Have a Pentair Mastertemp heater that will fire up and go on for a minute or two but then the temperature display will rapidly increase up to over 100 degrees and then the heater shuts down and displays an E05 code. Any suggestions?
4 Suggested Answers
  • 990 Answers
SOURCE: I have a Pentair Mastertemp 250 pool heater with
This is an ignition flame falure code. Could be you don't have gas getting to the pilot, no spark to ignite the pilot or your ignition is not reading the flame. Sorry to say but it's probally time to get the pool guy out to look at it. Good luck.
Posted on Apr 15, 2010
SOURCE: getting a E05 code on my Mastertemp pentair
I have same problem. Mechanic not sure what to do. May need a new board.
Posted on Jul 31, 2010
  • 94 Answers
SOURCE: Pentair mastertemp 200 will work for a while and
If you are firing, and then going off and getting an E05, your igniter is to blame. It may be glowing but it's getting weak. The diagnostic goes further but that is usually the fix. with inactivity, the igniter is always to blame. You really need to fire it off weekly to make it reliable.
Posted on Feb 25, 2011
Pentair mastertemp 250 NA. heater will not fire, no error codes. starts fine, gas flows, igniter heating but still will not fire. It has a new valve, gas pressure entering valve from new regulator is 8.35...
All appearances - No fuel to ignite!
evrything else looks good, proper gas pressure, proper volts at igniter, etc - it should ignite! If fuel present, heater should Fire!
make sure all valves are open.
Gas valve is ON
AND purge any air from gas line.
IMPORTANT ****. If you bled gas line, don't try to ignite for a few minutes. Allow gas to dissipate first, use a fan to help.
Mar 05, 2015 | Pentair Mastertemp 250 Natural Gas Pool...
Why mastertemp wont turn off
Does it stay fired or does the fan just run for a few minutes after you shut it off?
Jul 17, 2014 | Pentair 400k Natural Gas IID Cupro-Nickel...
How to reset pentair master temp to factory default
There is no reset on the mastertemp. All that changes is the temperature settings. DO NOT push the yellow button on the back of the cpu board.
Jun 02, 2014 | Pentair Mastertemp Heater
Pentair Pool Heating Rapidly Increases Temp on Panel then shuts off.
Check the Thermal Reg in the header and also make sure you have adequate water flow thru the heater, make sure your filters are clean and there are no external by-pass valves open.
If you remove the Thermal Reg in the header and the heaters seems to run fine the replace with a new one.
May 03, 2017 | Pentair Minimax NT Heater
Pentair MasterTemp 400 Stack Flu Sensor Reading Stuck
check gas pressure and for clogged burn tubes unit is overheating
May 12, 2012 | Pentair Mastertemp Pool & Spa Heater Dual...
R=8 128 Code on Pentair Mastertemp Heater what does it mean?
check manual bypass possible overheating or running out of gas
Apr 10, 2012 | Pentair Mastertemp Heater
What temperature does a pentair high limit switch trip
check gas pressure if ok check burner tubes over heating
Apr 09, 2012 | Pentair Mastertemp Heater
Heater cycles on / off
This could be a water flo problem. you need to chech to be sure your by-pass valve is closed down enough to force water threw heater, There is a internal by-pass that could be a problem also, or a bad pressure switch. If the by-pass isn't the problem then you should check these also.
Jul 25, 2010 | Pentair 460736 Master Temp Pool Heater...
Pentair matertemp 400,000 BTU heater cycles on & off
My pentair matertemp 400,000 BTU natural gas heater cycles on and off before reaching desired temperature. I completely cleaned the DE filter and flow should not be an issue. When running the spa the pressure is 25. When running the cleaning system (polaris pop ups) the pressure is 30. Burner fires for 80 seconds then shuts off, reignites after 53 ceconds.Any tips on what might be the issue with the heater
Apr 04, 2010 | Pentair Mastertemp Pool & Spa Heater Dual...
Pentair Mastertemp Heater Logo
101 people viewed this question
Top Pentair Pool & Spa Experts
Jay Finke
Jay Finke
Jeffrey Turcotte
Jeffrey Turcotte
Are you a Pentair Pool and Spa Expert? Answer questions, earn points and help others