No hot Water after electric power surge.Califont not supplying hot water.
I would recommend you check your circut breaker frst. It should be in the on position. Reset it if it's off. If you still don't have hot water water contact a licened repair technician. The heating element may be burnt out.
Posted on May 23, 2011
I have the White Rodgers Intellivent on an OA Smith propane hot water tank, but cannot get any lights on the controller, even after shutting off the power and then back on. The plug is hot and the uni
The plug is HOT?
Unplug immediately.
Is the outlet hot? Is the circuit breaker hot. Have you had a surge event or nearby lightning strike?
Do you have electrical issues in home?
Add a comment.
Test outlet for correct polarity, and test for overvoltage and short.
The intellivent is very susceptible to surge and will stop functioning.
http://waterheatertimer.org/pdf/How-to-replace-water-heater-gas-valve.pdf
Copy following link for troubleshoot by type of gas control valve.
Including intellivent service manual.
http://waterheatertimer.org/How-to-troubleshoot-gas-water-heater.html#intellivent
Sep 09, 2012 | RTO W4 A.O Smith Gas Hot Water Heater...
Hi, I have a Rheem water tankless heater and there was a storm lastnight so suddendly I have no hot water. What can It be?
1) All tankless water heaters require voltage to operate electronic sensors and circuit board.
This is true for gas and electric tankless.
2) Check that circuit breaker is not tripped. Push circuit breaker all the way one direction and then all the way back other direction.
3) There are fuses located inside the tankless unit, so check your manual for location of each fuse.
Manual is filled with useful maintenance and troubleshooting steps.
4) Before calling service technician, open following link for troubleshoot resources including manuals, Rheem on-line chat, and useful links for maintaining tankless water heater.
http://waterheatertimer.org/Troubleshoot-Rheem-Tankless-water-heater.html
5) If you had nearby lightning strike, I don't know if your tankless is protected from surge.
I recommend whole-house surge protector for tank and tankless water heater electronics, and household circuits. Surge protection is installed in main breaker box, and is replaced after each surge event. Separate protection needed for co-ax TV satellite, co-ax surge protection can be found on some ordinary power strips.
http://waterheatertimer.org/Intermatic-trippers-and-parts.html#surge
Apr 11, 2011 | Rheem Tankless Hot Water Heater...
I need to know how to install a cellanoid in my Whirlpool Duet washer Mod # GHW9150PW4 is there a place to get the instructions?
Are you meaning the Water Inlet Solenoid Valve??????
If yes .... you need to know if your W/P Duet GHW9150P Front Load Washer really has a bad Water Inlet Solenoid Valve for the Hot and Cold water. This valve is where the Hot and Cold water hoses connect to the rear of your washer on the upper top left side in the rear as you are facing the washer. In my opinion it is highly unlikely that your Water Inlet Solenoid Valve is bad....but it is possible. Sometimes the filter screen in the inlet(s) of the Hot & Cold water valve can be stopped up with dirt, sediments, etc. If you turn off the water faucets and remove the Hot & Cold water hoses from the washing machine... you will be able to see the screens...if they are stopped up you can remove them with a small screw driver and clean them and reinstall them.
Hook up your hoses and turn on your water supply Hot and Cold faucets.
Here is a quick test procedure that you can do to verify the operation of the Water Inlet Solenoid Valve.
Verify that your water hoses are hooked up and the water faucets (Hot & Cold) are turned on.
Unplug the washer's 120Volt AC power supply cord from the electrical plug on the wall.
(1) Remove the top cover...There will be three screws on rear area of the cover: Left - Middle -Right.
(2) Once the top cover is removed...you will be able to see the Water Inlet Solenoid Valve...just follow the Hot & Cold water hoses from the wall to your washer. Usually the water inlet solenoid has a blue plastic housing assembly with (2) separate push-on or pull-off quick disconnect electrical connectors. One connector pair provides 120volt AC to the Hot water solenoid and the other connector pair provides the 120volt AC to the Cold water solenoid.
(3) Remove the push on or pull off quick disconnect electrical connector to one of the water inlet solenoids..It does not matter which one at this point in time.
(4) You will need an electrical 120v AC Test Cord. You can make this from an old lamp AC power cord or and old 120v AC Extension Cord. You will need two alligator test jumpers or leads (Radio Shack has them). The end of the test cord that plugs into wall is not to be modified. The other end of the test cord will have to be modified in order to conduct this testing. Strip back the insulation to reveal the two leads that will carry the 120v AC power. You should have one black lead (120v AC HOT) and one white lead (120v AC Neutral). Connect (1) alligator test lead to the black lead and insulate with electrical tape as necessary and connect (1) alligator test lead to the white lead and insulate with electrical tape as necessary You now have your 120v AC Test Cord ready. If you have a VOM test meter..you can connect the VOM meter to the two remaining alligator test leads. Have your VOM test meter set for AC Volts and on a scale that will measure 120v AC. Plug in your test cord to the 120V AC wall power. If everything is OK your meter should read approximately 120 Volts AC.
(5) Unplug your 120v AC Test Cord from the wall power.
(6) Connect your 120v AC Test Cord to your Water Inlet Solenoid Valve electrical terminals.
See Step (3).
(7) Plug your 120v AC Test Cord into wall power. If the water solenoid valve is good you should hear water surging thru the water solenoid valve. If you do not hear the water running thru the valve you can verify if the 120v AC is getting to the valve with your VOM. It should read 120v AC. If it does read 120Volts AC at the terminals of the valve and you do not hear the water then the valve is probably defective: Either stuck shut and won't open or the solenoid coil is open (Bad).
(8) Unplug your 120v AC Test Cord from wall power.
(9) Disconnect your (2) alligator test leads from the solenoid valve and re-install the electrical push on connectors that was disconnected in Step (3)
(10) You can now repeat this test on the other side of the Water Solenoid Valve (See Step 3).
(11) If both sides of the Water Solenoid Valve check out good...then your Water Inlet Solenoid Valve is good. If it does not check out then replace it.
(12) If your Water Inlet Solenoid Valve is good...then ....unfortunately, there is a good chance that the CCU module is bad. The CCU module is in effect a computer control unit and controls the overall operation of the washer. The CCU module will cost approximately $150.00
Mar 11, 2011 | Whirlpool Duet GHW9150P Front Load Washer
Will not heat we replaced both elements but still no hot water rheem model no.82v522marlene we suspect we had a power surge during last storm because the furnace went out also at the same time
Hi I suspect your thermostat will have also been damaged if you had a surge I always replace thermostats at the same time as the elements
Also check the wiring as sometimes surges can melt the copper core of the wiring, but be careful always turn off the power first before any electrical works!
Mar 06, 2011 | Rheem 50 GAL ELEC TALL Water Heater 6YR SC...
I have no codes, no hot water, gas and electric all ok,
Double check your incoming power supply to the heaters main control panel with a voltmeter.
Inspect the power supply inlet fuses and replace if necessary.
Remove and clean the inlet water supply filter; impeded water flow will not activate the flow switch.
Measure the water flow from each hot-water faucet. You need at least .75 gallons a minute.
Inspect the water flow control turbine. Mineral buildup on the blades will stop it from spinning.
If this is a new installation, make sure that the hot and cold-water lines are not crossed.
Test your plumbing for a cross connection. Turn off the water supply to you heater. Open all the hot
water faucets. If you get a steady steam of water from any of them, you have a cross connection that needs to be remedied. When all else fails, Rheem's customer support team is great. They have always help me with the most technical questions, even on older and outdated products.
Dec 11, 2010 | Rheem Tankless Hot Water Heater...
If there is an electricity failure how can we have a hot shower
Easy answer is you cant on these units. These tankless units store no hot water and need a 240V power supply to operate.
However!
In some areas in far north Queensland I came up with a back up power unit (I used to work for Rinnai who make similar units). These were for remote units that used battery lighting and just wanted a bit of hot water for remote workers.
Basically you need a spare car batttery and an electrical inverter or a back up petrol generator. These hot water units only use a very small amount of electrical power even when that are operating. I had a guy run the hot water for nearly two weeks on a car battery and inverter after cycone Larry hit Innisfail in North Queensland.
Depends how often you get power losses as to how much money you want to spend to cover yourself (99.9999% don't bother with no real hassles).
Jul 23, 2010 | Rheem Tankless Hot Water Heater...
Hot water connected but does not fill into the drum? The machine will provide us with a cold wash but on the warm and hot settings the hot water dies not pull through the connection
Turn off the water valves which supply the water to washer hoses. Switch the hot and cold water supply hoses and tighten. Turn the water valves back on and try to run a wash cycle using cold. If hot water only is entering the wash tub the water supply is ok. If this is the case you can unplug the washer and turn off the water valves. Remove the washer back cover and follow the water connection for the hot water. The water solenoid valve will have two electrical wires connected to it. Interchange the hot water solenoid wires with the cold water solenoid connection. Connect the water supply hoses hot to hot and cold to cold then plug the unit then test the washer on the cold wash. If the problem persists it could be a water hose restriction or the timer circuit could be defective. If you have hot water at the normal pressure purchase a new hot water solenoid valve. With the electrical cord unplugged be sure to restore the correct wire connections on the hot and cold water solenoid. To replace the hot water solenoid remove the hose clamp and hose to replace the old valve. Connect the unit to the water and electrical outlet. Turn on the water and test the unit for leaks being careful not to touch any electrical and moving parts. If all checks ok and the correct temperature work, unplug the unit and reassemble.
Jun 21, 2010 | Admiral AW22 Top Load Washer
Low water pressure in gas califont
by contacting the manufacture they can tell you how to do that.
Apr 12, 2010 | Jet Flo 04325143A Marine Heavy Duty Water...
The motor keeps surging
If there's a lot of sediment in your water supply, there's a chance that sediment has gummed up the pressure switches. I'm assuming it has a full power switch and high power switch. It runs on full power until a pressure switch is satisfied, and runs on low power to slowly build the pressure back up, at which a second switch is satisfied from the pressure and turns the motor off. These things are not easy to work on, and are made of metal probably too fragile to try any chemicals. You should probably contact the manufacturer.
Sep 19, 2009 | Karcher 1750 psi Electric Pressure Washer