LG LMN127HVT LMN127HVT 12 000 BTU Ductless Indoor WaMounted Multi Split Air Conditioner/Heat Pump Unit For Flex Multi Split Heat Pump/Air Conditioner Systems in White Logo
M
Matthew Bartl Posted on May 26, 2014
Answered by a Fixya Expert
Trustworthy Expert Solutions
View Our Top Experts
My indoor lg mini split unit the cool light flashes 4 time what's wrong
Cris Sparks
Level 2:
Sergeant:
  • Expert 338 Answers
  • Posted on Jun 14, 2014
Cris Sparks
Expert
Level 2:
Sergeant:
Answers
338
Questions
0
Helped
87158
Points
819
Indoor unit faults = CH04 or C4
Fascia LED's
- RED = None
- GREEN = 4 Flash
Contents = Drain Pump / Float Switch
Case of Error = Float Switch Open Circuit (High Level Water Alarm)
Indoor Status = Off
clean your condensate drain line you can do this with a shop vac,
Read more: http://dgoma.es/multisplit_lg/lg-multi-split-units-error-code/#ixzz34dr3Cu00
Follow us: dgoma on Facebook
I have an lg split system with 4 cieling mont units model# LMU540HV ITS BEEN WORKING FINE FOR YEARS now when i turns on it will run for 2-3 min. Then flash 5 time ive ive checked voltage alls good lights...
According to an LG installation manual for the LMU540HV, if the flashing light is viewed on the indoor unit with the ceiling cassette light on the far right flashing 5 times, it is an error code meaning there is a communication error between indoor and outdoor units. I would start by making all indoor and the outdoor units have power. I would especially check to see that fuses or circuit breakers to the outdoor unit have not failed. Or check the outside disconnect to make sure it is working. Check with a volt meter to be sure you have 220 volts present to the outdoor unit. Also, if the 4 indoor units have emergency power off switches, make sure all 4 are turned on. Checking to see power is present both indoors and outdoors a good place to start. It the outdoor unit has power, there may be a relay that has failed or a power circuit board has failed that would cause it not to communicate.
H4 error code is shown on AC display what can i do to slove this problem
Full list of Gree Air Conditioner Mini Split Units Fault Codes. When error codes appear on the Gree air conditioner indoor display, this tells the user there is an issue with the Gree AC unit. The error code displayed will inform you of the issue or problem that is occurring with the air conditioner. Knowing what the error code means and its definition will help you to understand and troubleshoot the exact Gree air conditioner part that needs to be fixed, cleaned, repaired, or replaced. You can then clean, fix, or replace the Gree part yourself and save money. See below for all error codes that can occur on Gree Mini Split AC's.
Gree Mini Split Air Conditioner Error Codes - How To Fix
Gree Viero AC Mini Split PDF Owners and Troubleshooting Manual
GREE DUCTLESS AIR CONDITIONING & HEATING SYSTEM INSTALLATION MANUAL
Gree Mini Split Air Conditioner Part Names and Locations
INDOOR AND OUTDOOR UNIT
The Gree Air Conditioning Vireo System has onboard error code diagnostics. The outdoor unit will provide status indicators and the indoor wall unit and remote control will display error codes. The following is a summary of the codes with explanations...
GREE AC DIAGNOSTIC ERROR CODES
Gree Vireo Mini Split Air Conditioner Error Code F0
Refrigerant Leakage Protection
1) Refrigerant leak(s).
2) Indoor coil temperature sensor not calibrated.
3) Refrigerant flow is restricted (ex. valve, exv, debris)
Outdoor Unit Red Light Indicator - 9 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code E1
System High Pressure
1) Over charged with refrigerant.
2) Blocked or dirty outdoor coil.
3) Extreme outdoor ambient conditions
Gree Vireo Mini Split Air Conditioner Error Code E2
Indoor Anti-Freeze Protection
1) Low return airflow.
2) Indoor fan speed is too low.
3) Indoor coil is blocked or dirty.
Outdoor Unit Yellow Light Indicator - 3 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code E4
Compressor High Discharge Temperature Protection
Please refer to the malfunction analysis (discharge temperature, overload) in service manual.
Outdoor Unit Yellow Light Indicator - 7 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code E5
Overcurrent Protection
1) Supply voltage is unstable.
2) Supply voltage is too low and system load is too high.
Outdoor Unit Yellow Light Indicator - 5 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code E6
Communication Malfunction
1) Communication cable is wired incorrectly between indoor and outdoor units.
2) Indoor or Outdoor control board malfunction.
Outdoor Unit Yellow Light Indicator - Continuous On
Gree Vireo Mini Split Air Conditioner Error Code E8
High Temperature Resistant Protection
1) Incorrect refrigerant charge level.
2) Refrigerant metering device malfunction.
3) Compressor malfunction.
Outdoor Unit Yellow Light Indicator - 6 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code EE
EEPROM Memory Malfunction
Control board malfunction.
Outdoor Unit Yellow Light Indicator - 11 flashes and 1 sec Off
Gree Vireo Mini Split Air Conditioner Error Code C5
System Configuration Malfunction
1) No jumper cap inserted on the control board.
2) Incorrect or damaged jumper cap on control board.
3) Indoor and outdoor units are not compatible.
Gree Vireo Mini Split Air Conditioner Error Code Fo
Pump Down or Gathering Refrigerant Status
Optional Service Mode
Outdoor Unit Yellow Light Indicator - 17 flashes and 1 sec Off
NOTE: All of the Gree Air Conditioner Model Numbers below are applicable for the error codes on this page...
Gree AC Vireo Models: VIR09HP115V1A, VIR12HP115V1A, VIR09HP230V1A, VIR12HP230V1A, VIR18HP230V1A, VIR24HP230V1A, VIR30HP230V1A, and VIR36HP230V1A.
Gree Mini Split Air Conditioner Error Code Charts
Gree Mini Split AC Remote Control Button Names
Gree Mini Split AC Remote Control Icons Display Screen
Gree Mini Split Air Conditioner Air Filter Cleaning Procedure
Need help with error codes on your Gree AC? Please leave a question below and we will be happy to help.
New LG mini split installation getting error CH05
I believe the wiring may be incorrect. Here arethe fault codes.
05
Comms Error, check your wiring, remove external pumps. Split/Multi - check volts from terminal N to 3 = 0 - 65 Vdc, Multi V - 4 Vdc terminals 3 and 4
5
Hope this helps
Bob
We have 2.0 HP inverter wall mounted LG aircon, when we turn on the ac, the indoor unit only is running and shut down after 3 mins. What is the solution?
Hi Marie, does the green indicator light on the front panel flash after it shuts down? If it does...count how many times it flashes this will refer to a fault code diagnostic.
Keith.
1helpful
LMN096HVT
Have you tried unplugging it and plugging it in again?
13helpful
2answers
4answers
Indoor unit flashes 5 times. error code meaning?
E-5 -Comms Error, check your wiring, remove external pumps. Split/Multi - check volts from terminal N to 3 = 0 - 65 Vdc, Multi V - 4 Vdc terminals 3 and 4
2answers
Top LG Heating & Cooling Experts
Ronny Bennett Sr.
Ronny Bennett Sr.
Mike Cairns
Mike Cairns
MattS1978