eric mandigo Posted on Dec 03, 2013
Answered by a Fixya Expert
Trustworthy Expert Solutions
View Our Top Experts
I have a tempra 24 plus and i have no pressure.
New install it has no pressure and will only run one service at a time.
snap101
Level 2:
  • Expert 117 Answers
  • Posted on Feb 13, 2014
snap101
Expert
Level 2:
Answers
117
Questions
0
Helped
122756
Points
254
Check power make sure you have enough going to it as well as make sure the filter in it isn't plugged up.
1 Related Answer
Anonymous
  • 6 Answers
  • Posted on Dec 06, 2011
SOURCE: what s de minimum working pressure for a tempra
The manual says a MAX of 150 PSI but are you possibly asking the minimum water flow to activate the unit? If so it is .58 GPM or 2.2 l/min.
1helpful
Tempra 24 Plus low water pressure
There are several potential causes of low water pressure with a tankless water heater like the Tempra 24 Plus:
  1. Flow rate limitations: Tankless water heaters require a minimum flow rate to operate properly, typically around 0.5-0.6 gallons per minute (GPM). If the flow rate drops below this threshold, the heater may shut off or fail to produce hot water. In your case, the initial flow rate of 3.4 GPM is well above this minimum, but the drop to 1.6 GPM suggests that there may be a flow restriction or other issue causing the lower pressure.
  2. Water supply issues: Low water pressure can also be caused by problems with the water supply itself, such as a clogged or damaged pipe, a water main break, or problems with the city water system. Check with your local water utility to see if there are any known issues or maintenance activities that could be affecting water pressure in your area.
  3. Water filter or softener issues: The whole-house water filter and softener that you installed could also be causing low water pressure if they are clogged or not functioning properly. Check to make sure that the filters are clean and that the softener is operating correctly.
  4. Plumbing issues: There could be issues with the plumbing in your home, such as a clogged or damaged pipe, a faulty pressure regulator, or incorrect pipe sizing. Have a licensed plumber inspect your plumbing system to identify any potential issues.
If you have already checked for these potential causes and are still experiencing low water pressure with your Tempra 24 Plus, it may be helpful to contact the manufacturer or a licensed technician for further assistance.
2answers
Tempra Plus 29 thermal breakers keep tripping, heater will not heat water. Heater was installed last February and worked fine until a few days ago. I've reset the 3 thermal breakers a couple of times... it...
You can find this site but you can't google the manufacturer site.
If you are not able to resolve a problem please contact us toll free at 800-582-8423 before removing the unit from the wall. Stiebel Eltron is happy to provide technical assistance. In most instances, we can resolve the problem over the phone.
Tempra 24 installation. No hot water. No power led on fron cover. Is the led supposed to be on all the time or just when water is ran?
First, check the circuit breaker. Also, did you upgrade to heavier wiring and a double 60 circuit breaker when you had this installed?
How to wire tempra 24 plus
1) Copy following link for wiring tankless electric water heater:
http://waterheatertimer.org/How-to-wire-Tankless-electric-water-heater.html
2) Look at label on side of unit for total KW
3) Product manual shows 24 Kw or 24,000 watts
24,000 watts divided by 240 volts = 100 amps
So your service panel must be about 250Amp rating to support this tankless electric water heater.
http://waterheatertimer.org/pdf/Tempra_tempra-plus-Tankless-electric-water-heater-manual.pdf
4) Look inside the unit to see how many L1L2 terminals show.
You should have two sets L1L2 terminals
http://waterheatertimer.org/images/Terminals-2-tankless-200.jpg
5) You need TWO 60 amp double pole breakers to supply power to this unit.
This means you need TWO #6 wires from one breaker going to L1L2.
And you need TWO MORE #6 wires from 2nd breaker to other set of L1L2 terminals.
6) Add comment for more help Jan 2013
If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7
Eletric water heater not heating up to 125
Include product brand, model and type for best possible answer.
Include if this is new installation, or installation that worked before and stopped working.
2answers
What s de minimum working pressure for a tempra 24?
Hello. let me help you. The water pressure is what it is in the house. In other words, the tankless water heater doesn't increase the pressure of the water, it only heats the water. There is no official minimum pressure but the minimum pressure you would be happy with in any home would be 20 pounds per square inch, PSI.
Top Stiebel Eltron Water Heaters Experts
littlewheel
ADMIN Andrew
ADMIN Andrew
Are you a Stiebel Eltron Water Heater Expert? Answer questions, earn points and help others