Siemens Electrical Supplies - Recent Questions, Troubleshooting & Support

0helpful
2answers

What does the ambere (yellow) light on the breaker

If the Siemens 20Amp 1-pole arc-fault circuit breaker is wired correctly and there are no problems with the circuit that it is protecting, when first turning it to the ON position, the amber light will come on then go out after about 10 seconds or so.

If the breaker is wired incorrectly or there is a fault in the circuit the amber light will stay on.
9/6/2022 12:48:46 PM • Siemens 20Amp... • Answered on Sep 06, 2022
0helpful
1answer

Siemens QF230A keeps tripping after installation.

So likely you have a 3 wire dryer cord and a 3 wire branch circuit. The dryer neutral is bonded to the dryer frame and the third wire of the dryer plug.

There were code exceptions for dryers and stoves that allowed timer motor circuits to use the neutral as a current carrier and frame ground.

To use the GFCI for the dryer you will be required to add an additional conductor (new 3 wire+ground cable) and separate the neutral to frame bond in the dryer and use a 4 wire dryer cord.

Likely you also have some GFCI single pole breakers and replaced ungrounded receptacles with grounded (another code exception) and they work OK. The dryer and stove are different as there is current on the third wire where as on the ungrounded receptacle GFCI there is no 3rd wire.

In breif, the neutral (current carrier conductor) from the dryer must be isolated from the dryer frame and dryer ground (fault current carrier conductor).

Or just leave it the way it was.

Check with local authority with jurisdiction for local code requirements.
6/25/2020 12:19:41 AM • Siemens... • Answered on Jun 25, 2020
0helpful
2answers
0helpful
1answer

Need a Wiring diagram for w0204ml1060u

10/2/2018 8:19:12 AM • Siemens... • Answered on Oct 02, 2018
0helpful
1answer

My company wired a residence Inn Hotel and we had

The only way to really see what's going on is with a scope to look at the wave form. The arc fault breaker is the latest attempt by the NEC to control the world. Let's get real here, why on earth would we need 'arc fault protection'? The circuitry is 'looking' for a arc on the load that would indicate a potential ground fault or short circuit. I've heard nothing but negative problems associated with these devices. Too bad they are now required by the NEC. I wonder who got that 'pushed' through'...? There probably making bank right now. Sorry to voice my opinion, let me get back to the problem at hand. I really doubt it's the Chinese ballasts. It's probably more to do with the voltage level with no load, compared to the loaded voltage level. Also, it could have to do with the 'Harmonic Distortion' created by a large 'lagging power factor' coming from the ballast load. A small filter at the service entrance would probably eliminate your problems, but it's really not your problem is it? The building owner would be the one that has to mitigate 'his' electrical system issues. A good engineer capable of doing a 'power study' could have the answers for you... If you need further help, I’m available over the phone at https://www.6ya.com/expert/craig_3fa289bf857b1a3c
5/16/2018 3:39:10 AM • Siemens Seimens... • Answered on May 16, 2018
0helpful
2answers

No electricity in all bathroom outlets

you may have agfi outlet in the circuit. the outlet has 2 push buttons in the middle. it maybe an outside outlet that is tripped some contractors hook up the circiut like that
11/25/2017 8:43:32 PM • Siemens... • Answered on Nov 25, 2017
0helpful
1answer

How do I lock out a 200 amp Siemens circuit breaker ?

Check garvin Industries website. they offer a multiple of different lock systems for breakers
10/7/2017 8:37:47 PM • Siemens... • Answered on Oct 07, 2017
0helpful
2answers

Main breakers keeps blowing what is the reason i

Add up all the amps from active breakers. Do they add up over 200? If not, then I suspect a bad main breaker. If they do, then you need a larger service box and or main breaker.
9/28/2017 4:19:43 AM • Siemens 200 Amp... • Answered on Sep 28, 2017
0answers
0helpful
1answer

Can i use a fuse box panel in detached garage and connect it to circuit breaker at house

A four wire service out to the fuse box would be required.
5/3/2017 4:16:44 AM • Siemens 100 Amp... • Answered on May 03, 2017
0helpful
1answer

Can I use siemens tandem qt breaker in g3030mb1200 panel

No. your panel is designed for full size circuit breakers. Check the label inside the panel and it will tell you what style circuit breakers are allowed.
5/3/2017 4:15:22 AM • Siemens Ite Twin... • Answered on May 03, 2017
0helpful
1answer

Siemens 200amp Load Centre will not reset and no power to box after a short in the bathroom?

It sounds like the breaker at the metering base is tripped. You will need to locate the meter base outside to find the breaker. You can also call your local utility company service provider and report a power outage. they typically will come out free of charge to verify power.
4/28/2017 12:13:52 PM • Siemens... • Answered on Apr 28, 2017
0helpful
2answers

Siemens Main Breaker 125 Amp gets warm and trips

sounds like a loose connection ,or possibly a weak main breaker.
12/7/2015 9:57:13 AM • Siemens /ITE... • Answered on Dec 07, 2015
0helpful
1answer

I have a Siemens Outdoor Load Center W0408ML1125. It has the neutral bar but not the ground bar. Where do I attach the ground?

Yes it's correct the Ground Bar connects to the metal box, scrape some paint off to make a good bond, this also requires 4 wires to be correct, green ground, white insulated neutral, black L1 and red L2
2/27/2015 2:02:50 AM • Siemens... • Answered on Feb 27, 2015
Not finding what you are looking for?
Siemens Logo

119 questions posted

Ask a Question

Usually answered in minutes!

Top Siemens Electrical Supplies Experts

john h

Level 3 Expert

29494 Answers

Brad Brown

Level 3 Expert

19187 Answers

CJ Rock
CJ Rock

Level 3 Expert

4429 Answers

Are you a Siemens Electrical Supply Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...