Question about Hayward H Series Millivolt 250,000 Btu Pool Heater H2501
Hayward H2501, pilot is lit, but burners will not turn on. Pressure in filter is at 15 PSI. Checked the connections and they are ok
  • 116 Answers
SOURCE: Hayward H250 (millivolt) pilot won't stay lit
make sure the flame hits the thermo couple if so then replace it lows has them in the water heater section thermo couple gets hot makes millivolt signal then opens gas valve
Posted on May 09, 2009
  • 139 Answers
SOURCE: hayward heater not staying lit
possibly poor pilot adjustment or insuficient mv output from thermopile
Posted on Jun 19, 2009
  • 139 Answers
SOURCE: Hayward Comfortzone pool heater pilot will stay
check for continuity at all control and safety components,i.e. press switch,high limits,thermostat,on/off switch and flame roll out switch
Posted on Jun 21, 2009
  • 12 Answers
SOURCE: hayward h250ed1 heater wont stay lit
Try cleaning your filter if dirty there will not be enough flow to llet heater fire. If filters clean you can try jumping the pressure switch.
Posted on Jun 25, 2009
  • 9 Answers
SOURCE: Hayward 250 heater won't fire up
Check the control circuit, specifically the pressure switch, for continuity with an ohm meter....any reading over 2 ohms needs to be investigated
Posted on Jun 28, 2009
My Hayward h250 Millivolt heater won't stay on. If I jump the "TH" connections I can get the main burners to come on, once I remove the jumper, the main flame goes out. I replaced the pilot assembly and...
you prolly have an electrical short somewhere. follow the circuit and if any safety is getting around 200-250 dc millivolts then theres the problem. otherwise you have an open safety switch, or tsta controls
Aug 07, 2013 | Hayward H Series Millivolt 250,000 Btu...
I have a h150 pool heater. when you light the pilot it would go on but it would turn off once the valve was in the on position. service tech came to the house and changed the thermocouple. it finally...
Having multiple issues with a milli-volt heater very common and can be expensive to fix at times. Start by cleaning EVERY connection in the safety circuit and the pilot circuit. If you have a milli-volt meter that would help a lot.
Jul 13, 2017 | Hayward H Series Millivolt 250,000 Btu...
Hayward mod h1501 light pilot it stays lit turn temp up and it run,s but when we turn it down and shut it off the pilot go,s out and we have to lite it every time we use it,s out. a new gas valve in will...
Check the burner tube closest to the pilot side of the burner tray. Is it burning a nice blue like all the rest? If it is not, clean out the jet on the manifold in front of the tube.
If it is ok, can you get a millivolt reading off the generator (thermocouple)? If so, get the reading with just the pilot on it, then with the burner load. Finally, watch that reading as the burners run for a while to be sure it climbs.
The only other thing I can think of would be to get manometer readings to verify gas pressures before and after the valve.
Jul 30, 2009 | Hayward H Series Millivolt 250,000 Btu...
Jun 27, 2009 | Hayward H Series Millivolt 250,000 Btu...
My Hayward pool 350000 heater will light and stay lit and heat the pool for a while, but will just shut off including the pilot light. When I re-light it it works for a while again and then shuts off...
Sounds like the pilot assy needs to be replaced. It has 2 functions one is to light the main burner but also to let the system know that the burner is lit. If it thinks the burners are not lit it turns the gas off
Jun 23, 2009 | Hayward H Series Millivolt 250,000 Btu...
Hayward heater not staying lit
Jun 19, 2009 | Hayward H Series Millivolt 250,000 Btu...
Pool heater will not flame
sounds like a flame rectification probelm...look in the manual for solutions
May 30, 2009 | Hayward H Series Millivolt 250,000 Btu...
May 08, 2009 | Hayward H Series Millivolt 250,000 Btu...
Heater won't stay lit
On your main gas manifold you have orfaces that screw into it at each burner. Remove these and see if their are small spider webs in them. They will look like little lint balls. They can keep your main burner from getting gas and in turn keep the heater from sensing flame. The pilot lights and the heater starts but no flame at the main will shut it rite down. See if this helps.