Model # ckl49-il serial # 0506126514. This unit stopped working yesterday, noticed the fan on the outside compressor wan't turning, how do i test the capacitor and fan to see which one to replace?
  • 776 Answers
By far the most common problem with air conditions is the relay (known as a "contactor") by the air conditioner industry. This allows a low voltage (24 volts) electromagnet to turn on the 220 volt motor for fan and compressor. A replacement will generally cost about 50 to 75 dollars on Amazon.com.
Look for the wires entering the unit, The pair of wires entering the unit will go into a small (4" x 2" x 2") unit (the contactor). Another pair small diameter wires will go into the contactor (those are from the thermostat (or control panel of your furnace blower) and control the electromagnet switch.
The pair of output wires exit the unit and go to the compressor motor and fan.
You can check the output power by
1) Turning off the circuit breaker to the A/C
2) Unplugging the switch (must be a second switch within 3 feet of the A/C) near the house
3) opening up the outside panel on the A/C
4) Set voltage meter probes on the two output wires on the Contactor (make sure voltage meter is set to 220 volt AC range or higher)
5) turn on the outdoor switch
6) turn on the circuit breaker (if no body is near the unit and you can see the voltage meter without touching it)
7 check voltage meter to see that is says 220 volts AC
If not, then the contactor is bad and needs to be replaced.
A professional can usually do it for $200 including service call. I highly recommend calling a professional if you feel uncomfortable in any way about working with 220 volt systems. This voltage will kill you if you make a mistake!
-Mark
Posted on May 28, 2011
Btu rate model ckl49-il serial 0506103005
Built in June of 2005, it has a BTU rating of 49000 BTU or 4 tons. This is a 12 SEER, R-22 cooling only unit.
Aug 10, 2014 | Goodman Heating & Cooling
My 4 year old Ruud home a/c compressor stopped working. inside fan blows but compressor won't turn on...what can I do prior to calling the gas company who installed the unit...
Ruud parts warranty from factory is 5 years, the capacitor has possible gone out, it will be in the contol compartment on the out side unit and is a dual run capacitor that controls the compressor and fan motor. Recommend if capacitor is bad to replace entire capacitor. As Stated above the parts are under warranty if under five years old. To verify age the date code is in the serial number after the "F" **** week/year of manufacture. Also outside unit has independent power supply so check fuses if any and circuit breaker.
Aug 21, 2011 | Ruud UBHC Air Conditioner
My outside unit has just stopped running. I checked around the unit and there does not seem to be any noticable problems.
If the outside unit is not running - (no fan motor or no compressor) it's likely that you've blown a fuse or tripped a breaker.
That is where I'd start.
Aug 06, 2011 | Heating & Cooling
My Armstrong Concept 1200 stopped working yesterday (model EFC14MAA-1A, Serial # 6099F44101, 42000 BTUs). All breakers are OK. On the outside compressor unit, I can depress the relay and the fan and...
sounds like your problem is in the air handler. Sounds like the fan is not kicking on in the air handler this could be the board or the cap or fan motor you can run a micro farad test on the cap that goes to your evap motor be sure you take the leads off the cap and the mf are written on the cap itself. does the outside suction line which is the big line starting to freeze up? you can check your motor winding by running an ohms test across the motor winding. You do this by reading on the motor which wires goes to your start and run windings. You should get and ohms reading and if they are bad you will get infinity.
Jul 31, 2011 | Heating & Cooling
Outdoor fan will stop running and compressor overheats and shuts off. it wont come back on til u reset it at the thermostat. the outdoor unit has a new compressor and fan motor.
I realize the outdoor unit has a new compressor and fan motor - therefore - both those components should be ok - however - the fan motor 'should not' be going off - and the fact that it is going off is what is causing your compressor to overheat and shut off.
The reason the fan motor is going off is - it is bad (breaking down electrically) and is going off on the internal overload. If this is the case (a) the motor needs to be replaced or (b) it's possible that the fan capacitor needs replacing; but fan capacitors generally do not cause much problem, and when they do go bad they usually develop an obvious (to the eyes) bulge. If the capacitor has a bulge in it - I would surely change it out -and probably would (as a shot in the dark) anyway - since they are relatively cheap ($10-$15).
In your complaint you say that "the outdoor fan will stop running and compressor overheats and shuts off." If it happens 'exactly' that way then I'm betting your problem will be that the fan motor is defective as mentioned above, with an outside chance of the capacitor being defective, in which case if it isn't the capacitor - you will need a new fan motor. Note: outside fan motors are notorious for being fickle and it would not surprise me in the least to find a fairly new outside motor that is defective. I would check and see if you had any warranty on it.
All that being said - it is also possible that your outside unit has a 'high pressure cut-out switch,' although most units don't have them anymore, these days. However, if you have such a switch - it is possible (very likely) that it is shutting off the AC. Note: a high pressure cut-out switch will 'shut the entire outside unit off,' not just the fan motor. If that is what is happening then there's a good chance you have such a switch.
If it is happening that way, (the entire outside unit stops) then I would try 'washing the outside coil' really, really good and see if it will run ok afterwards.
Note: outside coils are sometimes difficult to get clean - sometimes requiring you to disassemble to some degree in order to make sure you get them clean.
Always, Always turn all power (including inside thermostat) OFF when washing the outside coil.
Jun 07, 2011 | Heating & Cooling
AC compressor wiil not turn on
You will have to find the contactor which is located in the outside unit. And check the voltage at the contactor, 26 v as this is the thermostat calling for the compressor to come on. You can also push in the contactor and see if the fan and compressor start. There should be an outside fuse box close to your condensing unit. Good luck
Jul 23, 2010 | Samsung AW1203B Air Conditioner
Kenmore Refrigerator - The refrigerator, which as purchased in 2002, stopped working yesterday. We had a cleaner clean the house - she pulled out the fridge, and cleaned under and inside fridge - we...
good checks,
one or two more
is the fan next to the compressor working
ar the coils by the comprssor clean
and one lasrt thing
there is a block on the compressor, unplug the unit pop that block off and shake it if it rattles there you go
Oct 04, 2009 | Refrigerators
I have a Goodman ckl49-1 airconditiong unit that
Check for burned wires at the outside unit and if the fan doesn't work could be the capacitor or the fan motor itself , i would try replacing the capacitor first is no more than $25.
Aug 27, 2009 | Heating & Cooling
Goodman ckl49-1 fan doesn't work after a really bad storm.
It is possible that the rain has washed out the bearings and the motor is frozen up. You may need to replace the motor. Also you don't need to put more oil in the compressor. The compressor comes with oil already sealed in it and it does not need to be changed or any more oil added to it.