Indoor unit fan is not working on high speed
Indoor & outdoor units both come on, but no cooling is coming out of the indoor unit, speed fan is continually on low
Posted by Dr Matthew Banno on
Tony Jenkins
    New Friend:
Check your wiring, make sure you have both the lights and motor power connected to the hot wire and 1 to the ground. Hope this helps
Posted on Dec 24, 2011
How do I get the fault codes up on a Panasonic split air conditioning system CUE24FKR
14.2.2 To Make a Diagnosis1 Timer LED starts to blink and the unit automatically stops the operation.
2 Press the CHECK button on the remote control continuously for 5 seconds.
3 "- -" will be displayed on the remote control display.
Note: Display only for "- -" (No signal transmission, no receiving sound and no Power LED blinking)
4 Press the TIMER ? or ? button on the remote control. The code "H00" (no abnormality) will be displayed
and signal will be transmit to the main unit.
5 Each press of the button (? or ?) will increase error code
number and transmit error code signal to the main unit.
6 When the latest abnormality code on the main unit and
code transmitted from the remote control are matched,
Power LED will light up for 30 seconds and a "beep" sound
(continuously for 4 seconds) will be heard. If no codes are
matched, Power LED will light up for 0.5 seconds and no
sound will be heard.
7 The breakdown diagnosis mode will be canceled unless
pressing the CHECK button continuously for 5 seconds or
operating the unit for 30 seconds.
8 The LED will be off if the unit is turned off or the RESET
button on the main unit is pressed.
Diagnosis
display Abnormality / Protection control Abnormality
Judgement Emergency operation Primary location to verify H00 No abnormality detected - Normal operation H11 Indoor / Outdoor abnormal communica
tion > 1 min after starting
operation Indoor fan operation
only • Internal / external cable connections
• Indoor / Outdoor PCB H14 Indoor intake air temperature sensor
abnormality Continue for 5 sec. - • Intake air temperature sensor (detec
tive or disconnected) H15 Outdoor compressor temperature sensor
abnormality Continue for 5 sec. - • Compressor temperature sensor
(detective or disconnected) H16 Outdoor Current Transformer open cir
cuit - - • Outdoor PCB
• IPM (Power transistor) module H19 Indoor fan motor mechanism locked 7 times occurance
continuously - • Indoor PCB
• Fan motor H23 Indoor heat exchanger temperature sen
sor abnormality Continue for 5 sec. O
(Cooling only) • Heat exchanger temperature sensor
(detective or disconnected) H24 Indoor heat exchanger temperature sen
sor 2 abnormality Continue for 5 sec. - • Heat exchanger temperature sensor
(detective or disconnected) H27 Outdoor intake air temperature sensor
abnormality Continue for 5 sec. O • Outdoor temperature sensor (detec
tive or disconnected) H28 Outdoor heat exchanger temperature
sensor abnormality Continue for 5 sec. O • Outdoor heat exchanger temperature
sensor (detective or disconnected) H30 Outdoor discharge air temperature sen
sor abnormality Continue for 5 sec. - • Outdoor temperature sensor (detec
tive or disconnected) H33 Indoor / Outdoor wrong connection - - • Indoor / Outdoor supply voltage H38 Indoor / Outdoor mismatch (brand code) H50 Ventilation motor abnormality 7 times occurance
• Ventilation motor H51 Nozzle lock abnormality 2 times occurance
continuously - • Nozzle H52 Limit switch abnormality - - • Indoor PCB H97 Outdoor fan motor mechanism locked 2 times occurance
within 30 minutes - • Indoor PCB
• Fan motor H98 Indoor high pressure protection - - • Air filter dirty
• Air circulation short circuit H99 Indoor heat exchanger anti-freezing pro
tection - - • Insufficient refrigerant
• Air filter dirty F11 Cooling / Heating cycle changeover
abnormality 4 times occurance
within 30 minutes - • 4-way valve
• V-coil F90 PFC control 4 times occurance
within 10 minutes - • Voltage at PFC F91 Refrigerantion cycle abnormality 2 times occurance
within 20 minutes - • No refrigerant
(3-way valve is closed) F93 Compressor rotation failure 4 times occurance
within 20 minutes - • Compressor F95 Cool high pressure protection 4 times occurance
within 20 minutes - • Outdoor refrigerant circuit F96 IPM (power transistor) overheating pro
within 30 minutes - • Excess refrigerant
• Improper heat radiation
• IPM (Power transistor) F97 Outdoor compressor overheating protec
within 10 minutes - • Insufficient refrigerant
• Compressor F98 Total running current protection 3 times occurance
within 20 minutes - • Excess refrigerant
• Improper heat radiation F99 Outdoor Direct Current (DC) peak detec
tion 7 times occurance
continuously - • Outdoor PCB
• Compressor
Note:
"O" - Frequency measured and fan speed fixed.
The memory data of error code is erased when the power supply is cut off, or press the Auto Switch until "beep" sound heard following by pressing the "CHECK" button at remote controller.
Although operation forced to stop when abnormality detected, emergency operation is possible for certain errors (refer to Error Codes Table) by using remote controller or Auto Switch at indoor unit. However, the remote controller signal receiving sound is changed from one "beep" to four "beep" sounds.
Oct 13, 2017 | Panasonic Heating & Cooling
Luxpro psd111 thermostat shows snowflake (sometimes blinks), outdoor fan works, but no cool air comes out inside- no air flow at all. Is it the thermostat or an a/c unit malfunction?
If the outdoor unit is running the indoor fan should definitely be running. Turn power off to indoor unit. Put red green and yellow wires together behind the tstat with a wire nut. That is power (red), indoor fan (green), and compressor (yellow.) Turn power back on. This is bypassing the tstat and you should have indoor fan and outside running as well. If yes the problem is in the tstat, if no indoor fan the problem is in the unit. Good Luck!! Let me know!!
If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
Apr 28, 2017 | Heating & Cooling
Fujitsu a/c outdoor model number AOTG12LVC indoor unit economy light flashing continuously, operation light single flash, timer light single flash this sequence repeats
Serial communication error. This means that the indoor unit is not communicating with the outdoor unit usually because the outdoor unit is faulty. You can check the indoor unit by switching it to 'fan' mode and seeing if all functions work normally (fan speed, louvers move as directed). If it responds normally, then it's probably ok so you can turn your attention to the outdoor unit. A common problem with the outdoor controllers is that they are susceptible to bugs, geckos, etc. shorting them out which will mean replacement of the board.
Mar 05, 2017 | Fujitsu Heating & Cooling
Mitsubishi timer light 6 times blinking
Indoor unit indicator
RUN lamp = 6 time flash
TIMER lamp = Comes on
Outdoor unit indicator (LED5) = Stays off
Description of trouble = Indoor fan motor error (2)
Cause = Defective fan motor, Connector poor connection
Conditions of flashing = When air conditioner is operating and indoor fan motor is turned ON, indoor fan motor speed of 400 rpm or under continued for more than 30 seconds. (Air conditioner stops.)
May 29, 2016 | Mitsubishi Heating & Cooling
How to troubleshoot thermostat wiring?
I'm not sure if the thermostat is wired correctly. First, the thermostat is wired directly to the outdoor unit (compressor/condenser unit). It is NOT directly connected to the indoor unit. It connects to a low voltage control panel in the outdoor unit that sends a signal to your indoor fan/evaporator. This wire is called the fan relay switch and physically runs between the low voltage controls of the indoor and outdoor units. If the fan relay is bad it's possible that the unit runs continuously. To prevent destroying your outdoor unit there is a safety feature that prevents the indoor fan from shutting down while the outdoor unit is running. If the indoor fan did shut down while the outdoor unit was running than you would slug your compressor. That is, your compressor normally sees refrigerant gas but is instead seeing refrigerant liquid. That would not be good since this scenario would destroy your compressor. It sounds like a faulty fan relay. The actual contactor portion of the relay is in the outdoor unit.
Aug 22, 2014 | Honeywell Electronic Programmable...
Front grill
Check the air filter and if it is dirty, replace..
Turn equipment off and let the ice melt.
After ice melts, place a/c in cooling mode and set the thermostat to 3 degrees below room temp display.
The indoor unit fan should start blowing cold air immediately and then turn off once the room temp drops one degree below the cooling temp setting.
If the indoor unit does cycle off, check the outdoor unit and make sure it turns off at the same time.
If the outdoor unit continues to run and the indoor fan is not running, the indoor unit will ice up.
A defective compressor relay that is stuck in a closed position will cause icing of the indoor unit because it keeps the compressor running when it should turn off with the indoor fan.
Do you have an error code being displayed on the controller?
Is there an led light that is flashing on the indoor unit?
Another possibility causing the indoor unit to ice up is if the freon in the system starts to get low.
Make sure the ice has all melted for this next check.
Pretty easy to check without special tools.
If the air filter is clean and there is no dust/ dirt blocking the fins on the indoor unit, turn a/c back on to cool and check that the indoor unit fan comes on and is blowing air good.
Once everything seems to running good go to the outdoor unit.
There will be two lines with black rubber insulation covering them.
Peel back the insulation three inches on each line and observe the copper lines.
If either line starts to frost up the a/c system is most likely low on refrigerant.
Another cause of indoor unit icing could be that the aluminum fins behind the air filter are clogged with dust or other foreign material.
This would block the air that must be pulled in causing the indoor unit coil to become too cold due to lack of air flow and it will ice up.
Operating the cooling system when the outdoor temperature is below 60 degrees can cause the indoor unit to ice up also.
I'm Robert.
Florida certified a/c contractor. 30 years experience.
Hope this helps.
Mar 18, 2014 | Fujitsu Heating & Cooling
Why is Mr Slim MS-SGF24VC outdoor unit working when indoor unit off
Possibly a bad control board in the outdoor unit. Pull the disconnect outside to stop machine, wait 10 seconds and out back in. White mist was likely frost built up on indoor coil due to condenser running without the fan.
Jun 11, 2017 | Heating & Cooling
Does not cool
CHECK FREON LEVEL...IF GOOD CHECK FOR DISCONNECTED
THERMOSTAT OR COMPRESSOR OR CONTACTOR WIRE AT OUTDOOR UNIT WITH POWER OFF. CHECK FOR A BLOWN CAPACITOR OR UNIT GROUNDED OR BURNT WIRE. BAD BREAKER OR SEE IF OUTDOOR FAN COMES ON AND COMPRESSOR KICKS IN ( MAKES WHIRRING NOISE ) .
INSIDE CHECK BOARD FOR BLOWED FUSE, GROUNDED WIRE, MAKE SURE SYSTEM IS GETTING 24 VOLTS, IF NOT CHECK THERMOSTAT WIRES OR TRANSFORMER ON INDOOR UNIT.. IF YOU SET THERMOSTAT TO OFF AND ON AND THE INDOOR FAN COMES ON..YOUR GETTING 24 VOLTS.NOW YOU NARROWED TO THE BOARD OR LOOSE WIRE, FUSE OR THERMOSTAT. IF YOU TURN YOUR UNIT ON COOL AND AUTO AND THE INDOOR AND OUTDOOR FANS COME ON AND THE COMPRESSOR KICKS IN
BUT IS NOT COOLING...CHECK AND POSSIBLY ADD FREON...
ALSO CHECK AND MAKE SURE INDOOR BREAKER IS ON.
Apr 09, 2010 | Heating & Cooling
Split unit, I get heat but no cold
I have run into this with the LG brand systems. try shutting power off to the outdoor unit to reset all units. If problem persists, it could have to do with a charge level of refrigerant (freon) or possibly a failed control board.
Btw, I’m available to help over the phone in case u need at https://www.6ya.com/expert/cody_17f08cf8e340c06c
May 16, 2009 | Fujitsu 24R1 Air Conditioner
Sharp Air Conditioner. Model # AF-S85NX. Does this A.C. fan cycle on & off in the auto cool mode or does remain on continuously. I need a small A.C. that cycles off and on with the compressor.
If you set you r AC to FAN mode the unit will not cool, it only runs in the indoor but the outdoor will off. If you set to AUTO the unit will cool but the indoor blower will automatically run slower when the room is cool or attain the room temp. setting. If you set it to COOL the fan speed is fix depending on your setting and it also operate in cool.