Question about Eaton Computers & Internet
A Eaton 9315 ups 80kVA has Inverter failure and AC Output Over voltage. Any help?
Gruber Power Services
    Mentor:
    An expert who has written 3 tips or uploaded 2 video tips.
  • 176 Answers
Sound like IGBT. It's a black block looking device mounted directly on the heat sink of the inverter leg. Remember you have 3 legs total to check. If I remember right there are 3 IGBT's per leg. You could also have blown a DC capacitor.
Posted on Jul 29, 2015
I mistakenly connected energy source at the AC inverter output .Inverter is 5KVA cyberpower inverter.After correcting the connection, It cannot switch from DC to AC( fault signal is displayed on its...
John,
It's shorted out, either replace the part or buy a new one.
If you need UPS, Surge, or Power Related help don't hesitate to contact me!
Daniel • [email protected] • Power & Systems Innovations • 800.260.2259 • www.psihq.com
Sep 24, 2013 | Cybernet Systems CyberPower DC to AC...
The ups is showing an alarm of input AC under voltage. What is the course?
A Eaton 9315 ups 80kVA has Inverter failure and AC Output volatge Over voltage. I checked all the wires from and to the inveretr control board, i replaced the inverter control board. The system still with that issue. Any opinion about it?
thanks
Sep 14, 2012 | Powerware Eaton PW9130 3000VA Tower UPS ...
When the normal goes and the generator starts up to supply the ups 9315 the load on display would show it being taken in steps but at 225 amps it would just drop off and start the process of ramping up the...
I suggest that you contact the manufacturer (Eaton). They have tech support teams with decades of experience with the 9315: Toll Free: 1 800 843 9433
International: +1 919 871 1800
E-mail (Hardware): [email protected]
Mar 08, 2011 | Powerware 9315 UPS System
Is the fuse in a powerware 9135 user replaceble
There are numerous fuses (rectifier, inverter, charger, battery) on the 9135 that are located internal to the unit and not readily accessible to the user. Generally a blown fuse is accompanied by another component failure which caused the fuse to blow in the first place. As a result, additional troubleshooting and testing is usually required to identify the root cause of the failure. This of course leads to soliciting the services of a technician who has access to the schematics, test equipment, and parts to initiate a repair. Without the schematics, it's like working in the dark. For complete support, please contact Eaton (Eaton bought Powerware so now it's the Eaton 9135):
Toll Free: 1 800 356 5737
E-mail: [email protected]
www.eaton.com/9135
Jan 05, 2011 | Eaton Powerware 9135 UPS (700465446) UPS...
Xantrex Inverter/Charger has no AC output
HI
Checking AC Output
1. After the battery voltage and connections have been checked, disconnect the inverter.s AC output wires from
the power distribution system and connect a light to the AC output of the inverter/charger.
2. Disconnect the remote panel to eliminate it as a possible problem.
3. Turn the inverter ON using the power switch on the front panel of the inverter. The 100-watt light should
illuminate. Measure the voltage at the AC output wires using the multimeter. The reading should be 114.126
VAC or approximately 230 VAC if the unit is an international model. If the light does not illuminate, there is
a problem with the inverter. Contact Xantrex technical support.
May 21, 2010 | Kitchen Ranges
Output voltage unable to get above 90 V AC on battery tried on running car and only got 90 Volt AC also.
With the car voltage at 13.8V and you have less then a 400 Watt load the inverter is probably bad. The output voltage is not adjustable by the user.
Good Luck,
Gil
Feb 27, 2010 | Vector 400 Watt Power Inverter #VEC024
Hi we have problem with 6kva 9120 eaton ups,
Maybe you have many overvoltage situations at your area, that the UPS can't handle. It's a good idea to put before the ups an overvoltage protection or a stabilizer. Ask the manufacture for the overvoltage protection of the ups that can handle.
Stelios.
Feb 22, 2010 | Eaton Powerware® 9120 UPS System
Hi i jus need box and speaker specs for the dual 2 ohm 10pw3
General Information Manufacturer: Eaton Corporation
Manufacturer Part Number: 103004248-5592
Manufacturer Website Address: www.eaton.com/EatonCom/Markets/NorthAmerica
Brand Name: Eaton
Product Series: PW3105
Product Model: PW3105 700
Product Name: Powerware PW3105 700VA Tower UPS
Product Type: Standby UPS
Technical Information Plug/Connector Type: NEMA 5-15P
Receptacles: 4 x NEMA 5-15R - Battery Backup System
Switching Time:
  • 6 ms
  • 6 ms
Dataline Protection: RJ-45 Internet
Power Description Load Capacity: 700VA/420W
Input Voltage: 110V AC
Input Voltage Range: 0V AC to 160V AC
Output Voltage: 115V AC
Frequency:
  • 50Hz
  • 60Hz
Management Overload Protection: Circuit Breaker
Interfaces/Ports Interfaces/Ports: 1 x USB
Battery Information Batteries: Maintenance Free Sealed Lead-acid
Backup/Run Time: 3 Minute 420W Full-load
Physical Characteristics Form Factor: Tower
Dimensions:
  • 4.4" Height x 11" Width x 7" Depth
Weight: 9.7 lb
Miscellaneous Certifications & Standards:
  • Safety: UL 1778 3rd Edtion/CSAC22.2 No107.3, Designed to meet UL497A
  • EMI: FCC Class B
  • Software Included: Powerware LanSafe Software
    Green Compliance: Yes
    Green Compliance Certificate/Authority: RoHS
    Jan 22, 2009 | Powerware PW3105 700 (103004248-5501)...
    How to determine the age of my 9315 and pbIII?
    Call Eaton/Powerware and provide the serial number.
    Apr 04, 2008 | Powerware PowerRite Plus UPS System
    Computers & Internet Logo
    536 people viewed this question
    Top Eaton Computers & Internet Experts
    Gruber Power...
    Gruber Power...
    jimixclay
    Tom Chichester
    Are you an Eaton Computer and Internet Expert? Answer questions, earn points and help others