Question about Kohler Electrical Supplies
I have a 20RESAL Kohler generator. It starts but will not transfer. I get a comm error message. Where do I start looking to find the problem?
Posted by terryg5201 on
Pieter Vleeshouwers
  • Kohler Master
  • 2,027 Answers
5 Related Answers
Anonymous
  • 77 Answers
SOURCE: ERROR MESSAGES
nthemba- all the error codes you see indicates phone line condition or error at reciving fax's end. For more details you can refer to
http://h10025.www1.hp.com/ewfrf/wc/document?docname=bpu02549&lc=en&dlc=en&cc=us&product=79477&rule=17804&lang=en
Posted on Oct 10, 2008
CarlGehrke
Carl Gehrke
  • 169 Answers
SOURCE: kohler 12kw generator starts but shuts down after 3sec
Your gas pressure is too low and you may not have a large enough supply pipe. You need at least 10 inches of water column with the engine running to operate an LP vapor fueled engine. Because the engine is starving for fuel, its governor opens the throttle to WOT (so it goes to high revs) but there isn't any fuel to make horsepower with so the output voltage falls and the undervoltage alarm trips.
Carl
Posted on Dec 03, 2008
mamicheddy
mamicheddy
  • 79 Answers
SOURCE: Hello, I have a Kohler Marine Generator that says OC on the menu when I try to start it. Any ideas?
OC stands for Over Crank. How long does it take before the genset starts?
Posted on May 07, 2009
Fred Yearian
  • 5603 Answers
SOURCE: kohler confidant 4 generator service manual and wiring diagram
First thing is to check oil level as low oil pressure will shut it down.
Posted on Aug 11, 2009
noman_att246
SOURCE: The monitoring system of our Kohler propane
The monitoring system of our Kohler propane generator has sent a "UU" message. What does this mean as it causes the generator to shut down 10 seconds after starting? Also how can this be corrected?
Posted on Jun 02, 2011
Service manual 20resal
Contact Nixon Power Services in TN they can supply you with one
Oct 11, 2013 | Kohler 20resa 20kw Home Emergency Backup...
We just installed the Kohler 20RESAL in a open air enclosure behind my clients house and when it's running it's incredibly loud. You certainly can't talk to anyone if you are standing next to it and the...
No be careful !!! the muffler is designed to give a certain engine back pressure and emissions. Changing this or piping it out can increase back pressure to dangerous levels. If you build an enclosure make sure the air flow in and out is sufficient and the hot air out does not get sucked back in as cooling air (short cycle) engine damage and fire can result !
Sep 24, 2013 | Kohler 20RESAL - 20kW Home Standby...
First start up
Try disconencting the remote start wires between the transfer switch and the generator, if ot still does it you have a bad control board. If it stops, then check the transfer switch for correct wiring of utility and generator power wires, also check with an ohm meter if the run contacts in the transfer switch are closed, that would indicate loss of sensing, or bad board
Jul 19, 2013 | Kohler Electrical Supplies
Kohler 20resal 100amp transfer switch RXT will not auto start?
Disconnect generator remote start wires in the ATS. Put an ohm meter across the remote start terminals in the ATS and kill utility power, you should here a click in the ATS and the ohm meter should indicate close to zero ohms. If it does then your ATS is fine and the problem is gen control board or wiring between the two. If it does not show that value, then the start relay in the ATS is suspect.
Feb 12, 2013 | Kohler Generator 20kw 20res W/ 200 Amp...
My Generator will not start up
Will it start manually? if so remote ATS issue, if not check battery
Oct 27, 2012 | Kohler 20RESAL - 20kW Home Standby...
My gen starts and runs for 1 min or so then dies restarts then dies again and again. if i start it under load ( turn on air con) it will run for 10 min then die allen
Is there a fault?? All UL listed generators including Kohler are required to lockout on a fault on shut down. This really sounds like a problem with your 2-wire auto start connection between your automatic transfer switch and genset. RDT model automatic transfer switch it is the 2 middle wires on the green connector and terminals 3&4 in the generator. close to run and open to shut down. Any open at any time will cause the unit to shut down. The 12 will shut down instantly upon an open because your 5 minute cool down is built into the transfer switch.
Jun 27, 2011 | Kohler 12 kW Emergency Power System -...
The monitoring system of our Kohler propane generator has sent a "UU" message. What does this mean as it causes the generator to shut down 10 seconds after starting? Also how can this be...
May 28, 2011 | Kohler 12 kW Emergency Power System -...
I have a Kohler 12RESM1 propane generator with oc/uu code
U need to make sure that the relay driving ur auto start stay closed all thru the crank cycle.
Feb 04, 2010 | Kohler 12 kW Emergency Power System -...
Overcrank error message
The 'overcrank' error simply means it tried to start but never actually started. It cranked for an extended period. Check the fuel and starting issues you would normally check to start the engine.
If you need further help, I’m available over the phone at https://www.6ya.com/expert/craig_3fa289bf857b1a3c