20 Most Recent Amana VTH12 12,000 BTU Vertical Terminal Air Conditioner System VTAC with Heat Pump and Choice of Back-up Electric Heater Size - Page 8 Questions & Answers

0helpful
1answer

My Amana PTAC unit is not cooling properly I just cleaned everything on it the coils and everything is still not cooling properly

check to see if the compressor on the outdoor unit is running, if so it could possibly have a refrigerant leak or faulty 4 way valve
5/9/2016 8:48:27 PM • Amana Heating &... • Answered on May 09, 2016
0helpful
1answer

Control panel

Google Amana air conditioner parts. You'll have plenty of them to choose from
2/21/2016 5:41:47 AM • Amana Heating &... • Answered on Feb 21, 2016
0helpful
1answer

Amana air unit does not kick in, compressor hums

Hi Bowmunster, Sounds like it could be a couple of things - the run capacitor could have failed or the compressor has seized - having said that a wire could have burnt off the compressor terminals Good luck
1/9/2016 1:18:53 AM • Amana Heating &... • Answered on Jan 09, 2016
0helpful
1answer

Furnace was turning on for a few seconds then shutting off. I turned it completely off for ten minutes and then back on. Now it is running normally. Is it fixed or do I still need a repair?

Maybe the reboot did the trick - with lots of the electronics now on common appliances and gadgets, a reboot, as in computers, often does the trick. Continue to monitor so that if the issue re occurs you have it addressed under warranty.
11/23/2015 3:36:55 PM • Amana Heating &... • Answered on Nov 23, 2015
0helpful
1answer

Amana 90 furnace won't ignite. Inducer fan runs for 30 seconds then shuts off and nothing happens. Try to turn fan on at thermostat and nothing happens. Ac works fine.

Most likely one of two issues is occurring. Either the inducer fan is not providing enough draft because it is either spinning too slowly or the impeller is damaged, or the pressure switch that the inducer motor air flow is supposed to activate is not operating properly. If the pressure switch fails to activate, the furnace will not open the gas valve and fire the ignition believing that there is not sufficient draft the vent the combustion gases.
10/17/2015 4:03:30 PM • Amana Heating &... • Answered on Oct 17, 2015
0helpful
1answer

Compressor starts then in less then 1 minute shuts off

It is going out on high head pressure wash the outside coil on the comdenser
10/6/2015 3:00:03 AM • Amana Heating &... • Answered on Oct 06, 2015
0helpful
1answer

I have a ap148ds and on my screen it says E2 and will not turn on

check the two sensors, one of the sensors to be defective
9/18/2015 7:25:47 AM • Amana Heating &... • Answered on Sep 18, 2015
0helpful
1answer

OUTSIDE UNIT WONT COME ON

no 240 volts at unit, bad contactor, 24 volts not there to pull contactor in.
9/8/2015 5:17:37 PM • Amana Heating &... • Answered on Sep 08, 2015
0helpful
1answer

HOW DO I CLEAN THE A-COIL

need to take coil cleaner and spray the underside of coil with fan running. when you turn a/c back on it will rinse itself through condensate.
9/8/2015 5:16:30 PM • Amana Heating &... • Answered on Sep 08, 2015
0helpful
1answer

What is the temperature in cooling for a ptac unit

should get a 10 to 12 degree drop between supply and return air.
9/8/2015 5:10:14 PM • Amana Heating &... • Answered on Sep 08, 2015
Not finding what you are looking for?
Amana VTH12 12,000 BTU Vertical Terminal Air Conditioner System VTAC with Heat Pump and Choice of Back-up Electric Heater Size Logo

0 questions posted

Ask a Question

Usually answered in minutes!

Top Amana Heating & Cooling Experts

Mike Cairns
Mike Cairns

Level 3 Expert

3054 Answers

Jay Finke
Jay Finke

Level 3 Expert

1397 Answers

Cindy Wells

Level 3 Expert

6688 Answers

Are you an Amana Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

View Most Popular

Amana Heating & Cooling

  • Amana Heating & Cooling

Most Popular Question

put in website amana atb2232mrw00 manual

  • Heating & Cooling
Loading...