On a heat pump the difference from heat to cool is the reversing valve.
In cooling or heating the Y1 terminal will always be energized, this is the contactor.
Depending on brand the reversing valve will either be energized in Heat or Cool. At the outdoor unit check to see if the reversing valve is getting 24 volts in cool, if not check to see if it is getting 24 volts in heating. The easiest way to check if the reversing valve is shifting, is to feel the big copper tube, (it is not the suction line on a heat pump) this is a refrigerant vapor line. It will be cold in cooling and hot in heating.
Check your thermostat installation instructions and heat pump installation instructions to determine the proper terminal designations for your heat pump and thermostat. There are some brands out there that use the B terminal as common to the 24 volt circuit, so you have to check the wiring and make sure this is not common.
If it is energized in Cool then the Y1 and O terminal will be energized. You will have 24 volts from common usually the C terminal to Y1 and O.
If it’s energized in Heat then the Y1 and B terminal should be energized. You will have 24 volts from common usually the C terminal to Y1 and B.
If you get heat when you’re calling for cooling or vice versa then switch the wire between the B and O terminals.
Jack South
  • 195 Answers
  • Posted on Oct 10, 2009
SOURCE: Rheem Heat pump 5 ton heat strip 10KW what
I would say this is around 75 amps of draw at max for both the compressor and heat units. . Therefore--at least 90 amp breaker, and probably 100 amps for good measure, and at least #4 or #2 wire to the unit.
Anonymous
  • 18 Answers
  • Posted on May 22, 2010
SOURCE: Trouble Wiring in Rheem heat pump
The red wire goes back to the furnace red, the blue back to the thermostat blue, the brown back to the furnace C terminal, the yellow back to thermostat Yellow (if there is a Y terminal on that furnace, land your Y's there. The purple wire outside comes back and ties to the W terminal on the furnace. Now you have a dual fuel unit so you will need a dual fuel kit or a thermostat that has dual fuel capability along with an outdoor sensor.
Anonymous
  • 674 Answers
  • Posted on Sep 09, 2010
SOURCE: Replacing a Rheem Heat Pump
The difference is that the reversing valve is energized it heat mode for one brand and energized in the cooling mode for the other brand. An "O" on the circuit board indicates energized in cooling and a "B" on the circuit board indicates energized in heating.
raj somaiya
  • 5370 Answers
  • Posted on Dec 05, 2010
SOURCE: im replaceing the fan moter
If the fan is running for few minutes then it stops then check the fan relay.If the fan relay is weak then this happens.Get the fan relay checked. Thanks.Helpmech.
2answers
Where are the heat strips on a rheem classic 10 seer heat pump
3 Ton Heat Pump Split System ' eBay
www.ebay.com/bhp/3-ton-heat-pump-split-system
eBayGoodman 3 Ton 14 SEER Heat Pump Split System GSZ140361 with Installation Kit.10k Heat Strip,Thermostat,Wiring, Disconnect Box,Pad. $1,912.00; Buy It ...
Need wiring digram for Rheem air conditioner model RPKA-049 JAZ
Mine doesn't have a plastic bag and the diagram on the cover is too faded to read is there somewhere online I could get a wiring diagram for the Rheem RPKA-049JAZ heat pump?
1helpful
I have a new Rheem heat pump. The cooling works fine but won't blow hot air in HEAT setting. I have reset the breakers for heat pump and air handler, changed filters and pulled batteries and reset the...
if this is indeed a heat pump you rthermostat should also have a emergency heat setting does it work on that setting... a heat pump on heat wuns the outside unit and has a recersing valve that changes the refigerant flow ..is the outside runnignduring heat mode... if you turn the thermostat in emergency heat the outside should shut down and indoor heat should come on...of this is not happening you have a wiring issue if both are not working... braeburn thermostats usually have behind the cover dip switches... i am not exactly sure what model this is but if indeed a heat pump the thermostat should have a r,w2,y,e,g,c,o,and b terminal... rheem wiring should be as follows
red to r white to w2 , g=green , yellow to y terminal there should be a wire hooked to the b terminal usually brown sometimes orange on the b terminal that is your reversing valve terminal.
you are going to have to make sure the thermostat is configured to energize the b termianl and will have to go into the installer setup to do this...hopefully you still have the paper work on thermostat... most heat pumps use the o terminal for reversing valve but rheem uses the b terminal
hope this helps out some repost with anymore probs...also make sure the switches are set to electric or gas whatever you have heat pump or not etc. inside thermostat
1helpful
Heat PumP: Rheem Two Stage Heat, One Stage Cool Thermostat Replac
R = R with jumper to RC hot side of transformer
B = Reversing valve
Y = Compressor relay
G =Blower
C = common on transformer (X on old t'stat)
W2 = Auxillary heat
E = Emergency heat