Question about Intertherm Heating & Cooling
Indoor fan motor continue to run even if the thermostat is in auto position with the cool and heat switch in the off position. The furnance don't have a fan on and off switch in the furnance like most. The only way to turn the fan motor off is to turn off thr high power switch. I change indoor fan relay but the problem still exist.
    Prodigy:
    An expert who has answered 500 questions.
  • 540 Answers
Try this, disconnect the fanwire (green) on the furnace, if it shuts off then the hot wire from the thermostat is touching the green wire or bad thermostat. Thank-you-very-much!
Posted on Aug 26, 2008
How do I get the fault codes up on a Panasonic split air conditioning system CUE24FKR
14.2.2 To Make a Diagnosis1 Timer LED starts to blink and the unit automatically stops the operation.
2 Press the CHECK button on the remote control continuously for 5 seconds.
3 "- -" will be displayed on the remote control display.
Note: Display only for "- -" (No signal transmission, no receiving sound and no Power LED blinking)
4 Press the TIMER ? or ? button on the remote control. The code "H00" (no abnormality) will be displayed
and signal will be transmit to the main unit.
5 Each press of the button (? or ?) will increase error code
number and transmit error code signal to the main unit.
6 When the latest abnormality code on the main unit and
code transmitted from the remote control are matched,
Power LED will light up for 30 seconds and a "beep" sound
(continuously for 4 seconds) will be heard. If no codes are
matched, Power LED will light up for 0.5 seconds and no
sound will be heard.
7 The breakdown diagnosis mode will be canceled unless
pressing the CHECK button continuously for 5 seconds or
operating the unit for 30 seconds.
8 The LED will be off if the unit is turned off or the RESET
button on the main unit is pressed.
Diagnosis
display Abnormality / Protection control Abnormality
Judgement Emergency operation Primary location to verify H00 No abnormality detected - Normal operation H11 Indoor / Outdoor abnormal communica
tion > 1 min after starting
operation Indoor fan operation
only • Internal / external cable connections
• Indoor / Outdoor PCB H14 Indoor intake air temperature sensor
abnormality Continue for 5 sec. - • Intake air temperature sensor (detec
tive or disconnected) H15 Outdoor compressor temperature sensor
abnormality Continue for 5 sec. - • Compressor temperature sensor
(detective or disconnected) H16 Outdoor Current Transformer open cir
cuit - - • Outdoor PCB
• IPM (Power transistor) module H19 Indoor fan motor mechanism locked 7 times occurance
continuously - • Indoor PCB
• Fan motor H23 Indoor heat exchanger temperature sen
sor abnormality Continue for 5 sec. O
(Cooling only) • Heat exchanger temperature sensor
(detective or disconnected) H24 Indoor heat exchanger temperature sen
sor 2 abnormality Continue for 5 sec. - • Heat exchanger temperature sensor
(detective or disconnected) H27 Outdoor intake air temperature sensor
abnormality Continue for 5 sec. O • Outdoor temperature sensor (detec
tive or disconnected) H28 Outdoor heat exchanger temperature
sensor abnormality Continue for 5 sec. O • Outdoor heat exchanger temperature
sensor (detective or disconnected) H30 Outdoor discharge air temperature sen
sor abnormality Continue for 5 sec. - • Outdoor temperature sensor (detec
tive or disconnected) H33 Indoor / Outdoor wrong connection - - • Indoor / Outdoor supply voltage H38 Indoor / Outdoor mismatch (brand code) H50 Ventilation motor abnormality 7 times occurance
• Ventilation motor H51 Nozzle lock abnormality 2 times occurance
continuously - • Nozzle H52 Limit switch abnormality - - • Indoor PCB H97 Outdoor fan motor mechanism locked 2 times occurance
within 30 minutes - • Indoor PCB
• Fan motor H98 Indoor high pressure protection - - • Air filter dirty
• Air circulation short circuit H99 Indoor heat exchanger anti-freezing pro
tection - - • Insufficient refrigerant
• Air filter dirty F11 Cooling / Heating cycle changeover
abnormality 4 times occurance
within 30 minutes - • 4-way valve
• V-coil F90 PFC control 4 times occurance
within 10 minutes - • Voltage at PFC F91 Refrigerantion cycle abnormality 2 times occurance
within 20 minutes - • No refrigerant
(3-way valve is closed) F93 Compressor rotation failure 4 times occurance
within 20 minutes - • Compressor F95 Cool high pressure protection 4 times occurance
within 20 minutes - • Outdoor refrigerant circuit F96 IPM (power transistor) overheating pro
within 30 minutes - • Excess refrigerant
• Improper heat radiation
• IPM (Power transistor) F97 Outdoor compressor overheating protec
within 10 minutes - • Insufficient refrigerant
• Compressor F98 Total running current protection 3 times occurance
within 20 minutes - • Excess refrigerant
• Improper heat radiation F99 Outdoor Direct Current (DC) peak detec
tion 7 times occurance
continuously - • Outdoor PCB
• Compressor
Note:
"O" - Frequency measured and fan speed fixed.
The memory data of error code is erased when the power supply is cut off, or press the Auto Switch until "beep" sound heard following by pressing the "CHECK" button at remote controller.
Although operation forced to stop when abnormality detected, emergency operation is possible for certain errors (refer to Error Codes Table) by using remote controller or Auto Switch at indoor unit. However, the remote controller signal receiving sound is changed from one "beep" to four "beep" sounds.
Oct 13, 2017 | Panasonic Heating & Cooling
My Goodman heat pump doesn't blow air through the vents into the house, but the fan comes on when the thermostat is turn on for the air conditioning
Check first that
  • the air conditioning equipment is turned on,
  • the thermostat is calling for cooling, and that
  • the blower unit or air handler is actually blowing air through the ductwork.
Here are the details of what to check in what order if your air condtioner or heat pump doesn't start at all when you set the room thermostat to call for cooling:
  1. Check the Room Thermostat Temperature Setting: Set the thermostat to at least 5 degrees below room temperature. Our elderly mom has no patience with switches and controls. She regularly calls her air conditioning service company with a service request, sometimes late at night, because she has simply failed to set the temperature on the thermostat lower than the room temperature. Don't drive your A/C like our mother.
  2. Check that the Room Thermostat is set to "Cool" not "Off" or "Heat". If the thermostat is not set to "cool" it is simply turning off your A/C. If the thermostat display is blank then it's not receiving power (for modern digital thermostats). Check that electrical power is on at the air handler and to the the low-voltage transformer that supplies power to the thermostat.
    If the thermostat has power, check that when you set the thermostat temperature down at least 5 degrees below room temperature the thermostat calls for cooling. If it doesn't then check for broken or shorted thermostat wires anywhere between the wall thermostat and the control board at the air handler.
    You can easily eliminate possible thermostat problems as a cause of failure of the air conditioner to start by simply eliminating the thermostat from the picture: disconnect the thermostat wires at the blower unit's control board and instead connect the two thermostat terminals directly together with a jumper wire. If the system starts then the problem is in the thermostat itself or in its wiring.
    If the thermostat is working but the compressor condenser unit won't start, you could skip ahead
    to COMPRESSOR / CONDENSER DIAGNOSTICS but I wish you'd double check the remaining steps in this article first because there are some sneaky snafus listed below that might still be the problem.
  3. Check that electricity is on for the equipment. Check all of the electrical switches and controls that can turn electrical power off at the indoor air handler or at the outdoor compressor/condenser unit. There are more of these switches than you might guess. Here's a list of what to check:
    Electrical power switches and service switches outside by the compressor, inside at the air handler, and fuses or circuit breakers in the electrical panel. Don't forget to check that the access covers to the equipment are properly closed and latched. Otherwise a
    BLOWER DOOR SAFETY SWITCH could be keeping the equipment from running.
    There are several other safety switches and controls, both manual and automatic that can leave an air conditioner or heat pump turned "off" such as a blower compartment door interlock safety switch, an electric motor overload or overheat switches, and a condensate tray spillage detector switch.
    Some hard-to-find electrical switches on an air conditioner or heat pump could be keeping your air conditioner from starting, such as
    a FLOAT SWITCH on Condensate Tray that could
    be
    causing CONDENSATE PAN SWITCH LOCKOUT - condensate spilling into an overflow pan that uses a sensor switch can be enough to shut down your air conditioner.
    or
    a blower MOTOR OVERLOAD RESET SWITCH could be keeping a fan motor from starting.
    A bad or failed starter capacitor could also be leaving your system shut down, failing to start a blower, fan, or compressor motor.
    See CAPACITORS for HARD STARTING MOTORS
    Watch out: See A/C - HEAT PUMP CONTROLS & SWITCHES to be sure you have found and checked everymanual or automatic electrical switch on the system.
  4. Check the electrical supply voltage. Even if electricity is on, if the supply voltage has fallen too far below the operating voltage range of your air conditioner it's likely that the system will not operate, particlarly, you may note that the compressor motor won't start.
    See VOLTS MEASUREMENT METHODS
Aug 22, 2017 | Goodman Heating & Cooling
I have a Rheem Classic Super Quiet 80 gas furnace (for heat). The fan stops when the "heat" turns on.
Any time I ever had trouble,first thing to suspect is the thermostat.
They lose contact sometimes and sometimes you tap the face and they work til next glitch.
If the thermostat has some years on it,go ahead and replace it.
Can't you just leave the heat and fan in auto? That would be best,I think. don-ohio
Jan 10, 2017 | Heating & Cooling
I have new blower motor. it dosen't stop running
Could be a bad blower motor resistor,mounted by the blower.
Sep 28, 2016 | 2002 Dodge Ram Pickup 1500
Indoor blower won't shut off on heat pump
I would look to replace a relay that is not shutting off or replace the thermostat itself.
Nov 14, 2015 | Honeywell Heating & Cooling
I am new to a heat pump. The thermostat has an 'auto' setting and an 'on' setting. I am confused as to which one to use for heat. Can you help me?
n most heat pump thermostats you have two control switches and the temp setting. One control switch will say "Heat", "Off", "Cool" while the other says "On" and "Auto". The three position switch is for whether you are heating or cooling. The two position switch is for the fan control. "On" will make the fan run constantly whenever the three position switch is in HEAT or COOL mode. Some people use this to circulate air at all times. MOST people use the AUTO mode, where the fan is controlled by the circuitry and runs during the times of heating and cooling only.
Oct 16, 2015 | Heating & Cooling
My blower motor wont turn off in my furnance?
check the fan setting on your thermostat. On means always on, auto/int means only comes on during heating/cooling. if the thermostat is set to auto / int and the fan keeps running? you may have a bad fan relay switch. It may be integral on the primary control board of your unit.
Sep 04, 2014 | Heating & Cooling
Air will not come out when turned on smell of burned oil. A/C is also effected
Do this.
1.)At your thermostat...Turn system switch to off position(dont have it in heat,cool, or auto mode).
2.)At your thermostat...put fan switch from auto to on position.
Do you have a indoor fan(is air coming out the small registers in ceiling or floor).
Do you smell "Oil" smell(most likely an electrical smell).
If you have no indoor blower, a bad smell, most likely your indoor blower motor fried, your control box has fried,or a combination of both.
Hopefully it's just a fan motor but the smell should go away after a bit.It shouldnt linger for days.
My guess if it lingers you burnt your transformer from a low side short.
Call a tech.
Jul 29, 2009 | Heating & Cooling
The fan in the airhandler wont shut off.
The fan is controlled by a blower timer board located inside the air handler, or on older units it has a relay called (of all things) a blower relay. If these items were at fault I doubt removing the thermostat would cause the blower to go off. if bad causing this problem the blower would continue to run even with thermostat removed.
But it is also controlled by the thermostat.
You mentioned that if you remove the thermostat it cuts off. There are 2 switches on most thermostats.
1 has Cool, Off, Heat, and Emergency Heat (on a heat pump stat)
2 The other switch has On and auto (it is for the fan motor only)
I believe because it stops when you remove the thermostat that the switch on the fan is set to on possibly. It should be on auto-matic. This way the fan motor only come on with cooling or heating. If in the on it stays on all the time. If this is the case just switch to AUTO.
Or the thermostat may be wired wrong. The G terminal is where the fan motor gets instructions from the thermostat. Make sure its on G at the stat and the correct wire at the blower coil is being used for the corresponding wire going from the stat to the blower for G. Don't confues G for green it could be any color. The terminals are not for color but it makes more sence to make them color - letter identified. On the other end soemtimes the wires are not colored the same so look carefully.
Also a whisker of a thermostat wire could be touching inside the thermostat and causeing the motor to run 100%. Look carefully at this and see if it has too long of thermostat wires stickinhg on out under the screws to where they may tough other things.
If neither things stop or show the problem and it deffinately stops when thermostat is removed the thermostat is most likely bad.
If this helps you 1 way to make the repairs your\self or helps you realize you need a technician please rate mne as high as you can.
May 14, 2009 | Heating & Cooling
Honeywell digital thermostat won't turn off ac.
The Honeywell CT87 thermostat is a normal round thermostat, not digital and may have a sub-base installed with it that has a two switches on it. One is for Fan (Auto or On)and the other is for Heat, Cool and Off. Make sure the Fan switch is in the Auto position and the other switch is in either the Cool or Off mode. If you continue to get cooling, you have a short in the thermostat wire or a stuck relay in th indoor or outdoor unit. To test this, while the unit is running; remove the round outer ring on the thermostat by pulling it straight off towards you. You will find 3 slotted head screws that hold the thermostat to the sub-base. These screws are located at the 3 o'clock, 7 o'clock and 9 o'clock positions. Turn these screws counterclockwise with a small head screwdriver. They are held in place so should not fall and get lost. With the front of the thermostat removed from the base, the air conditioner should stop running. If the unit continues to run, you will need to have your A/C system inspected by a technician. If in fact your thermostat is digital, look to see how it is mounted to its sub-base and remove it. If the system stops, you may have a bad thermostat or the Fan switch is in the On position. Hopefully this will help.
Sep 11, 2007 | Honeywell CT87B ROUND HEATING&COOLING...
Heating & Cooling Logo
180 people viewed this question
Top Intertherm Heating & Cooling Experts
Dennis Boxerman
Dan Webster
Dan Webster
Bill Long
Are you an Intertherm Heating and Cooling Expert? Answer questions, earn points and help others