Question about Rheem Gas/Electric Package Unit Air Conditioner 2 Ton 16 SEER 2 Stage 60,000 BTU. R410A All In One

Open Question

My gas furnace will not come on line when calling for heat

Induction/exhaust motor runs bit nothing else i have a two flash then pause code on control board

Posted by stanley steeley on

Ad

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

1991 Miller/Nordyne cmf-80 furnace Periodic non ignition


That's a "mind of its own" condition that I've gained & lost customers over. When the unit first starts in heat, you mentioned the induced draft motor will start with no other reaction from the system, that should be the best time to locate the issue by using a volt meter. If you are getting 24 volts to MV/PV at the gas valve then you know all of the heating circuit has "proved", and that the gas valve is the problem. If not, the backtrac until you find 24v. Now if you are simply just changing parts until you find the problem, which we've all done, I believe you've changed all that you can. Check all wire connections. Its probably a loose, corroded, or damaged wire/cannon plug(the plastic plugs that multiple wires are connected), stopped up gas pilot orifice, or the gas valve its self. Hope this helps!

Feb 15, 2017 | Heating & Cooling

1 Answer

My Lenox EL296uhv furnace quit running has error 227 & 228 code.


Your induction blower motor makes vacuum as it blows out the exhaust. these code are saying that there is no vacuum..It is probably caused by your exhaust being blocked by something. Maybe snow or ice build up due to cold temp. Try a hair dryer to heat up exhaust pvc pipe melt ice in pipe. CAREFULL do not get it so hot it melts.

Feb 15, 2015 | Heating & Cooling

1 Answer

New furnace, Water In Induction Motor, Yellow Flame


The problem is too much gas as opposed to not enough air. It is still running rich. Did you take into account the elevation of the location your furnace is installed at. The higher above sea level the less air that you have to aid in cumbustion. The condensation is from excess gas being cold and causing water to accumulate. Can you run it like this? Yes but it will cause issues with soot and carbon deposits. It will also cost you more money in the long run.

Dec 23, 2013 | Goodman Manufacturing Goodman GCH950453BX...

1 Answer

My heil n9mp2 isnt working just hums


is the flame igniting and then cutting off? on a gas furnace, the induction fan motor(draft motor) should start first (if the furnace is so equipped), then the flame, then the blower. if you have an induction motor (flue gas exhaust mmotor) this may be your problem (the induction motor isn't starting), if your unit doesn't have one, have you checked to see that you have gas? finally, the capacitor on the blower motor may be causing the motor not to start.

Jan 06, 2013 | Heating & Cooling

2 Answers

Turns on but no heat


From what I saw when I googled you furnace it has a hot surface igniter. It only gets hot when it's time to light the furnace. You should be able to see it glowing red when the furnace is trying to light. The furnace has a safety feature which shuts the gas valve when it doesn't detect a flame to prevent gas build up in the furnace. There are other safety features also. If the draft inducer motor isn't running the gas valve won't open. Overheat switches some of which have to be reset manually. Adjust the thermostat until it calls for heat then observe what is or isn't happening in the furnace. It will go thru a purge cycle first. The draft inducer motor will run to do this. After the purge the hot surface igniter should get hot a glow, then the gas valve will open and the burner will light. Let me know what you find.

May 04, 2010 | Goodman GMS90703BXA Heater

1 Answer

Burner ignites and goes out (Goodman Gas-fired furnace)


Hi,
The problem you have is water in the exhaust pipe.
Check to see if the pipe has sagged anywhere or if there is a trap in the line.
If you hear gurgling then it is definetly water....
Some times can be hard to find, even a pipe 1/4 full will cause problems. They are very sensitive to flue problems.
Make sure that the flue pipe either runs back to the furnace or out to the outside, a continuos slope either way witha high spot in the middle.
Also check the bottom drain of the blower if it has one, have had them plug and trap water also..

I hope that this will help you to solve your problem!

Thanks for using Fixya!!

Heatman101

Dec 24, 2009 | Goodman GMS90703BXA Heater

1 Answer

Armstrong upflow,unit works intermittent problem,call for heat nothing happens,error code of 5 blinks then 6 blinks. i have no manuel, and the panels dont have the codes on them. anyone have access to the...


Armstrong

FAILURE CODES

LED Status Fault Description
Off
No Power to the System Control

Steady Flash (11 or more flashes with no pause)
Normal Operation (Standby or call for heat)

2 Flashes
Pressure Switch Closed When It Should Be Open

3 Flashes
Pressure Switch Stuck Open 30 Seconds or Longer After Call for Heat (System in 5-minute delay mode before next call for heat). On/off switch in "off" position during a call for heat will generate this code.

4 Flashes
Open Limit Switch or Limit Switch Circuit

5 Flashes
Flame Sense Signal Sensed Out of Proper Sequence

6 Flashes - pause - 1 Flash (see Note 1)*
Soft Lockout Type 1 (Failure to light within 4 trials for ignition)

6 Flashes - pause - 2 Flashes (see Notes 1 & 2)*
Soft Lockout Type 2 (Flame sense lost during run)

6 Flashes - pause - 3 Flashes (see Notes 1 & 2)*
Soft Lockout Type 3 (Pressure switch opened during run)

6 Flashes - pause - 4 Flashes (see Notes 1 & 2)*
Soft Lockout Type 4 (Limit or limit circuit opened during run)

6 Flashes - pause - 5 Flashes (see Note 1)*
Soft Lockout Type 5 (Flame has gone away after Error Code 5)

6 Flashes - pause - 7 Flashes (see Note 1)*
Soft Lockout Type 7 (Self-check failure)

10 Flashes* - SV9520H8034 only
Line Input Voltage Polarity Reversed

Dec 12, 2009 | Coleman Heating & Cooling

4 Answers

York 92 % eff. furnace shuts down on # 3 error (pressure switch)


i have fixed almost every one of pc9 -----we have installed in our company,code three{flashes} at first new presure switches installed, same thing,york knows about this,induction motor bearings,could be bad.our local york dist, has boards,inducer, ***.motor, dual press.switch,free.as is known as the only way to fix.after all else is ruled out.one local competator called us if we wanted to join class action suit . good luck.furnaces work good at first, season or two then bam

Nov 28, 2009 | York Furnace Draft Inducer Blower Fasco #...

2 Answers

I HAVE A YORK STELLAR PLUS,MODEL PEUDD12N09501C 15 YEARS OLD. THE AIR INDUCTION MOTOR RUNS FOREVER. THE AIR INDUCTION MOTOR COMES ON , THE THE THERMOSTAT CALLS FOR GAS, THE IGNITOR LIGHTS THE GAS, FURNACE...


Check the filters first, then check for blockage in the return or supplies. An easy way to do this is by putting your hand in front of the vents to make sure accurate airflow is there. Your furnace has limit switches on it that detect heat, and if heat is getting trapped inside the unit to much, you will trip these switches and the blower will just run forever. Then you have to reset it or wait forever. But try those few things first. Hope this helps.

Nov 26, 2009 | York Yankees Bedding MLB Comforter

1 Answer

Furnace start buts shuts off


It sounds like you have an obstruction in the exhaust vent. Thats why when you bybass the pressure switch it runs ok. Steve

Dec 15, 2008 | Goodman GMS90703BXA Heater

Not finding what you are looking for?
Rheem Gas/Electric Package Unit Air Conditioner 2 Ton 16 SEER 2 Stage 60,000 BTU. R410A All In One Logo

Related Topics:

87 people viewed this question

Ask a Question

Usually answered in minutes!

Top Rheem Heating & Cooling Experts

Lawrence Oravetz

Level 3 Expert

10548 Answers

ray gallant

Level 3 Expert

71004 Answers

Marat Brikov

Level 3 Expert

515 Answers

Are you a Rheem Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...