20 Most Recent Honeywell HZ-680 Oil Filled Radiator Heater - Page 3 Questions & Answers

0helpful
3answers

I have a Honeywell non programmable thermostat. Two zone boiler in floor system. Neither of the thermostats are showing any digital display and can't be turned on. Any ideas?

No high voltage, bad transformer, blown fuse, tripped float switch, bad tstat. If you need further help, reach me via phone at https://www.6ya.com/expert/thomas_092728000e6acb79
3/18/2023 5:44:15 PM • Honeywell... • Answered on Mar 18, 2023
0helpful
1answer

The boiler stopped reacting to HCW80 thermostat communication OK but works from the kitchen floor sensor

If your boiler is not reacting to the HCW80 thermostat, but is still working with the floor sensor in the kitchen, there may be an issue with the thermostat itself or its connection to the boiler. Here are some steps you can take to troubleshoot the issue:
  1. Check the thermostat: Ensure that the thermostat is set to the desired temperature and mode (e.g. heating mode). You can also try replacing the batteries if applicable.
  2. Check the wiring: Verify that the wiring between the thermostat and boiler is securely connected and not damaged. You can refer to the thermostat and boiler manuals for wiring diagrams.
  3. Check the thermostat settings: Some thermostats have settings that may need to be configured properly, such as the communication protocol and wiring mode. Refer to the thermostat manual for guidance on these settings.
  4. Reset the thermostat: Try resetting the thermostat to its default settings to see if this resolves the issue.
  5. Contact a professional: If the above steps do not resolve the issue, you may need to contact a professional HVAC technician to diagnose and repair the problem. They will be able to inspect the thermostat and boiler system and identify any issues that may be causing the problem you are experiencing.
3/18/2023 2:47:22 PM • Honeywell... • Answered on Mar 18, 2023
0helpful
2answers

I have no power to my Honeywell thermostats or my Honeywell hz311 zone controller and the fuse is not blown

A mon avis, vous n'avez pas d'alimentation sur vos thermostats Honeywell ou votre contr?leur de zone Honeywell hz311 et que le fusible n'est pas grill?, il y a probablement un autre probl?me ?lectrique ? r?soudre. Voici quelques ?tapes que vous pouvez suivre pour d?panner ce probl?me V?rifiez le disjoncteur : Assurez-vous que le disjoncteur pour votre syst?me de chauffage et de refroidissement n'a pas saut?. Si c'est le cas, r?enclenchez-le et v?rifiez si l'alimentation est r?tablie. V?rifiez les connexions de c?blage : V?rifiez les connexions de c?blage ? votre contr?leur de zone Honeywell hz311 et ? vos thermostats Honeywell. Assurez-vous qu'ils sont tous bien branch?s et que les fils ne sont pas desserr?s ou endommag?s. V?rifiez les transformateurs : V?rifiez les transformateurs dans votre syst?me de chauffage et de refroidissement. Si les transformateurs sont d?fectueux, ils ne pourront pas fournir l'alimentation n?cessaire ? votre syst?me. Remplacez les transformateurs si n?cessaire. V?rifiez tout de m?me les fusibles sur les transformateurs : V?rifiez les fusibles sur les transformateurs et remplacez-les si n?cessaire. Contactez un professionnel : Si vous ne parvenez pas ? r?soudre le probl?me, il est peut-?tre temps de contacter un professionnel qualifi? pour examiner votre syst?me et diagnostiquer le probl?me. Il est important de prendre des pr?cautions de s?curit? lors de la manipulation de tout syst?me ?lectrique. Veuillez contacter un professionnel pour vous aider ? r?soudre le probl?me. Si vous n'?tes pas s?r de ce que vous faites.
2/25/2023 6:27:43 PM • Honeywell... • Answered on Feb 25, 2023
0helpful
1answer

Honeywell thermostat LR95329 problems

If your Honeywell thermostat LR95329 is providing heat but not air conditioning, there could be a few different reasons why. The fact that the fan operates in fan mode indicates that the issue is likely related to the A/C function of the thermostat. Here are some steps you can take to troubleshoot the problem: Check the wiring: Make sure the wiring connections for the A/C are secure and in the correct position. Verify that the wires for the R/Y and R/W connections are properly connected and not damaged. Check the transformer: A faulty transformer can cause issues with both the heat and A/C functions of the thermostat. Check the voltage at the transformer to ensure it is providing the proper amount of power. The voltage should be between 24 and 30 volts. Check the circuit board: If the wiring and transformer are functioning properly, the issue may be with the circuit board. Inspect the circuit board for any signs of damage or wear, such as burn marks or loose connections. Contact a professional: If you are unable to resolve the issue on your own, it may be necessary to contact a professional HVAC technician to diagnose and repair the problem. It's also worth noting that the voltage readings you provided to customer service are within an acceptable range for the R/Y and R/W connections. The R/G reading is slightly lower, but this is likely due to the fact that the fan is drawing some of the voltage.
2/24/2023 9:01:05 AM • Honeywell... • Answered on Feb 24, 2023
0helpful
1answer

I JUST PURCHASED a honeywell LR 95329 thermostat. I can't get the AC to come on.

It sounds like there may be an issue with the wiring or configuration of your Honeywell LR 95329 thermostat. Here are a few things you can check:
  1. Make sure that the thermostat is properly wired. Double-check the wiring connections for the cooling mode (usually the yellow wire) and make sure it is securely connected to the corresponding terminal on the thermostat.
  2. Check the configuration settings of the thermostat. Ensure that the thermostat is configured for cooling mode and that the temperature is set to a temperature lower than the current room temperature.
  3. Verify that the air conditioning unit is working properly. Check to see if the unit is receiving power and that all the connections are secure.
  4. It's also possible that the thermostat is defective. If you've verified that everything else is working properly, you may want to consider contacting Honeywell customer support for further assistance or consider consulting with a licensed HVAC technician.
2/23/2023 4:27:48 AM • Honeywell... • Answered on Feb 23, 2023
0helpful
2answers

How do I reset all

How do I override settings on a Honeywell thermostat RTH221B
1/28/2023 5:51:47 PM • Honeywell... • Answered on Jan 28, 2023
0helpful
1answer

Honeywell Thermostat RTH230B does not call for heat

It sounds like it's wired correctly given you can operated it manually. Is this a new thermostat? Has the program function ever worked? Ensure you have the current date/time including am/pm set properly so the program understands it's starting point. If that's not the issue try setting your temperature set points to extremes. If that enables your HVAC to react it means your temperature sensor is failing.
1/19/2023 6:03:35 PM • Honeywell... • Answered on Jan 19, 2023
0helpful
1answer

Gas Rayburn Nouvelle it has a new Honeywell gas valve V4600C and thermocouple fitted. ,Inlet pressure 28 outlet 14m.bar trips grey. start button after 10 mins.

limited info generic answer ---is the pilot lighting and holding when calling for heat does gas light unit then go out that would be a s--afety shutting it down [[[high limit--fan-dirty filters -improper install -etc ]]]---if your familiar with gas systems proceed and test the circuits if unfamiliar have gas or repair company come and evaluate
1/16/2023 3:11:19 PM • Honeywell... • Answered on Jan 16, 2023
0helpful
1answer

Honeywell TZ4 - all 4 zone lights green, when called for cool, Cool light turns green then quickly turns off with clicking sound. AC#1 clicks but will not turn on and no humming observed,

It sounds like there may be an issue with the Honeywell TZ4 thermostat and the cooling system connected to it. Based on your description, it appears that when the thermostat calls for cool, the cool light turns green briefly, then turns off with a clicking sound. Additionally, the first air conditioner unit clicks but does not turn on, and the outdoor unit clicks, the fan moves for a second, then stops. This could be caused by a variety of issues, including a malfunctioning thermostat, a problem with the wiring between the thermostat and the air conditioner, or a problem with the air conditioner unit itself. To troubleshoot this issue, I would recommend checking the following:
  • Check the wiring between the thermostat and the air conditioner to make sure it's not loose or damaged.
  • Check the thermostat to make sure it's functioning properly.
  • Check the air conditioner unit for any visible damage or malfunction.
  • Check the compressor, it could be a failed compressor that is not running.
If the problem persists after checking these things, it's best to call a professional technician to diagnose and fix the problem as it might require specialized knowledge and skills.
1/15/2023 9:33:54 PM • Honeywell... • Answered on Jan 15, 2023
0helpful
2answers

Honeywell cm921 keeps automaticaly turn target temp to 35 c

The problem you're experiencing with your heating system could be caused by a malfunctioning thermostat. The thermostat may not be properly calibrated, or it could be faulty, causing it to incorrectly read the temperature and turn on the heating when it's not needed. It could also be caused by a problem with the heating system itself, such as a malfunctioning valve or a blocked duct.
1/14/2023 10:58:25 PM • Honeywell... • Answered on Jan 14, 2023
0helpful
1answer

Honeywell Chronotherm IV PLUS thermostat

It must be wired or it will not work. Take a look at the installation instructions before you attempt any reconfiguration! screenshot 2022-12-28 at 17.46.39-undefined-undefined-0.png
12/28/2022 8:16:26 PM • Honeywell... • Answered on Dec 28, 2022
0helpful
1answer

I had a Honeywell Pro series th411ou2005 t stat and it went out.

Model #RTH6360D1002 Model #RTH7560E1001/E check for these at HD or lowes, you will t stat with aux or emergency heat.
12/25/2022 1:53:54 AM • Honeywell... • Answered on Dec 25, 2022
0helpful
1answer

I want to replace an outdoor temperature sensor with a Honeywell C7089U Outdoor Sensor. Should I tuck it into the Heatpump side panel as it is right now or mount it up on the wall ?

Wouldn’t mount directly above heat pump due to graft from unit, outside anywhere is fine, directly behind unit likely best location.
12/10/2022 3:25:09 AM • Honeywell... • Answered on Dec 10, 2022
0helpful
1answer
0helpful
2answers

Can I replace my Honeywell RTH6300B1005 with a Honeywell RTH6350/RTH6450 Series model?

Yes. Turn power off, take picture and match terminals
11/26/2022 1:12:59 PM • Honeywell... • Answered on Nov 26, 2022
0helpful
1answer

How to reset my HONEYWELL PROGRAMER ST699

1800 honeywell
10/23/2022 10:11:54 PM • Honeywell... • Answered on Oct 23, 2022
0helpful
1answer

What's the color of the thermostat wires and what ones go to my Honeywell Home RTH1111B

You have too many ones (1) in the model number. Honeywell Home RTH111B Check out the installation videos in the link. https://www.google.com/search?q=Honeywell+Home+RTH111B ..
10/20/2022 5:34:24 PM • Honeywell... • Answered on Oct 20, 2022
0helpful
1answer

Honeywell thermostat not working for heat

a one zone home, ????? is it a home or RV? or? no model Honeywell told. so yeah hard . no HVAC system told we can not guess what the stat is connected to ever. my stat has batteries, for power loss, (my Huge generator is backup) but I modified mine to run on batteries or 24vac too. it is and option on my system and the extra wire was there for me. so works for COLD AIR demand not said but kinda Implied? what I do is always have a spare thermostat (in my KIT) that way if one fails , the water pipes in the house do not rupture at 0C. (my neighbor just did and $75,000 damage feb2021.) ouch. my wild guess is the heater on other end is off line, breakers tripped. door left open (hatcH) or hot ignitor dead is it Gas fired NG or what? blower dead inductor blower dead. and more can do lost more , even loose wires. or the 24vac transformer popped dead.
10/20/2022 3:44:39 PM • Honeywell... • Answered on Oct 20, 2022
0helpful
1answer

Is an Armstrong R40403-003 furnace control board a viable replacement for a Honeywell ST9120C-4057?

Hi, It's possible as I'm seeing these products listed on several pages together. However, I would check with a local hvac representative before going through with the replacements for safety. Thank you.
10/20/2022 1:55:25 AM • Honeywell... • Answered on Oct 20, 2022
0helpful
1answer

I have Honeywell HZ311 and the heat light is constant red... yet, the furnace seems to be heating/working normally. Shouldn't the light be green?

it is normal refer to page 10 in your instructions/manual or go on line and google honeywell hz311 manual
10/14/2022 2:01:19 PM • Honeywell... • Answered on Oct 14, 2022
Not finding what you are looking for?
Honeywell HZ-680 Oil Filled Radiator Heater Logo

29 questions posted

Ask a Question

Usually answered in minutes!

Top Honeywell Heating & Cooling Experts

Paul Carew

Level 3 Expert

3808 Answers

Cindy Wells

Level 3 Expert

6688 Answers

john h

Level 3 Expert

29494 Answers

Are you a Honeywell Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions