Intertherm P3RA-048K Air Conditioner "amps" Questions

Ad

Question about Ruud Heating & Cooling

1 Answer

...box 30 amp 240 volt 30 amp requires #10 wire. Your disconnect should be 1.25 times the rated amps of the unit. Typically if the unit draws 22 amps in the literature they will rate it for 30 ...

Ad

Question about Dometic Heating & Cooling

2 Answers

no problems. Just what is the amps on the 13,500 no problems. Just what is the amps on the 13,500 - model # 59516.741. Thanks. to run this air condition u have to have at least 15 amps 20 amps ...

Ad

2002 Chevy Monte Carlo: Cooling Fan Assembly 2002 Chevy Monte Carlo: My cooling fan assembly is squealing when I turn on the AC, does the whole assembly need to be replaced? Usually will need ...

57915531 pulls 22.5 amps, should not pull over 15 amps, why? voltage is 117,filter and fins are clean, cools fine and motor does not appear to have any issues. could capacitors be causing this? run ...

Question about Heating & Cooling

2 Answers

...Unfortunately, there is no solution that is etched in stone. Most electricians calculate 10 amps per ton, as a rule of thumb. Hope this help

Question about Carrier Heating & Cooling

1 Answer

...there is three terms.what do they mean,compressor lra/rla and fan fla Compressor LRA ( locked rotor amps)meaning that if you hold that rotor and do not allow it to turn, it would draw that many amps. ...

Question about Heating & Cooling

1 Answer

...THREE AC units. We can hook up to 50 amp shore service or run our 52 amp generator. When we have 50 amps available can we run all THREE Air Conditioners at the same time? Yes. Each air conditioner is ...

Question about Heating & Cooling

1 Answer

...most of freon & tried again. Had low suction & low head pressure. Was pulling about 40 amps before it cut off. Thank compressor is bad ,what do you think. inefficent compressor.

Question about Heating & Cooling

1 Answer

What is the amp draw on a Liebert A/C Unit (FH245AUA00 - 480V 3 Phase) ? amp draw will be 6.9 amps per leg cutout switch will be rated for 30 amp locked rotor per leg fan runs 5 amp draw continuous ...

Question about Heating & Cooling

1 Answer

...blower motor FLA 5 Amp, and condenser fan motor FLA is 1.5 amp , you add all three and get 31.5 Amps which is your max amps, this is used in determining wire gauge and breaker size for unit. This ...

Not finding what you are looking for?
Intertherm P3RA-048K Air Conditioner Logo

285 questions posted

Ask a Question

Usually answered in minutes!

Top Intertherm Heating & Cooling Experts

john h

Level 3 Expert

29494 Answers

Brad Brown

Level 3 Expert

19187 Answers

Paul Carew

Level 3 Expert

3808 Answers

Are you an Intertherm Heating and Cooling Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...