Heating & Cooling Logo
Laverne Hooper Posted on Sep 17, 2018
Answered by a Fixya Expert
Trustworthy Expert Solutions
View Our Top Experts
My AC unit has went to emergency heat mode on my thermostat, and I can not get it off. We have not had the heat on at all.
David Ellis Rhea
Level 3:
  • Master 3,462 Answers
  • Posted on Sep 17, 2018
David Ellis Rhea
Master
Level 3:
Answers
3462
Questions
Helped
784893
Points
10903
Try to find the circuit breaker or the fuse box and find the circuit breaker or fuse that controls the AC and flip it off, until you are able to get this repaired.
Most often, when this happens, it is a short circuit that has damaged the controls of the A/C or the thermostat. ( Such as a lightning hit) God bless our efforts.
5 Related Answers
Anonymous
  • 124 Answers
  • Posted on Nov 10, 2008
SOURCE: MY HEAT PUMP SYSTEM WILL NOT WORK IN EMERGENCY MODE
the thermostat sub base has a place to connect a wire usually white to energize the heat strips when you push the stat way hotter than the house temp. that is why the strips come on in normal heat. it also has a terminal that is only energized in emergency heat and it also should have a wire connected to it so that terminal can supply power to the strips when the stat is switched into emerg heat . you can identify the terminal from the wiring diagram and if need be jumper w2 wire over to the aux terminal and it will work. they both go back into the airhandler and power the same strips. w2..................................................................................................w2 in airhandler to strips or w2...jumper to aux......................................................................................................................w2 in airhandler to strips.
Anonymous
  • 710 Answers
  • Posted on Apr 27, 2009
SOURCE: HVAC problem
One thing you can check is the condensation line to see if there are wires going to it. This is the plastic pipe coming out of the indoor unit. If there is a float switch and the condesate line is clogged then it will not allow the a/c to operate. If the line is clogged you can use a WET/DRY vacuum on the end of the pipe which should be next to the outdoor unit. Hope this solves the problem. Good luck. Keep me posted please.
co7196
Ned C Cook
  • 3433 Answers
  • Posted on Jun 02, 2009
SOURCE: Dometic AC that the fan shuts off but the compressor keeps running
call dometic dealer. I hear they have a bad circuit board that is replaced.
Anonymous
  • 534 Answers
  • Posted on Sep 16, 2009
SOURCE: Thermostat will not turn on AC unit or the fan in
Here is what I would try to see if the thermostat is bad. Take the facing off the thermostat. Once this is done you will see where the wiring is connected should be a red green yellow and white Turn off power to unit make a diagram as to where the wiring was connected red to r green to g and so on Remove these wires red green and yellow and twist them together Go to the power source and re energize the unit once this is done all components should come on if not the thermostat isn't your problem Red is your low voltage power supply (24 volts) Green is your fan motor in furnance, yellow is your outside cooling unit. 1 other thing you might check. In the furnance if the doors are not properly installed on the face of the furnance it may not allow the unit to come on. There is a safety switch on the furnance where the filter is that if the door is not put on properly the whole system loses power and will not work. Hope this helps. Good Luck
Dave
Anonymous
  • 301 Answers
  • Posted on Oct 17, 2009
SOURCE: I only have two settings. Which is which and how so?
I think you probably have a heat pump. Aux heat is electrical resistance heat coils that produce heat when the heat pump can not produce enough to keep the temperature up (caused by low outside temperature or a problem with the refrigerant system). This resistance heat can be switched on by the emerg. heat button. It also can come on automaticlly (sp) and will be indicated by the aux being shown on the thermostat. Sometime if you set the heat up several degrees by thermostat the aux will come on to help the system catch up to the desired temperature setting. The emerg. heat is a way to turn on the AUX manually. If you do not have a heat pump system then it is possible that you have a heat pump thermostat installed on a non heat pump system. Emergency heat and Aux are both the secondary.
Hope this makes sense1
Bob
Testimonial: "So in other words, either my thermostat is mismatched or I actually have THREE heat settings. Thanks a lot Bob. Your input made all the difference."
1helpful
2answers
My AC Carrier unit is blowing 110 at vent set to cool 68 degrees ambien temp 88 degrees.
Low refrigerant levels (most common cause.)
it sounds like your outdoor unit is running, but the AC is blowing out hot air, start with cleaning the condenser coils. Spray the coils with a water hose, clearing away the loose dirt and foliage. If the AC continues to blow warm air, call an HVAC expert for help with refrigerant levels.
1helpful
My air conditioner every so often makes a noise as if the emergency heat mode is on when this happens the outside unit fan is not turning then it will stop and fan will start.
Sounds like you have a heat pump condensing unit going into defrost mode... If the thermostat was recently replaced, the orange or blue wires need to be swapped, if not, then either thermostat is failing or the control board in the condensing unit is failing...
1helpful
2answers
I have a heat pump and a Honeywell thermostat and the emergency heat randomly kicks on
The emergency heat likely randomly kicks on when your heat pump enters defrost mode.
If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
2answers
Why doesn't the compressor start in the heat mode
If the compressor is off and the heat coil is on - this is normal for the "E" or emergency heat setting. Check for proper connections between the Heat-pump, furnace(heat source) and the thermostat and that the thermostat is capable of controlling a heat-pump with secondary/emergency heat units. Thermostats designed for this have 4 settings: Cool / off / heat / E(emergency heat). in the "heat" setting, both the Heat-pump and Aux heat work together to maintain temperature. In the "E" setting, only the Aux heat source is used. The "E" setting should only be used in extreme cold - when the Heat-pump can no longer produce heat.
1helpful
I do not have a manual for my thermostat
You have a heat pump unit most of the time the unit will operate in normal mode heat setting on your thermostat but when the temp of house can't keep up the emergency heat will kick in. With that being said you can switch the t-stat to emergency mode and that will take the heat pump out of action and bring in the back up heat. You might have electrical heat strips or maybe a fuel such as natural gas or propane. hope that answers your question Ken
Goodman AC Unit with Heat Pump - Works great cooling when switched to heat the outside unit does not come on - inside comes on and uses emergency heat? What can I check? I first checked the contactor and...
Because the outdoor unit works in cooling, it sounds as though the contactor and other components outside are working correctly. The problem sounds as though it might be somewhere in your thermostat. Has the thermostat been replaced recently? If so, make sure it was wired correctly. If not, check all of the connections and contact points in your thermostat. In order for your outdoor unit to run, you must have 24vac at your "C" Common and "Y" connections. You must have this in COOL mode. Now it has to be determined why you don't have it in HEAT mode. Definitely a thermostat issue.
Hope this helps and good luck! :-)
1helpful
2answers
Carrier 38CKC042300. oUTSIDE UNIT FAN WAS TURNING REAL SLOW. ac UNIT IS OFF BUT FAN TO OUTSIDE UNIT IS STILL TURNING. sHOULD NOT BE TURNING AT ALL WITH AC UNIT OFF
The outside fan may run if the unit is in defrost mode this is normal for most heat pumps it is there way of trying to keep the outside unit from staying iced over so the next time the unit runs it will have air flow through the coil and the ice will not be there to prevent air flow.
1helpful
Bob
6helpful
4answers
Abbreviation definitions.
Economy Mode = EM
Auxelary Mode = AUX
in em mode heat pump does most of the work in aux either an electric heating element is used or gas depending on if it is gas or all electric
Top Heating & Cooling Experts
Paul Carew