E4 Error Code

Says its Abnormality of the OutDoor Unit? Unit runs for 1/2 hr fine, then the light starts blinking 4 times continuously but still running fine and after a 1/2 hr of blinking lite, unit shuts off.

1 Answer

Steve F

Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

  • Master 1,361 Answers
  • Posted on Apr 09, 2014
Steve F
Master
Level 3:

An expert who has achieved level 3 by getting 1000 points

Superstar:

An expert that got 20 achievements.

All-Star:

An expert that got 10 achievements.

MVP:

An expert that got 5 achievements.

Joined: Jun 16, 2011
Answers
1361
Questions
2
Helped
567459
Points
3788

Could be overheating and a sensor is triggering the machine to turn off or it could be short of gas. Check all pipework connections for tightness and especially look for oily residue on any of them. This would indicate a leak. Unfortunately, if there is a leak, you would require a licensed air con Tech to repair the leak and regas it.

5 Related Answers

Anonymous

  • 1420 Answers
  • Posted on Sep 04, 2007

SOURCE: no cooling after power out, indicator lights pattern not in manual

The Mitsubishi units have to be reset by turning off the indoor units by switching the remote or thermostat to off. Then turn off the breaker to the outside unit(s). After 30 seconds,turn on the breaker and then you can turn on the remote for cool. If no lights come on on the inside units, most likely you have blown a fuse soldered on the main PC board. At this point, call your technician. A goos tech will be able to wire in an in-line fuse holder so if it should happen again, you can easily replace the fuse. If you do see a light or two come on at the indoor unit but the outdoor unit does not start after 3 or 4 minutes, sounds like you will need to call a technician. Most likely you have a blown fuse on the main PC board of the outside unit. It is not an easy one to replace. Good Luck!

Ad

Anonymous

  • 2 Answers
  • Posted on Aug 15, 2009

SOURCE: Inside unit runs left light blinks compressor will not start

In your out door unit you will have a dual capacitor. One side will be used to help start the outdoor fan and the other side is used to start the compressor. I have a fluke 187 volt ohm meter and can read uF. You probably have a bad capacitor. Its easy to change and by far the cheapest thing to do before calling a tech. It is out side where the electrical enters the outdoor unit. Be sure to kill all power to the outdoor unit and ground the capacitor before you remove and test. This has been the summer of capacitors here in SW Missouri. I have replaced several in the area.

Anonymous

  • 5 Answers
  • Posted on Jul 14, 2010

SOURCE: Indoor unit turns on, then compressor turns on and

sonds like a short somewhere in the system

Anonymous

  • 12 Answers
  • Posted on Jul 21, 2010

SOURCE: outside unit do not run.Red light blink 6

That is a trouble code signalling that your unit needs service. It is time to call a professional for help!

Anonymous

  • 12 Answers
  • Posted on Jul 21, 2010

SOURCE: eo error code

You need a professional here. Once this has been repaired, I would suggest running the wiring to the outdoor unit inside some sort of piping to protect it.

Ad

Add Your Answer

×

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

0helpful
1answer

How do I get the fault codes up on a Panasonic split air conditioning system CUE24FKR

14.2.2 To Make a Diagnosis1 Timer LED starts to blink and the unit automatically stops the operation.
2 Press the CHECK button on the remote control continuously for 5 seconds.
3 "- -" will be displayed on the remote control display.
Note: Display only for "- -" (No signal transmission, no receiving sound and no Power LED blinking)
4 Press the TIMER ? or ? button on the remote control. The code "H00" (no abnormality) will be displayed
and signal will be transmit to the main unit.
5 Each press of the button (? or ?) will increase error code
number and transmit error code signal to the main unit.
6 When the latest abnormality code on the main unit and
code transmitted from the remote control are matched,
Power LED will light up for 30 seconds and a "beep" sound
(continuously for 4 seconds) will be heard. If no codes are
matched, Power LED will light up for 0.5 seconds and no
sound will be heard.
7 The breakdown diagnosis mode will be canceled unless
pressing the CHECK button continuously for 5 seconds or
operating the unit for 30 seconds.
8 The LED will be off if the unit is turned off or the RESET
button on the main unit is pressed.
Diagnosis
display Abnormality / Protection control Abnormality
Judgement Emergency operation Primary location to verify H00 No abnormality detected - Normal operation H11 Indoor / Outdoor abnormal communica
tion > 1 min after starting
operation Indoor fan operation
only • Internal / external cable connections
• Indoor / Outdoor PCB H14 Indoor intake air temperature sensor
abnormality Continue for 5 sec. - • Intake air temperature sensor (detec
tive or disconnected) H15 Outdoor compressor temperature sensor
abnormality Continue for 5 sec. - • Compressor temperature sensor
(detective or disconnected) H16 Outdoor Current Transformer open cir
cuit - - • Outdoor PCB
• IPM (Power transistor) module H19 Indoor fan motor mechanism locked 7 times occurance
continuously - • Indoor PCB
• Fan motor H23 Indoor heat exchanger temperature sen
sor abnormality Continue for 5 sec. O
(Cooling only) • Heat exchanger temperature sensor
(detective or disconnected) H24 Indoor heat exchanger temperature sen
sor 2 abnormality Continue for 5 sec. - • Heat exchanger temperature sensor
(detective or disconnected) H27 Outdoor intake air temperature sensor
abnormality Continue for 5 sec. O • Outdoor temperature sensor (detec
tive or disconnected) H28 Outdoor heat exchanger temperature
sensor abnormality Continue for 5 sec. O • Outdoor heat exchanger temperature
sensor (detective or disconnected) H30 Outdoor discharge air temperature sen
sor abnormality Continue for 5 sec. - • Outdoor temperature sensor (detec
tive or disconnected) H33 Indoor / Outdoor wrong connection - - • Indoor / Outdoor supply voltage H38 Indoor / Outdoor mismatch (brand code) H50 Ventilation motor abnormality 7 times occurance
continuously - • Indoor PCB
• Ventilation motor H51 Nozzle lock abnormality 2 times occurance
continuously - • Nozzle H52 Limit switch abnormality - - • Indoor PCB H97 Outdoor fan motor mechanism locked 2 times occurance
within 30 minutes - • Indoor PCB
• Fan motor H98 Indoor high pressure protection - - • Air filter dirty
• Air circulation short circuit H99 Indoor heat exchanger anti-freezing pro
tection - - • Insufficient refrigerant
• Air filter dirty F11 Cooling / Heating cycle changeover
abnormality 4 times occurance
within 30 minutes - • 4-way valve
• V-coil F90 PFC control 4 times occurance
within 10 minutes - • Voltage at PFC F91 Refrigerantion cycle abnormality 2 times occurance
within 20 minutes - • No refrigerant
(3-way valve is closed) F93 Compressor rotation failure 4 times occurance
within 20 minutes - • Compressor F95 Cool high pressure protection 4 times occurance
within 20 minutes - • Outdoor refrigerant circuit F96 IPM (power transistor) overheating pro
tection 4 times occurance
within 30 minutes - • Excess refrigerant
• Improper heat radiation
• IPM (Power transistor) F97 Outdoor compressor overheating protec
tion 4 times occurance
within 10 minutes - • Insufficient refrigerant
• Compressor F98 Total running current protection 3 times occurance
within 20 minutes - • Excess refrigerant
• Improper heat radiation F99 Outdoor Direct Current (DC) peak detec
tion 7 times occurance
continuously - • Outdoor PCB
• IPM (Power transistor)
• Compressor

Note:
"O" - Frequency measured and fan speed fixed.
The memory data of error code is erased when the power supply is cut off, or press the Auto Switch until "beep" sound heard following by pressing the "CHECK" button at remote controller.
Although operation forced to stop when abnormality detected, emergency operation is possible for certain errors (refer to Error Codes Table) by using remote controller or Auto Switch at indoor unit. However, the remote controller signal receiving sound is changed from one "beep" to four "beep" sounds.
0helpful
1answer

My panasonic air conditioner model CF-E24GKR is does not appear to be working the green power light is flashing and it is blowing cold air

14.2.2 To Make a Diagnosis:
1 Timer LED starts to blink and the unit automatically stops the operation.
2 Press the CHECK button on the remote control continuously for 5 seconds.
3 "- -" will be displayed on the remote control display.
Note: Display only for "- -" (No signal transmission, no receiving sound and no Power LED blinking)
4 Press the TIMER ? or ? button on the remote control. The code "H00" (no abnormality) will be displayed
and signal will be transmit to the main unit.
5 Each press of the button (? or ?) will increase error code
number and transmit error code signal to the main unit.
6 When the latest abnormality code on the main unit and
code transmitted from the remote control are matched,
Power LED will light up for 30 seconds and a "beep" sound
(continuously for 4 seconds) will be heard. If no codes are
matched, Power LED will light up for 0.5 seconds and no
sound will be heard.

When you have the error code you will be able to diagnose the fault.
0helpful
1answer

My Panasonic inverter split zircon with r410a blinking the red timer running indoor motor while out door unit not running?

To display memorized error (Protective operation)
status:
1. Turn power on.
2. Press the CHECK button on the remote controller
continuously for 5 seconds.
3. "- -" will be displayed on the remote controller display.
Note: Display only for "- -". (No transmitting signal, no
receiving sound and no Power LED blinking.)
4. Press the "TIMER" or button on the remote
controller. The code "H00" (no abnormality) will be
displayed and signal will be transmitted to the main
unit. The power LED lights up. If no abnormality is
stored in the memory, three beeps sound will be
heard.
5. Every press of the button (up or down) will increase
abnormality numbers and transmit abnormality code
signal to the main unit.
6. When the latest abnormality code on the main unit
and code transmitted from the remote controller are
matched, power LED will light up for 30 seconds and
a beep sound (continuously for 4 seconds) will be
heard. If no codes are matched, power LED will light
up for 0.5 seconds and no sound will be heard. 7. The breakdown diagnosis mode will be canceled unless pressing the CHECK button continuously for 5
seconds or operating the unit for 30 seconds. 8. The same diagnosis can be repeated by turning
power on again.
To clear memorized error (Protective operation) status after repair:1. Turn power on.
2. Press the AUTO button for 5 seconds (A beep
receiving sound) on the main unit to operate the unit
at Forced Cooling Operation mode.
3. Press the CHECK button on the remote controller for
about 1 second with a pointed object to transmit
signal to main unit. A beep sound is heard from main
unit and the data is cleared.
• Temporary Operation (Depending on breakdown status)
1. Press the AUTO button (A beep receiving sound) on
the main unit to operate the unit. (Remote control will
become possible.)
2. The unit can temporarily be used until repaired


panasonic error codes-xt1cn2hhaugflni22i0hbhn0-4-1.png
0helpful
1answer

My 2hp Panasonic is blinking when turn on and the compressor stop working while the outdoor fan will be blowing cool air.

1. Turn power on.
2. Press the CHECK button on the remote controller
continuously for 5 seconds.
3. "- -" will be displayed on the remote controller display.
Note: Display only for "- -". (No transmitting signal, no
receiving sound and no Power LED blinking.)
4. Press the "TIMER" or button on the remote
controller. The code "H00" (no abnormality) will be
displayed and signal will be transmitted to the main
unit. The power LED lights up. If no abnormality is
stored in the memory, three beeps sound will be
heard.
5. Every press of the button (up or down) will increase
abnormality numbers and transmit abnormality code
signal to the main unit.
6. When the latest abnormality code on the main unit
and code transmitted from the remote controller are
matched, power LED will light up for 30 seconds and
a beep sound (continuously for 4 seconds) will be
heard. If no codes are matched, power LED will light
up for 0.5 seconds and no sound will be heard.
1helpful
1answer

Panasonic air con - when you turn the air con on it runs for about 3 mins and then the timer light flashes. Air con will not work.

• Once abnormality has occurred during operation, the unit
will stop its operation, and Timer LEDs blink.
• Although Timer LED goes off when power supply is turned
off, if the unit is operated under a breakdown condition, the
LED will light up again.
• In operation after breakdown repair, the Timer LED will no
more blink. The last error code (abnormality) will be stored in
IC memory.
• To make a diagnosis:
1. Timer LED start to blink and the unit automatically
stops the operation.
2. Press the CHECK button on the remote controller
continuously for 5 seconds.
3. "- -" will be displayed on the remote controller display.
Note: Display only for "- -". (No transmitting signal, no
receiving sound and no Power LED blinking.)
4. Press the "TIMER" or button on the remote
controller. The code "H00" (no abnormality) will be
displayed and signal will be transmitted to the main
unit.
5. Every press of the button (up or down) will increase
abnormality numbers and transmit abnormality code
signal to the main unit.
6. When the latest abnormality code on the main unit
and code transmitted from the remote controller are
matched, power LED will light up for 30 seconds and
a beep sound (continuously for 4 seconds) will be
heard. If no codes are matched, power LED will light
up for 0.5 seconds and no sound will be heard.
7. The breakdown diagnosis mode will be canceled by
pressing the CHECK button continuously for 5 sec-
onds or without any operation the remote control for
30 seconds.
8. The LED will be off if the unit is turned off or the
RESET button on the main unit is pressed.

When you have the error code, we can work out what to do next.
0helpful
1answer

My Panasonic split air conditioner has stopped cooling - model:CU-W18DKR. The internal unit and internal fan operate normally. The external unit fan does not run like normal and no compressor sounds f

Sounds like a faulty outdoor controller board. If you are in Australia, call Prime Electronics or Statewide Appliances for spares.
Part number: NPCWA743383

• To make a diagnosis
1. Timer LED start to blink and the unit automatically stops the operation.
2. Press the CHECK button on the remote controller continuously for 5 seconds.
3. "- -" will be displayed on the remote controller display.
Note: Display only for "- -". (No transmitting signal, no
receiving sound and no Power LED blinking.)
4. Press the "TIMER" or button on the remote controller. The code "H00" (no abnormality) will be displayed and signal will be transmitted to the main unit.
5. Every press of the button (up or down) will increase abnormality numbers and transmit abnormality code signal to the main unit.
6. When the latest abnormality code on the main unit and code transmitted from the remote controller are matched, power LED will light up for 30 seconds and a beep sound (continuously for 4 seconds) will be heard. If no codes are matched, power LED will light up for 0.5 seconds and no sound will be heard.
7. The breakdown diagnosis mode will be canceled by pressing the CHECK button continuously for 5 seconds or without any operation the remote control for 30 seconds.
8. The LED will be off if the unit is turned off or the RESET button on the main unit is pressed.

Or better yet, get a tech to check first.
0helpful
1answer

Hi my panasonic CS-PS18NKQ is not working,timer indicator keep on blinking.

• To make a diagnosis
1. Timer LED start to blink and the unit automatically stops the operation.
2. Press the CHECK button on the remote controller continuously for 5 seconds.
3. "- -" will be displayed on the remote controller display. Note: Display only for "- -". (No transmitting signal, no receiving sound and no Power LED blinking.)
4. Press the "TIMER" or button on the remote controller. The code "H00" (no abnormality) will be displayed and signal will be transmitted to the main unit.
5. Every press of the button (up or down) will increase abnormality numbers and transmit abnormality code signal to the main unit.
6. When the latest abnormality code on the main unit and code transmitted from the remote controller are matched, power LED will light up for 30 seconds and a beep sound (continuously for 4 seconds) will be heard. If no codes are matched, power LED will light up for 0.5 seconds and no sound will be heard.
7. The breakdown diagnosis mode will be canceled by pressing the CHECK button continuously for 5 seconds or without any operation the remote control for 30 seconds.
8. The LED will be off if the unit is turned off or the
RESET button on the main unit is pressed.

When you have the error code, you can narrow down the problem.
0helpful
1answer

Hi I have a panasonic split air conditioner. It turns itself off immediately after turning on, the timer button then flashes and that's all.... I have checked for an error code it is H00. I have also made...

Hi Tania,
Have you gone through this checking sequence.? it's from a Panasonic a/c manual. It could be something as simple as a clogged filter. Once you have rectified the fault, you will probably have to clear the fault code as described at bottom below, before it will condescend to work again.
David
  • Once error occurred during operation, the unit will stop its operation, and Timer LED blinks.
  • Although Timer LED goes off when power supply is turned off, if the unit is operated under a breakdown condition, the LED will ON again.
  • In operation after breakdown repair, the Timer LED will not blink. The last error code (abnormality) will be stored
    in IC memory.
14.2.2 To Make a Diagnosis

  1. 1 Timer LED starts to blink and the unit automatically stops the operation.
  2. 2 Press the CHECK button on the remote control continuously for 5 seconds.
  3. 3 "- -" will be displayed on the remote control display.
    Note: Display only for "- -" (No signal transmission, no receiving sound and no Power LED blinking)
  4. 4 Press the TIMER ? or ? button on the remote control. The code "H00" (no abnormality) will be displayed and signal will be transmit to the main unit.
  5. 5 Each press of the button (? or ?) will increase error code number and transmit error code signal to the main unit.
  6. 6 When the latest abnormality code on the main unit and code
    transmitted from the remote control are matched, Power LED will
    light up for 30 seconds and a "beep" sound (continuously for 4
    seconds) will be heard. If no codes are matched, Power LED will light up for 0.5 seconds and no sound will be heard.
  7. 7 The breakdown diagnosis mode will be canceled unless pressing the CHECK button continuously for 5 seconds or operating the unit for 30 seconds.
  8. 8 The LED will be off if the unit is turned off or the RESET button on the main unit is pressed.
14.2.3 To Display Memorized Error Code (Protective Operation)
  1. 1 Turn power on.
  2. 2 Press the CHECK button on the remote control
  3. 3 "- -" will be displayed on the remote control display. Note: Display only for "- -" (No signal transmission, no receiving sound and no Power LED blinking)
  4. 4 Press the TIMER ? or ? button on the remote control. The code "H00" (no abnormality) will be displayed
    and signal will be transmit to the main unit.
  5. 5 Each press of the button (? or ?) will increase error code number and transmit error code signal to the main
    unit.
  6. 6 When the latest abnormality code on the main unit and code transmitted from the remote control are matched,
    Power LED will light up for 30 seconds and a "beep" sound (continuously for 4 seconds) will be heard. If no
    codes are matched, Power LED will light up for 0.5 seconds and no sound will be heard.
  7. 7 The breakdown diagnosis mode will be canceled unless pressing the CHECK button continuously for 5
    seconds or operating the unit for 30 seconds.
  8. 8 The same diagnosis can be repeated by turning power on again.
14.2.4 To Clear Memorized Error Code after Repair (Protective Operation)

  1. 1 Turn power on (in standby condition).
  2. 2 Press the AUTO button for 5 seconds (a "beep" sound is heard) on the main unit to operate the unit at Forced Cooling Operation Mode.
  3. 3 Press the CHECK button on the remote control for about 1 second with a pointed object to transmit signal to
    main unit. A "beep" sound is heard, and the Error Code is cleared
0helpful
1answer

The air conditioner gives me an E4 problem error, it starts up fine then afetr only a few minutes it shuts down... how do i solve this problem? how do i fix it?? please help me?

E4 is an"Abnormality of Outdoor Unit." There are many reasons. 1. High discharge temp due to condenser coil blocked or less rpm of fan motor. Clean coil or replace fan capacitor. 2. No gas and hence pumping oil. Find leak and arrest it. Recharge gas.
5helpful
1answer

Carrier Celesta R - error code = E4 what does it mean?

E-4 ..........short of asor no gas/E4 is an "Abnormality of Outdoor Unit."Find leak and arrest it. Recharge gas.
Not finding what you are looking for?

168 views

Ask a Question

Usually answered in minutes!

Top Mitsubishi Heating & Cooling Experts

 Mikey
Mikey

Level 3 Expert

6904 Answers

vince

Level 3 Expert

2530 Answers

Brad Brown

Level 3 Expert

19187 Answers

Are you a Mitsubishi Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...