Wather heater will not ignite
Valve SIT-610 AC3 gas to valve but none to orfice. Took off the gas line to the control and gas under pressure was present. Took line off to orfice and no flow from valve, with control pressed down for a long time.
  • 1 more comment
  • Stan Kline Aug 17, 2008
    That is my problem: When I hold down the knob in the pilot position the gas is supposed to flow so that the pilot may light. Cleaned the orfice first. No gas flows so the pilot does not light. I took off the gas line to the orfice and still no gas out of the unattached tube.with the knob pressed down in the pilot position.
    I have to get the gas to flow with this knob pressed down in the pilot position. Still perplexed!
  • Stan Kline Aug 18, 2008
    Used a short stick to prop the pilot valve open. Waited [forever] and finally smelled some gas. Turned the valve off and waited quite some time to vent all the gas out of the heater. Did not want it to go boooom!
    Started the process all over again. Held the knob down in the pilot position and lit the pilot, then waited long enough for the pilot to stay on and moved the knob to on. Behold the thing works! Still do not know why the initial attempts to ignite the boiler die not work. Next day it worked again.
    I see the note above. Is there a retrofit piezoelectric started for this boiler?
    Thanks to everyone!!!!
    Stan
  • tex2539 Dec 25, 2008
    Unable to light pilot on a A. O. Hot Water Heater
  • 706 Answers
You'll probably need to ignite the pilot light before it will allow gas to flow for the heater to ignite and warm the water.. Most controls have a Pilot position that you switch it to , than using a long match .. locate the pilot light in the access opening at the bottom and get the pilot light to stay lit.. Hope that helps...
Posted on Aug 16, 2008
  • Rick Gelin
    Rick Gelin Aug 17, 2008
    If you have gas pressure to the control assembly ( which you said you do) and you select the "pilot" position.. and press the red button.. you should have gas flowing ( albeit only a small amount) to the pilot jet itself..If you do not, then you probably have a defective gas conrtoller.. Sounds like tha to me.. and it also sounds like you have a pretty good understnading of the contrl system .. Here is a short tutorial on how it is supposed to work...
    If you have an older model furnace or water heater that uses natural gas, or if you have a set of gas logs in your fire place, you have probably seen the small blue flame known as the pilot light. You may even have been able to experience the thrill of relighting the pilot light when it goes out. Let's take a look at how the pilot light works.
    The basic idea behind a pilot light is simple. Its purpose is to provide the flame needed to light the gas coming out of the main burner. When the furnace "turns on", a valve releases gas into the burner and the pilot light ignites that gas.
    The way that a pilot light is created is also simple. It is made by allowing a small amount of gas to come from the gas pipe through a small tube. You light the gas escaping from the tube, and it burns all the time.
    You can see, however, that the pilot light creates a potential safety problem. If the pilot light flame were to ever blow out, the gas would keep coming out of the pilot light tube. If this gas were to collect inside your house and then ignite, it would create an explosion. To solve this problem, the pilot light tube has a valve that cuts the gas to the pilot light in the event that it ever blows out.
    This valve is actually a fascinating little piece of equipment. It has to be able to sense whether that pilot light is lit or not, and for safety reasons it needs to be able to do that without requiring any outside electricity. How can you create a pilot light sensor that works reliably over the course of many years without any electricity?
    The answer to that question is ingenious. The way to do it is to use the heat of the pilot light flame to generate the electricity by using a thermocouple.
    Thermocouples generate electricity directly from heat. They take advantage of an electrical effect that occurs at junctions between different metals. For example, take two iron wires and one copper wire. Twist one end of the copper wire and one end of one of the iron wires together. Do the same with the other end of the copper wire and the other iron wire. If you heat one of the twisted junctions with a flame and attach the two free iron wires to a volt meter, you will be able to measure a voltage.
    In a pilot light, one of the junctions of a thermocouple is sitting in the pilot light's flame. The electricity that is created runs to a small electromagnetic valve and holds it open. If the pilot light blows out, the thermocouple quickly cools off. It stops generating electricity and the valve closes.
    To relight the pilot light, you have to push a button that opens the value manually. Then you light the pilot light and wait for the thermocouple to heat up (about 30 seconds). Once it is hot, the thermocouple is generating the electricity needed to hold the value open. Then you can let go of the button.
    The problem with pilot lights is that they waste a lot of gas. Therefore, most modern appliances do not have a pilot light. Instead, they use a piezoelectric spark to light the burner.
  • Rick Gelin
    Rick Gelin Aug 18, 2008
    You could probably retrofit a piezo electric ignitor in there ( similar to one used on a gas barbeque grill) however the likelyhood of having to continue reigniting that is normally pretty low. It should stay lit until an event happens .. water tank bursts and leaks water of something similar.. In all probability the spring loaded mechanism that opens the gas valve may have gotten stuck.. so now that it is operating normally.. it should probably be OK.. Glad you got it going..
Pentair mastertemp 250 NA. heater will not fire, no error codes. starts fine, gas flows, igniter heating but still will not fire. It has a new valve, gas pressure entering valve from new regulator is 8.35...
All appearances - No fuel to ignite!
evrything else looks good, proper gas pressure, proper volts at igniter, etc - it should ignite! If fuel present, heater should Fire!
make sure all valves are open.
Gas valve is ON
AND purge any air from gas line.
IMPORTANT ****. If you bled gas line, don't try to ignite for a few minutes. Allow gas to dissipate first, use a fan to help.
Mar 05, 2015 | Pentair Mastertemp 250 Natural Gas Pool...
1F ERROR CODE appears on Hayward model # h250PED2
Code Fault Diagnosis Step Remedy
None
Open FC3 and/or
F1 Fuses
1. Check for faulty Gas
Valve wiring.
Inspect Gas Valve wiring. Ensure insulation on wiring is not worn. If
OK, proceed to step 2.
2. Verify that Gas Valve is
not defective.
Mesure for resistance across Gas Valve terminals and between each
terminal and ground. If short exists, replace Gas Valve. If OK, proceed
to step 3.
3. Check for faulty Control
Module wiring.
Inspect Control Module wiring. Ensure insulation on wiring is not worn.
If OK proceed to step 4.
4. Control Module is
defective.
Replace Control Module.
Ignition Failure 1. Ensure gas supply shutoff
valves are open.
Ensure that main gas shutoff installed adjacent to heater is open. Ensure
that knob on gas valve inside unit is in ''on'' position. If OK, proceed to
step 2.
2. Check for low gas supply
pressure
Ensure inlet gas supply pressure is between the minimum and maximum
values indicated on rating plate. If OK, proceed to step 3.
3. Check for faulty flame
sense wiring or connection.
Inspect flame sense wiring. Ensure wire harness terminals are securely
fastened to flame sense and to control module. If OK, proceed to step 4.
4. Check for faulty gas valve
Inspect gas valve wiring. Ensure wire harness terminals are securely
fastened to spade terminals on gas valve. If OK, proceed to step 5.
5. Check for gas valve
failure or gas valve relay
failure.
1. Measure voltage across gas valve during trial for igintion. If 24VAC
is present and gas valve does not open, gas valve is defective. Replace
gas valve.
2. If 24VAC is not present, gas valve relay on control module is
defective. Replace control module.
6. Check for blockages in
gas orifices and burners
Inspect gas orifices for blockages which could prevent gas flow. Remove
and inspect burners for blockage
Jan 02, 2015 | Hayward H Series Electronic Ignition...
Water heater burner wont light
Problem is not thermocouple:
Thermocouple should be finger-tight plus 1/4 turn
Overtightening will short thermocouple against gas control valve, and solenoid switch will not open, and no gas will reach pilot once red button is released.
Tip of thermocouple has to sit in the pilot flame.
If pilot flame will stay on, then thermocouple is good.
Problem is not solenoid switch.
The gas control valve solenoid opens and closes gas supply to gas control valve.
On mechanical gas control valve, when you push down the red button to light pilot, then you are opening the solenoid and letting gas flow into gas control valve.
When heat is applied to thermocouple, a small electric current travels to gas control valve, and this causes solenoid to stay open.
If you extinguish pilot, then no current travels to gas control, and solenoid clicks off.
You can hear it click, and this is how you test it.
However, since you are getting gas to pilot light, then the solenoid is not the problem.
This leaves 4 possible problems:
1) Bad gas control valve thermostat.
http://waterheatertimer.org/pdf/How-to-replace-water-heater-gas-valve.pdf
2) Inadequate gas pressure. Call gas company.
3) Dirty combustion parts. Clean the burner with wire brush and water.
4) Clogged air intake on FV water heaters: Rheem FV gas water heaters have glass vial that will break if combustion is slowed by clogged air intake.
http://waterheatertimer.org/How-to-repair-Rheem-TRD.html
http://waterheatertimer.org/How-to-troubleshoot-gas-water-heater.html
Oct 06, 2012 | Rheem 40 Gallon FVR NATGAS Water Heater 6...
We have a 10 year old Rheem PVW50 Power Vented water heater that works on gas. The last couple of days it has been giving out problems. It will not maintain hot water in the tank. I restarted it and...
The igniter is glowing, but no gas ignites?
So either the gas is entering combustion chamber and not lighting because igniter is positioned incorrectly -or- no gas is entering combustion chamber because air in gas line or bad gas control valve thermostat or gas line is clogged.
When you 'restart' the water heater, somehow you are getting gas to the burner and it is igniting.
I'm not sure what the flame switch is. If the ECO was cut out, the gas control valve would not send power to the igniter and there would be no gas available for 'restart.'
I would adjust location of igniter, check if gas is entering combustion chamber, clean the gas line to the burner, and bleed gas line for air, but another suspect could be the gas control valve thermostat.
Identifying numbers are usually on side of gas valve.
Open following link to help identify gas valve:
http://waterheatertimer.org/How-to-adjust-temperature-on-water-heater.html#intelli
http://waterheatertimer.org/How-to-install-gas-water-heater.html#clean
Jul 02, 2011 | Rheem Water Heaters
Can a legacy heater #rnc-le30lttf be converted from lp gas to natural gas?
yes it will require the correct size orfice and spring in the valve something yo should be able to get from the manufacture... fairly easy to do as the orfice just unscrews and you instal the new one... the natural gas orfice will be a little smaller as it is lighter ... the spring in the valve is so that the diaphram opens and closes properly due to the different required pressure... good luck
\pleae vote.
Jan 03, 2011 | General Heating & Cooling
What would cause a furnace to not ignite all burners? York diamond 90 gas furnance - igniter glows, click, hear gas, first burner ignites but not the rest, flame sensor shuts it down. Any...
You could have plugged orfices in the line coming out of the gas valve. Next you could have a plugged gas regulator.The only way your going to find this out is to check gas pressure before the gas valve during a call for heat and then check it after the gas valve during a call for heat you could have a bad gas valve. Try this let me know what you find Thanks and please leave feedback
Dec 16, 2010 | Heating & Cooling
My minimax NT 400 heater will not ignite. The fan turns on. The start sequence proceeds as it should. Gas flow starts (I can smell it), but there is no ignition. The sequence repeats 3 times, and then the...
You may have low gas flow. This is tough to check but if you have a manometer you can check gas pre on the back side of the gas valve with heater off and then while it is trying to start. If you don't have a large enough meter or gas line this will often be the problem and give you the gas smell since it will feed gas but not enough to light.Good luck.
Apr 25, 2010 | Pentair Minimax NT Heater
I have a Rudd furnace model UGRA-04EMAES in heating cycle inducer makes pressure switch ignitor lites up no gas pressure i rplaced gas valve and board still no gas. Wat next?
Well first you want to verify that there is gas pressure coming from the connector. Turn off the valve and disconnect the connector. Then turn on the valve for 1 second and back off. You should get plenty of gas flow. Be careful doing this!. Then inspect the opening at the adapter to the control. There is a screen inside there. Make sure the screen is clear(not plugged with pipe dope,lint ect). When the igniter reaches the 2200 degrees you should hear the gas solenoid valve click open releasing gas. If you hear it click and no gas is released you will need to inspect the burner orfices. The orfice has an extremely small hole and there is a posibillity that they are plugged with debris. You will need to use a very small wire(like a tie strap) and insert it into each hole and see if there is anything in the orfice. If you do not hear the gas valve click then it might not be getting the signal it needs due to a weak igniter or flame rectification sensor. Does your furnace have a stand-by pilot that is lit by the hot surface igniter or does the igniter directly light the burner assembly?
Feb 20, 2010 | Heating & Cooling
Burners are bleeding gas causing rollout flames
multiple problems can be causing this: 1.burner orfice restricted 2. make up air 3. blower motor or relay defective 4.gas pressure to high 5. not enough gas pressure 6. restriction in gas line 7. defective gas valve 8. defective control or ignition module........recommend qualified tech. to look at
May 23, 2009 | Pitco Frialator 35C Deep Fryer
Heating & Cooling Logo
1,887 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen