Question about Carrier Heating & Cooling
Carrier furnace 58mvp100-f-151200 variable speed fan motor won't run
  • Gary Davd
    Gary Davd May 11, 2010
    you need to check the power going to it ???? the power comes off the relay that is mounted on the control board do you have power?? if so how many volts??
4 Suggested Answers
SOURCE:
SOURCE: fan speed setting of my Carrier furnace model 58wav091-14
most time, you don't have to do anything because the default setting for wiring with fan speed already. if not, trace the motor wires from motor with red , white and black from motor fan to PL2 and PL1. the best is look at a diagram from your actual furnace.
Posted on Nov 09, 2008
  • 746 Answers
SOURCE: carrier furnace model # 58PAV090-14 fan runs but
See the link:
http://hvac-talk.com/vbb/showthread.php?t=77420
Posted on Mar 19, 2009
Therinnaiguy
  • 1420 Answers
SOURCE: Carrier furnace, pilot does not light, fans run
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Posted on Nov 28, 2009
Have a carrier furnace model 58DHC095.it go thru its normal cycle for heat but the fan wont come on until the cycle end and furnace over heats. the fan works on all speeds and I have replaced the cont
There has to be a mechanical thermostat and it is sticking or other wise defective. I don't think that the control board is defective because it finally does turn the fan on. However the mechanical thermostat is there to prevent the fire box temperature from getting too high before the fan starts, but there must also be a over heat thermo disc that will shut the fire off when the fire box gets too high.
Oct 11, 2014 | Heating & Cooling
Furnace running all the time.
Pull the thermostat off the wall. If the fan keeps running, it is a relay in the board or just an independent fan relay.
Dec 13, 2013 | Goodman Manufacturing Goodman AEPF313716...
Fan won't blow on ac, but works on furnace
The fans heat speed is low speed and the cool speed is high speed. High speed is controlled by the fan relay normally open switch, the low speed is controlled by the temperature delay or time delay.
see diagram
Jun 05, 2013 | Coleman Home Electric Furnace Eb15b/Eb15d
Furnace won't stay lit
Are your air filters relatively new? Is a bird nesting in your units combustion air exhaust pipe? Does your draft inducer motor run before and after the gas has ignited? Check and confirm these 3 things first. Good Luck!
Mar 03, 2013 | Omega Trane Furnace Draft Inducer Blower...
Model 6k890 motor
Will the fan run with the fan switch in the ON position? as opposed to the AUTO position. If so the temperature or time delay or motor may be bad.
the fan switch operates the fan relay that controls high/cooling speed, heat speed is a time or temp delay.
Oct 25, 2012 | Dayton Gas Furnace Heater
I have a Trane Xe-60 furnace about 19 years old. During summer months, with thermostat set to deliver air, the outside condenser runs, but furnace blower does not. I can move thermostat lever from auto to...
THIS IS A COMMON PROBLEM WITH THE DOOR SWITCHES, MY FIRST ANSWER WOULD BE REPLACE THE SWITCH SECOND WOULD BE OPEN THE DOOR AND PUSH THE BUTTON IN AND SEE IF THE FURNACE WILL WORK. THIS SWITCH IS JUST A DOOR SAFTEY IF THIS WORKS. I HAVE TAPED A PIECE ON THE INSIDE OF THE DOOR WHERE THE SWITCH WILL HIT THE DOOR ABOUT A 1/4 INCH THICK AND SEE IF THIS WILL GET YOU RUNNING UNTILL YOU CAN GET A SWITCH
Oct 12, 2009 | Omega Trane Furnace Draft Inducer Blower...
Noisy Heil Gas Wall Furnace..Fan or bearings??
no, The fan should be secured with a set screw at the hub and not slip on the motor shaft Depending on the motor rating, It should be difficult to stall the motor by hand. But, no, they are not variable speedin that manner. It should be one with the shaft. Good Luck, Ned
Oct 06, 2009 | Heating & Cooling
Is there an easy way to tell if my intertherm furnace is programmable for variable fan speed. It has about 6 wires into the motor so I'm guessing it can . Or what do I need to do.
I have never heard of a variable speed Intertherm. If it has multiple wires it is likely just an adjustable fan where you can use a different lead for a different speed. Usually black is high blue is med. hi, red is low, ect. Check your wiring diagram on the furnace door. Why do you want to change the speed?
Nov 24, 2008 | Heating & Cooling
Fan speed setting of my Carrier furnace model 58wav091-14
Sep 29, 2008 | Haier HWR06XC5 Wall/Window Air Conditioner
Heating & Cooling Logo
252 people viewed this question
Top Carrier Heating & Cooling Experts
Felizardo Erilla
Felizardo Erilla
Donni Steen
Bill Long
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others