126 people viewed this question
Top Refrigerators Experts
Marvin
Marvin
john h