LG LS-L1210CL Mini Split Air Conditioner - Page 4 Questions & Answers
Error code Ch 07 ?
Ch-07 Splits = Compressor Over Current or discharge pipe temp high.
Reasons: LC condenser block-Clean it.
Less rpm of fan motor.-Replace capacitor.
Discharge temp sensor defective -Replace it.
Hope, is it helpful?
Operation and timer light flash
Please cancel your timer setting by reset the power. And also remove battery from your remote and reset it. Now start your unit.
Hi, I replaced a comp
Yes, your old one was probably a dual capacitor. The middle terminal was common to the compressor capacitor and fan capacitor. The new capacitor if for the compressor only. You will need to reuse the fan side of the capacitor or purchase a separate capacitor for the fan. I hope this helps.
Please help i got a LG r12awn split and the
Indoor Pipe Sensor or Outdoor Sensor Assy fault, Open or Short. Disconnect from PCB and measure resistance. Air sensor = 10 kOhm at 25C, Pipe sensor = 5
kOhm at 25C. If not replace sensor. Thanks.
Alraedy explained
Hi,
Here is a tip about troubleshooting your air conditioner...
There are many things that can cause your air conditioner not to cool...
AirConditioner Trouble - Review the Possibilities
heatman101
Out door is not working
Check for communication from indoor to out door.Check power in out door unit. If not, check the following.
Keep cool mode and temp setting minimum 3 degree less than room temp.
Check indoor unit return air sensor. Disconnect sensor from PCB and measure resistance. 8 kOhm at 30C and 13 kOhm at 20C if not replace air sensor
Check Indoor Pipe Sensor Disconnect from PCB and measure resistance. Pipe sensor = 5kOhm at 25C. If not replace pipe sensor.
Thanks and hope helpful?
Blower won't work and not cold
Check power to PCB and also power to blower motor. If power not to blower, then replace PCB. If power to PCB check room sensor and coil sensor for continuity. If no continuity, replace it.
LG Split Air conditioner is
you will need to check to see if the compressor is coming on, make sure it is getting the 220 volts, the wires are connected and not burnt, and that the fan is working. Check these things and if they are all good then feel free to past again, Tim
Pioneer show E7 A/C
E-7. This is a communication error between the indoor andout door units.Indoor unit coil sensor fault. Disconnect from PCB measure resistance. 10 kOhm at 10C and 4 kOhm at 30C. if not replace sensor.
The heat sistem is not working well is working
Air conditioning real definition is not giving cool but removing heat from the room. In same way for heating, it's not heating, removing cool from the room. When your indoor coil, air filter and blower wheel are full of dust, you won't get even 30% of cool or heat depend on your selection.
Simple solution for your problem is clean indoor unit completely. Check all sensor is working well. In heat mode keep temp minimum +3 degree than room temp. thanks and helpful.
We have LG air con
CH 33 -Excessive rise of standard compressor discharge temperature. If over 105°C check refrigerant charge. Over charged, release little gas still to normal PSI. If condenser full of debris, clean it.
Shows F6 message
F6 Outdoor refrigerant overcharged-Purge some gas and reset the unit and restart.
I have a 14.4 square
1tr could cover up area of 100 Sqft ( Nearly 10sqmtrs) 12,000BTU is 1Tr. Better you go with 1.5 Tr. Otherwise make any patrician work to short the area, if you can. Thanks.
Outdoor fan wont run, checked continuity good
Check power to f.motor. If not, check contactor relay is energizing. If not replace relay. Rotate manually, if hard, replace bearing or motor. If easy to rotate, but less rpm, replace capacitor. Thanks.
Lg spilt system turns of
You need to note the pattern of the flashes, short or long flashes etc.
there is a legend that explains all the possible codes.
Example: 3 long flashes 1 short flash, the legend will say something like hi pressure safety switch
or low pressure safety switch , this could mean dirty coils, inside and outdoors, or bad fan motors either location as well, the compressor may be over heating or overloading, or be gong bad. a capacitor may be the culprit, what you can do is see the fuses and airflows good and no coils blocked etc , notice if any motors stop causing the flasing lockout condition.
The aircon is on but is not cooling the room
Please follow these steps to get better cooling:
To get proper cool, keep the tips as follows:
1. Check air filter is cleaned. 2. Check indoor coil is cleaned. 3. Checkindoor blower motor is working. 4. Keep in cool mode. 5. Set temp minimum 3degrees less than room temp.6.Check compressor is working with correctpressure.
Thanks. Helpful?