Armstrong heat pump ,heat comes on and comes up to temp then outside unit does not come back on when calling for heat again ,air handler does come on
Anonymous
Level 2:
Scholar:
New Friend:
  • Expert 127 Answers
  • Posted on Aug 27, 2011
Anonymous
Expert
Level 2:
Scholar:
New Friend:
Answers
127
Questions
0
Helped
31178
Points
164
May have defective defrost control
Does anyone know the capacitor I need for my Armstrong Comfort 1000? Model number SCU10G60A-1
If you look at both the fan and compressor data plates the will say mfd ratings. Not the unit data plate but motor data plates.
Lennox ac stops working after normal shutoff untill i shut off power to air handler turn power back on ac runs till nornal temp reached shuts off will not come back on untill i kill power to air handler...
The 13HPX is a Heat Pump. It has a control board in the outside unit that will lock out after a few trips from one of the controls, such as a low or high pressure switch tripping. Turning the power off is making this board reset. Take the door off next time. to the outside unit and look at the lights on the control board. There should a sticker on the inside the door that you have to remove that describes why the unit is hard locking out according to the light configuration.
1helpful
Hey, I purchased your Honeywell RTH2510 Thermostat, but I didn't even think to label the wires when I took the old thermostat off. Upon installation of the new Thermostat (2510) the Air Conditioning...
The connections that you really need to reference would be at the air handler itself. That would tell you which wires go outside to the heat pump and which wires go to the air handler. I can however give you some basics that may help.
Heat Pump Wiring
Terminals/Colors/Function
R- Red- 24v power supply. (Usually a jumper between RC/RH)
G- Green- Fan
W- White- Heat (Sometimes W1-W2, first or second stage heat)
Y- Yellow- Cooling (Same applies as above i.e. Y1-Y2)
C- Common (Most people use blue unless it is used for B terminal and sometimes cooling on older 4 wire systems.
B/O- Reversing Valve for heat pump. Either powered heating or powered cooling, depending on system installed.
Aux- Also used for heat.
Note: Considering that the installer had their own way to run all wires, use different wires, connections, etc. This is just a reference to common wiring in the field.
How the most common system is hooked up:
Thermostat:
Red wire goes to R terminal
Yellow wire goes to Y1 or Y2 terminal
Green wire goes to G terminal
White wire usually goes to W1 or W2 terminal
Orange or Black wire goes to B/O terminal
Brown wire usually goes to Aux terminal
Blue wire goes to C terminal, unless its being used as stated above.
This is without using a fossil fuel kit or zone control board.
Where do they go from the thermostat?
Red
goes to the air handler transformer or board and goes outside to heat pump to power low voltage controls.
Yellow wire goes straight outside to Y terminals on heat pump unless going to a board inside first.
Green goes to the air handler fan relay.
Common goes to the air handler and outside to heat pump.
Black or Orange will go outside to heat pump terminals for reversing valve.
White usually goes outside to heat pump,and inside to air handler. Will explain reason further down.
Brown will go to the air handler to the heat relay for the emergency heat.
On a call for heat, with a powered cooling system (more common).
The R, Y, and G terminals energize, sending a signal to start the blower and pull in the contactor outside. Note that the Y terminal is usually cooling, but since this is a powered cooling system, the reversing valve is not energized, causing the system to run in heat mode. If you have powered heating, the reversing valve terminal will energize also. Depending on thermostat, if you set the temp substantially higher than room temp, it may kick on the emergency/aux heat to quickly raise the room temp. On a call for emergency/aux heat, the R, G, and E/Aux terminals are energized, turning on the electric/gas heat instead of the heat pump. This comes in handy since the heat pump can only pull so much heat from outside before its not enough to properly warm the house, usually around 30 degrees outside temp. If you are running the heat pump and the system goes into "defrost", the outside unit will send a signal back to the air handler, through the white wire I mentioned earlier, to tell the emergency/aux heat to come on while it is in defrost mode, providing heat whenever needed.
Again, this is just a reference guide to some basic wiring, but hopefully it will tell you where the problem is or at the least, give you a good start. There are variables in which things can change the wiring like a zoning system or fossil fuel kit. Even then, you should be able to get pretty close. Hope this helps and Happy Holidays!
Not sure the heat pump is producing enough heat
lower the fan speed to low and if you do not close your turns at 50 degrees Celsius then check the freon
1helpful
No heat when outside temp low When outside temp is 38 or above get heat. Is there a heater in the compressor that can fail?
I would start with your outdoor thermostat located in
the unit outside. I`m assuming this is a heat pump.
When the outdoor temthermostat is set to say 40F
anything lower than that and you are not using the
compressor, you are using electric heat thats located
in the air handler unit in the house.
I`m also assuming this is a split system and not a
packaged unit. If you are mechanically inclined and
you can locate the outdoor thermostat lower it below
the outdoor air temp and see if the unit comes on.
Sounds like you might have a problem with your electric heat or emergency heat
1helpful
Armstrong Heat pump Package Unit, Model#1B36DA-9B,
Hi, the outdoor unit will start to freeze when it is cold outside, but also it should go into a defrost mode to melt this ice either by the defrost board or defrost thermostat. You will know as steam will rise like smoke and some folks think it is on fire. If it never goes into defrost, get back to us and we can go through some things to check. Merry Christmas,
Shastalaker7
1helpful
2answers
My air handler comes on ,not the outside unit when my thermostat is in the off position even if i turn the thermostat down to 50 and have it turned off the air handler comes on for about 5 to 10 minutes...
If you have a standard thermostat the fan switch is for the air handler only. It completely over rides the thermostat for most settings. Now lets see this is what I'd expect:
fan switch on Indoor fan runs all time
Fan switch auto Indoor fan only runs when thermostat is set to cool or heat and the thermostat is turned up above room temp for heat or below room temp for cooling. In both of these modes the furnace blower comes on and stays on til the room temperature is satisfied. The outdoor unit only comes on for AC the out door unit will not come on for heat or the "on" setting on the thermostat. See exception 1 & 2 below...
Exception 1- (in a heat pump the out door unit runs in both heat and cool mode unless it has emergency heat turned on then it will not come on outside in the heat mode, and depending on the type of heat pump and furnace or air handler it is). A heat pump thermostat usually has "backup heat" and an "emergency heat" setting switch on the thermostat.
Exception 2 - On some thermostats they are made to cycle on the heat if the temperature reaches a preset temp (around 50'f usually but definitely by 40'f). This mode prevents freezing when if instance the homeowner is away or while the home is under construction. In this mode the fan inside can run but the heat usually comes on with it.
Exception3 - On some electric furnaces the heating strips may be individually controlled and thus not all come on at one time. This may give the feel of no heat especially if the room is cold.
Now there may be other exceptions but Ive tried to give you a heads up on some of the most common ones.
If you need more help please post more specifics about your unit/system as to for sure what switches are set to what setting and what is happening with each. My first though was that maybe your system is OK and you needed to know if the thermostat was working properly.
If this helpd you understand your problem would you please give me as hifgh a mark as you can. Thnaks for using fixya and good luck.
Weather King Heat Pump
sounds like the heat strips are not working properly on the unit. or the second stage is not wired in correctly on the thermostZAt and air handler.
Ruud heat pump question
Does the air handler take a minute or two to start, this would be normal so that it doesn't blow cool air into the house before the unit is warmed up. If not could be the fan relay is weak and needs replacing. As far as the outside unit it sounds like you need to check the refrigerant. In cooling they are 70/150 psi. This should be checked in cooling mode, once you turn it to heating mode the pressures switch bring heat inside the house instead of out. I hope this helps.
Top Ruud Heating & Cooling Experts
john h
Are you a Ruud Heating and Cooling Expert? Answer questions, earn points and help others