Have a goodman ck36-1b not cooling inside fan is running outside no icing up no debri checked inside thermostat is good is their a reset button for the coolung compressor weve had thunder storms
Air is cool but not cold seems like compressor isnt coming on no ice on outside unit
Turn the system off on the thermostat and set the fan to "ON", this will thaw the ice faster if it hasn't already. When the system has completely thawed, which could take hours sometimes, depending on how bad it's frozen, then turn system back to "Cool" and start these checks>
1. Make sure filters are clean! 2. Make sure there is proper airflow through vents. 3. Make sure outside condenser fan motor is running.
If you have either no or minimal airflow, check the indoor blower to make sure it's working, if it is, the evaporator coil is dirty restricting the airflow. Be sure the system is thawed because the ice will also block the airflow!
If the condenser fan motor is not running, either the capacitor or the fan motor will need to be replaced.
If your filters are clean, you have good airflow through the house, and everything comes on like it should, it will most likely be the charge of refrigerant in the system is too low and you have a leak somewhere. If you have to have it charged, be sure the system is thawed before the technician gets there, he will not be able to do anything while it's froze.
maybe it has tripped off on high pressure, as you have have said the fan is not turning so will cause high pressure. now assuming the problem is the fan is not running than check the condition of the condensator /capacitor for the fan motor. if the motors winding is still good replace the capacitor and try it ON.
Your out door unit fan motor not runs due to pressure not build up at Heat mode. If its cool mode only fan runs with compressor when thermostat calls for it.
Without having technical knowledge, don't press any reset button. Hope it's helpful?
Make sure the outdoor fan is running and check your air filters. Also make sure the indoor and outdoor coils are clean. If all is good then get the refrigerant charge checked.
Because the outdoor unit works in cooling, it sounds as though the contactor and other components outside are working correctly. The problem sounds as though it might be somewhere in your thermostat. Has the thermostat been replaced recently? If so, make sure it was wired correctly. If not, check all of the connections and contact points in your thermostat. In order for your outdoor unit to run, you must have 24vac at your "C" Common and "Y" connections. You must have this in COOL mode. Now it has to be determined why you don't have it in HEAT mode. Definitely a thermostat issue.
When the snowflake is blinking the thermostat in in a delay mode designed to protect your compressor. If it does not stop blinking in 15min the stat is bad otherwise something is wrong with the AC
was there any refrigerant loss? "bumping" that results in movng usualy causes a leak.If the system is totally empty, It shouldn't start.. If it did major oh nos! will appear. Does it not start all? and was it running when it got thumped? May have to call a tech out on it. Sorry.
If the inside fan motor is running OK you are low on refrigerant. If the inside fan motor is not running, repair the inside fan motor. Could also possibly be dirty inside coils.
The buzzing noise is your contactor drawing in from your thermostat. The fan part of your unit is on a different circuit from your outside A\C unit. Your thermostat is the conductor of the orchestra tying ths units together. It may well be that your A\C circuit breaker has tripped, if it has there is a reason for it's tripping. Resetting the breaker by turning it off then on may get your unit running, but a technician needs to ascertain why it tripped. Or it could be a bad contact switch inside the outside unit not letting enough electricity through the switch. More than likely the first issue. Good Luck