I have a carrier furnace. Pressure, draft safeguard, or aux limit switch did not close or reopened. This is what my furnace is blinking as a LED code. What should I do? My furnace does not turn on.
The limit switches are two wires that go to a small disk about the size of a dime. There should be a tiny button between the wires. Find all the limits and push them to reset them. The draft safeguard is the one that is located where the flu pipe leaves the unit. Sometimes the limits are stubborn and it's hard to push them in. If you can't get it reset then the limit will need to be replaced but it can be bypassed temporarily by jumping the two wire together. Do no do this as a permanent fix. It can cause death.
1. Thermostat calls for heat.
2. Draft inducer motor starts.
3. Pressure switch attached by a small plastic or
rubber tube senses the negative pressure produced by
the draft inducer and closes.
4. Draft inducer runs for 30 seconds to a minute
before you hear a gas hissing sound. The ignitor did
not glow, the flame sensor (a small metal probe about
1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops
with no ignition of gas to heat your home. Your
furnace shuts down and goes into a lock out condition
until you turn your power switch back off and on
again. Then the sequence starts all over again with no ignition of the
gas.
Solution: You
probably need to purchase and install a new ignitor. I would suggest that you
inspect your ignitor closely for cracks. Make sure
you do not touch the ignitor with your bare hands. If
you do not visually see a crack, then you could have a furnace control board
problem or a limit, rollout switch problem. Please see "limits, rollout
switches & furnace control boards" further down on this page. The furnace's
control board might not be supplying the voltage to the ignitor. If
your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right
back off, then you need to clean your flame sensor with light sand paper or
steel wool. You might need a new flame sensor, but most of the time they can be
cleaned an will work well after cleaning.
1. Thermostat calls for heat.
2. Draft inducer motor starts.
3. Pressure switch attached by a small plastic or
rubber tube senses the negative pressure produced by
the draft inducer and closes.
4. Draft inducer runs for 30 seconds to a minute
before you hear a gas hissing sound. The ignitor did
not glow, the flame sensor (a small metal probe about
1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops
with no ignition of gas to heat your home. Your
furnace shuts down and goes into a lock out condition
until you turn your power switch back off and on
again. Then the sequence starts all over again with no ignition of the
gas.
Solution: You
probably need to purchase and install a new ignitor. I would suggest that you
inspect your ignitor closely for cracks. Make sure
you do not touch the ignitor with your bare hands. If
you do not visually see a crack, then you could have a furnace control board
problem or a limit, rollout switch problem. Please see "limits, rollout
switches & furnace control boards" further down on this page. The furnace's
control board might not be supplying the voltage to the ignitor. If
your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right
back off, then you need to clean your flame sensor with light sand paper or
steel wool. You might need a new flame sensor, but most of the time they can be
cleaned an will work well after cleaning.