Question about Goodman Heating & Cooling
Install 2 ton 13 seer goodman furnace coil and condensing leak test with 110 psi of nitrogen overnight good the next day pull vacuum no leaks start up unit charge unit to proper charge check the next day system hadlow reading on suction side ice up
    Prodigy:
    An expert who has answered 500 questions.
  • 540 Answers
Goodjob, now check the valves stems for leaks.! .....Thank-you-very-much!
Posted on Aug 25, 2008
I had a 2 ton 13 SEER air handler installed last August to replace one about 27 years old. The condenser was installed about 14 years ago and it's rated as a 10 SEER. Is there a problem of them operating...
The air 'handler' is nothing more than a type of fan turned by a motor.
The condenser however is a sealed, closed system with coolant that will need to be properly removed (EPA stuff). The condenser must be installed with care, recharged, then checked for leaks.
There is far more involved than replacing an air mover.
I do most of my repairs myself but sealed systems that must be charged is something I leave up to a pro.
Feb 14, 2015 | Goodman Heating & Cooling
What is the problem with running a 10 SEER condenser with a 13 SEER air handler other than efficiency? I had a 2 ton 13 SEER air handler installed last August to replace one about 27 years old. The...
as most ac units are capillary tube control not tx valve having matched units is critical. as for cost the condensing unit is much more complex and expensive than the evaporator.
Feb 14, 2015 | Amana Goodman R-410A Heat Pump Condenser 2...
What could cause carrier fault code 42 besides bad inducer
Could be several causes.
1. Blockage on piping
2. Water in inducer housing slowing down inducer impeller
3. Condensate trap for furnace clogged up.
4. Inducer motor going bad.
5. Leak in vacuum hoses or not connected.
Welcome To the Best HVAC
Oct 09, 2014 | Carrier Comfort 13 Series 1.5 ton 14.5...
Purchased Rheem 4 ton 16 seer AC installer just left
Ask your installing company for the AHRI number. If installed with a
matching furnace and coil as listed in the certification then you will get 16 seer rating. If they installed something different than what is listed in the certificate then demand all parts listed or a refund.
Jul 18, 2014 | Rheem 14AJM49A01-RHLLHM4821JA 4 Ton 16...
No heat from furnace
If this is the first time unit has been fired up, you likely have air in the lines to purge first. Also make sure the gas supply is on/open. and that if there is a fuse present on the control board (likely a 3 Amp fuse) make sure it has not blown (which can happen simply by close proximity lightning strikes.)
Letting the unit go through the ignition sequence several times will purge the line. If furnace "locks out" on third start attempt, shut it off and start cycling it again until the furnace comes on..
This assumes the installation was checked for leaks initially.
Oct 27, 2012 | Coleman 3.5 Ton 13 SEER Complete Split...
I Have a doublewide, im wanting to know who i install freon and stop leak in my indoor central heat and air pump.
first you have to have a EPA certification too purchase, and to handle Refrigerant. in order to stop the leak first it must be located and in most cases soldered shut depending on the leaks location if the leak is in the tube sheet of the coils it my be better to replace the leaking coil. if the leak can be repaired the refrigerant must be removed from the system, leaving it in a vacuum then bring it up to atmospheric pressure (0 psi) using dry nitrogen. then the leak can be repaired, after leak has been repaired pressure test system at 120 psi for 20 min. watching gauges to see if pressure drops. If pressure holds, release nitrogen then evacuate system with vacuum pump. most manufactures require a 500 micron of less vacuum to ensure no moisture is in system then charge system according Manufactures Specification. charging and service ports are normally located at outdoor condensing unit where copper piping connects too condenser, charging manifolds are a necessary tool for this repair. I would highly recommend having a HVAC contractor preform this repair, amount of refrigerant that goes into the system is critical to performance of heat pump operation.
Sep 16, 2010 | Whirlwind FH-778 Air Conditioner
I just installed a GSC140421 using a coil CAPF
hey there, the matching coil for your unit is a Model# CAPF4860C6A. The coil you have installed is a 13 seer where the condenser is a 14 seer. Myy guess at this point without being there is you have a hot house (80 psi suction) while eliminating more heat from the condenser (180 psi). I am also guessing you are using r-22? If you could post your super heat and subcool readings and if ou have a txv or fixed orifice (guessing txv?) I could help you pinpoint the problem.
seth
Aug 02, 2009 | Goodman Heating & Cooling
Extremely long time to get cool air with 5 ton 13 seer goodman heat pump which is 3 years old.
Check your filter. Make sure it is clean. Make sure the outdoor unit is operational. (power on). Clean your condenser coil with a garden hose. If possible check your evaporator coil. If it is dirty clean it. Your furnace (or air handler) blower speed should be set on high. All of your registers (supply & return) should be open and unobstructed. Check for proper thermostat settings. If none of this information solves your problem , then your units charge needs to be checked. You could be over or undercharged with freon.
Good luck......
May 06, 2009 | Goodman Heating & Cooling
Heating & Cooling Logo
93 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others