What size capacitor do i use on a 12000 btu compressor unit

The compressor is not kicking in I need to know the right size and replace it
2/7/2024 10:05:16 AM • Amana... • Answered on Feb 07, 2024
0helpful
4answers

2 problems.. AC Comp cuts out. And Fan will not stop.

Unit#2 -Sounds like the contacts on the master switch are welded closed or the switch is broken, Replacing the switch should fix this unit.
#1 is a little more difficult to diagnose. The compressor is being taken off line by a circuit that protects the compressor from damage either; 1- liquid refrigerant getting back to the compressor which can be caused by something as simple as a clogged return air filter or evaporator coil on a heat pump or 2- overload situation caused by a bad condenser motor or a clogged condenser coil. The first thing you need to do is clean both coils and replace the filter,. Then check to be sure your getting good airflow across both coils. I think it's most likely an airflow issue I hope this resolves the problem GL!
7/9/2021 5:33:18 PM • Amana... • Answered on Jul 09, 2021
0helpful
3answers

Ptac fan keeps blowing

Reset the unit to factory setting by take the master switch off of 10 sec.
Then press and hold the cool and heat button down while turning the master switch back on.
2/4/2021 12:55:40 AM • Amana... • Answered on Feb 04, 2021
0helpful
3answers

Formula to calculate rating of capacitors in

It's not fixed formula, but as per basic rule, easy method tocalculate for motor capacitor. (2650 X full load amps) divided by supply voltage(mentionedin capacitor)= MFD. (Plus or minus 10% to 15%) Ex: 1 Tr which gives full load amps of 6 amps (2650 X 6)=15900 divided by 240(VAC)volts=66.25MFD (10% to 15% plus or minus) You can fix 56.32 mfd or 76.18mfd So, you can go in between 56.32 mfd and 76.18 mfd. If you calculate of 440VAC capacitor, it will be 36 mfd. Hope, it will be helpful . Thanks.
11/22/2019 11:07:01 AM • Amana... • Answered on Nov 22, 2019
0helpful
1answer

We have an Amana ptac unit in our sunroom.

These unit need to tilt backwards so water can drain
12/21/2017 8:57:35 PM • Amana... • Answered on Dec 21, 2017
0helpful
1answer

Where is the reset button

I don't think the Amana ASZ14 Heat Pump has a reset switch, but you can still reset it by resetting the power (when it's not running... turn your thermostat OFF first). To reset the power, locate your circuit breaker box. There should be a double-breaker for the Heat Pump and another double-breaker for the Air Handler. Turn them both off for at least 2-3 minutes. Then flip them back on and turn your thermostat back ON. You're thermostat may also have a RESET button that you can push. I have to reset mine every time I change the batteries in it. Here are some more repair tips... Heat Pump Troubleshooting & Repair: http://www.hometips.com/repair-fix/heat-pump.html Heat Pump Troubleshooting Repair Amana ASZ14 web page: http://www.amana-hac.com/products/heat-pumps/14-seer-asz14 ASZ14 Heat Pumps Amana ASZ 14 SEER Technical Manual (45-page PDF): http://www.manualslib.com/manual/877256/Amana-Asz-14-Seer.html Amana ASZ 14 SEER Technical Manual Amana ASZ (and ASX) Service Instructions (66-page PDF): http://www.acdirect.com/media/catalog/files/RS6200006.PDF
12/16/2015 8:47:58 PM • Amana... • Answered on Dec 16, 2015
0helpful
1answer

What does code F0 indicate?

provo te lidhesh direkt me spine 220 kompresorin
9/18/2015 7:32:08 AM • Amana... • Answered on Sep 18, 2015
0helpful
1answer

My ptac amana unit fan is hitting side what can i do

either fan wheel loose on shaft or bad bearings in motor
9/8/2015 5:20:20 PM • Amana... • Answered on Sep 08, 2015
0helpful
1answer

How to service with refridgerant

you would have to install line tap valves.
9/8/2015 5:14:25 PM • Amana... • Answered on Sep 08, 2015
0helpful
1answer

The unit fan only runs on low speed

bad switch or motor.
9/8/2015 5:07:43 PM • Amana... • Answered on Sep 08, 2015
0helpful
1answer

What can be done to preent mold in my Aprilair humidifirer attached to my A/C

use distilled water. clean system with bleach and water
9/8/2015 5:06:27 PM • Amana... • Answered on Sep 08, 2015
0helpful
3answers

I have an Amana ptac hotel type thru the wall

Hi,
If you reset the GFCI button and then when you go to turn it on the button pops again, then you have a short inside the units probably in the fan motor or the compressor..

heatman101
8/30/2015 2:56:57 AM • Amana... • Answered on Aug 30, 2015
0helpful
1answer

When the system is in the heating mode of operation and a dirty indoor coil is present, the system will have high sub-cooling?

subcooling is only a factor in the cooling mode. you convert the discharge psi to temperture and measure liquid line tempsrture. subtract difference it should be between 8 to 12 degrees.
8/10/2015 9:33:52 PM • Amana... • Answered on Aug 10, 2015
0helpful
1answer

Can High sub-cooling be the result of a dirty indoor coil?

no its related to the outside condenser
6/16/2015 12:14:13 AM • Amana... • Answered on Jun 16, 2015
0helpful
1answer

Too large of a metering piston in the indoor coil during cooling mode operation will cause the indoor coil to flood with refrigerant. True or False

That's correct. If the piston opening is too large it will allow more frozen through than designed and flood the evaporator coil.
6/10/2015 3:09:33 PM • Amana... • Answered on Jun 10, 2015
0helpful
1answer

Unit Cools when using unit controls when wall thermo is used it only blows warm air ??

the wall stat maybe bad. or wires to remote stat may be shorted
6/1/2015 5:09:39 AM • Amana... • Answered on Jun 01, 2015
0helpful
2answers

My heat pump is shot and is operating off the

You mean you are using the Emergency heat setting instead of the heat pump????...You're using Natural gas only now tn emergency heat????That's fine...I wouldn't replace a heat pump if you have Natural gas....it's too expensive compared to Gas....you may be able to still use the heat pump as an Air Conditioner only , it depends on what's wrong with it...otherwise you will have to get a Central Air unit instead...cheaper and just use the Gas for heat
5/28/2015 2:47:11 PM • Amana... • Answered on May 28, 2015
0helpful
1answer

Fan runs all the time and no heat

br means brown out protection engaged. Power was lost or voltage is to low, check for incoming power at correct voltage
3/12/2015 8:37:38 AM • Amana... • Answered on Mar 12, 2015
Not finding what you are looking for?
Amana PTH123B25AJ Heat Pump Air Conditioner Logo

276 questions posted

Ask a Question

Usually answered in minutes!

Top Amana Heating & Cooling Experts

Mike Cairns
Mike Cairns

Level 3 Expert

3054 Answers

Jay Finke
Jay Finke

Level 3 Expert

1397 Answers

Cindy Wells

Level 3 Expert

6688 Answers

Are you an Amana Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

View Most Popular

Amana Heating & Cooling

  • Amana Heating & Cooling

Most Popular Question

large metering piston in indoor coil

  • Heating & Cooling
Loading...