Where is the correct place for the thermostat wire to be placed at?
    Genius:
  • 1,044 Answers
Near the cooling coils along side fins.
Posted on May 23, 2011
  • 43,501 Answers
Here is a list of each common terminal and what their commonly used for. Alsolisted is what colors are commonly used. NEVER ASSUME these are what youhave. Verify all your wires by following each to each piece of equipment. Thiswill help you to be able to match your equipment with the terminal.
Here is the rest of the tip that I wrote...
Thermostat Wiring and Terminal Designations
heatman101
Honeywell thermostat
The wiring is correct but you have a programmable thermostat that needs to have a program to operate. The manual for this particular stat is straight forward and uncomplicated. Enter the times and functions with the right button and up/down arrows then press "DONE" (Left Button) to get it started. Hope this helped. Roger
Jan 30, 2014 | Heating & Cooling
Tip
Thermostat installation
1. Make sure you buy the correct thermostat for your application. 2. Always turn off power to unit before installation. You will blow fuse or a transformer.3. Mark all wires when you take them loose from old thermostat.4. On some thermostats you will have RH and RC you must place jumper between them to get heat and cool to work.....
on Mar 25, 2010 | Heating & Cooling
I HAVE A WHIRLPOOL ACCUBAKE RANGE, THE OVEN AND BROILER DOES NOT WORK. CHANGED SPARK MODULE AND STILL DOESN'T WORK. ANY SOLUTIONS?????
There are four other things to check on the oven, you will have to run a test on the broiler element, oven thermostat, selector switch and the oven cycling relay.
To test the broiler element, To access the broil element located on the roof of the oven cavity, first open the oven and remove the oven racks. Remove the screws that secure the element to the oven, remove the holding brackets from the element and slide the element forward.
There is normally a small amount of excess wiring attached to the terminals on the element that allow a little room for maneuverability (you may have to tilt the element to get the terminals through the holes). Look for loose or disconnected wires and if there is no sign of burning; reconnect the wiring to the back of the terminal. If a terminal end is damaged, replace it with a terminal end designed specifically for oven use only.
To test the broil element, remove the wires from the broil element terminals by removing the screws from the terminal or pulling the wires off the broil element terminal. Remember to label the wires for reinstallation.
Visually check the entire element for signs of burn.
Test the broiler element for continuity. Using the ohmmeter, set the range scale on R x 1 and place the probes on the element terminals. There should be continuity, with readings ranging from 19 to 115 ohms, however readings will vary from manufacturer to manufacturer and according to unit size and the wattage, be sure to check your manual for the manufacturer's specifications.
If there are any signs of element burning, or if there is no continuity, replace the element.
To test for a grounded broil element, place one probe on the element outer surface and the other on the element terminal as in the ground test for the baking element. If continuity exists, the element has shorted and should be replaced. Be sure to test both terminals.
To test a dual broil element, remove the wires from their terminals. Using the ohmmeter, set the range on R x 1. Place the probes on terminals A and C to check for continuity, followed by terminals B and C. To test for a grounded element, place one probe on the element outer surface. With the other probe, touch terminal A, followed by B and then C. If continuity exists, the element has shorted and should be replaced.
To install a new broil element, simply reverse the disassembly procedures and reassemble, being sure to follow the wiring diagram and install the wires to the correct terminals
To test the oven thermostat: Access the oven thermostat, which is located in different places depending on the make and model: On freestanding ranges, access the thermostat by removing the screws that hold the back panel in place at both ends. On models with front-loading controls, remove the panel and tilt it for access. Be careful not to let the wires disconnect from their components. Some built-in models have a removable backsplash. Lift the backsplash, rest it on the cook top and remove the screws from the backsplash, which holds the rear panel. On wall ovens or eye-level ranges, access the control panel by opening the door and removing the screws that secure it. The screws may be under the exhaust hood or below the control panel. If the control panel is hinged, simply tilt it towards you. On some models both the rear and front control panels must be removed. The screws may be found on the trim and occasionally the trim must be removed.
When testing the thermostat switch contacts for continuity, refer to the wiring diagram and remove only those wires being tested - and only one pair at a time. Test switch contact terminals as per your wiring diagram. If the switch lacks continuity at any of the contact terminal points then the entire thermostat switch needs to be replaced. Adjusting the thermostat: Test the oven temperature by placing the tester in the oven's center and leaving it for 30 minutes at 350 degrees. Record the minimum and maximum temperatures of three cycles, then add those figures together, divide the result by six and you have the oven's average temperature.
If the average temperature is more than 25 degrees off, try calibrating the thermostat by following your appliance manual instructions for thermostat calibration.
Normally, thermostats are calibrated by pulling the oven's thermostat knob off, turning the knob over and adjusting the calibration ring on the back. If your oven doesn't have a calibration ring you may need to replace the thermostat.
To remove the thermostat: Disconnect the capillary tube and push it through the back oven wall, being careful not to break the flammable capillary tube wire. Remove the screws that secure the thermostat to the control panel and gently pull the thermostat out, leaving the wires in place. To install a new thermostat, reverse the disassembly procedures (Step 7 above), transferring the wires individually from the old unit to the new.
To test the selector switch: In order to gain access to the oven selector dial, first move the range away from the wall and remove the back cover panel by undoing the retaining screws. This will expose the back of the oven selector dial. Note: There are many styles of ranges. If this does not describe your range, refer to your owner's manual for instructions on gaining access to your oven selector dial. Now you can begin to test each pair of switch contacts for continuity with your VOM. Using the ohmmeter function, set the range scale to R x 1, and touch one test lead to each terminal of the switch contacts to be tested. There will be several pairs of contacts, one pair for each setting (eg. broil, bake, etc.). Refer carefully to your wiring diagram (often placed on the inside of the access panel) when testing. It is a good idea to label the wires as you test and only remove one pair of wires at a time. If there is no continuity between any pair of contacts, the switch is defective and must be replaced. To install a new oven selector dial switch, remove the old switch from the control panel by undoing the nut or screws holding the switch in place, leaving all wires attached. Transfer the wires one at a time from the old switch to the correct terminal of the new switch. Check your wiring diagram to make sure all wires are on the correct terminals. Now mount the new switch to the back of the control panel and replace the cover.
To test the oven cycling relay: In order to gain access to the oven cycling relay, refer to your owner's manual. Removing the back panel of the range accesses most relays, but some ranges locate the relay under the oven compartment where the utility drawer is usually located. Now you can test the relay using your VOM. First, label each wire attached to the relay and remove them from the relay terminals. Using your VOM's ohmmeter function, set the range to R x 1 and touch one test lead to the terminal marked L and the other test lead to terminal H2. There should be NO continuity. Next, test the terminals marked H1 and H2. Again, there should be NO continuity. Finally, test the S and R terminals. Continuity should exist between these two terminals. If your relay does not pass all these tests, it is defective and should be replaced. To remove the relay, undo the two screws securing it to the range and replace with the correct new relay. Refer to your wiring diagram and labeled wires to ensure that the wires are on the correct terminals. Now replace the back panel or drawer and test the oven.
Hope this was helpful to you. Thanks for using fixya.
Jan 27, 2011 | Whirlpool Kitchen Ranges
The oven does not heat, the fan works but no heat. The amber panel light on the front doesn't come on either.
There is a faulty component inside the unit that is why it is not turning on. The power is working fine, because it is the power that operates the fan. Therefore the panel light that is not turning on is as a result of a bad component. In order to be sure what the faulty component is i will advice that you run a test on the oven, test the oven selector switch, to test the switch,
  1. There are many styles of ranges. If this does not describe your range, refer to your owner's manual for instructions on gaining access to your oven selector dial.
  2. Now you can begin to test each pair of switch contacts for continuity with your VOM. Using the ohmmeter function, set the range scale to R x 1, and touch one test lead to each terminal of the switch contacts to be tested.
  3. There will be several pairs of contacts, one pair for each setting (eg. broil, bake, etc.). Refer carefully to your wiring diagram (often placed on the inside of the access panel) when testing. It is a good idea to label the wires as you test and only remove one pair of wires at a time. If there is no continuity between any pair of contacts, the switch is defective and must be replaced.
  1. Remove the old switch from the control panel by undoing the nut or screws holding the switch in place, leaving all wires attached.
  2. Transfer the wires one at a time from the old switch to the correct terminal of the new switch.
  3. Check your wiring diagram to make sure all wires are on the correct terminals.
  4. Now mount the new switch to the back of the control panel and replace the cover.
Also you need to test the thermostat of the oven to be sure the problem is not from there,
  1. Access the oven thermostat, which is located in different places depending on the make and model: On freestanding ranges, access the thermostat by removing the screws that hold the back panel in place at both ends. On models with front-loading controls, remove the panel and tilt it for access. Be careful not to let the wires disconnect from their components. Some built-in models have a removable back splash. Lift the backsplash, rest it on the cook top and remove the screws from the back splash, which holds the rear panel. On wall ovens or eye-level ranges, access the control panel by opening the door and removing the screws that secure it. The screws may be under the exhaust hood or below the control panel. If the control panel is hinged, simply tilt it towards you. On some models both the rear and front control panels must be removed. The screws may be found on the trim and occasionally the trim must be removed.
  2. When testing the thermostat switch contacts for continuity, refer to the wiring diagram and remove only those wires being tested - and only one pair at a time. Test switch contact terminals as per your wiring diagram. If the switch lacks continuity at any of the contact terminal points then the entire thermostat switch needs to be replaced.
  3. Adjusting the thermostat: Test the oven temperature by placing the tester in the oven's center and leaving it for 30 minutes at 350 degrees. Record the minimum and maximum temperatures of three cycles, then add those figures together, divide the result by six and you have the oven's average temperature. If the average temperature is more than 25 degrees off, try calibrating the thermostat by following your appliance manual instructions for thermostat calibration.
  4. Normally, thermostats are calibrated by pulling the oven's thermostat knob off, turning the knob over and adjusting the calibration ring on the back. If your oven doesn't have a calibration ring you may need to replace the thermostat.
To replace the thermostat of the oven, please follow the steps below:
  1. Disconnect the capillary tube and push it through the back oven wall, being careful not to break the flammable capillary tube wire.
  2. Remove the screws that secure the thermostat to the control panel and gently pull the thermostat out, leaving the wires in place.
  1. Reverse the disassembly procedures,
  2. Transfer the wires individually from the old unit to the new.
Hope this helped. Thank you for using fixya.
Jan 21, 2011 | Explorer Appliances B196 ELECTRIC Kitchen...
I removed the wires from the old thermostat before I realized that I needed to label them so that they could be placed in the proper place on the new thermostat.
Heating, red wire to R terminal and white wire to W terminal. Fan, green wire to G terminal. A/C, yellow wire to Y terminal, there may be a jumper from R1 to R2 terminals. If you have a blue wire it should go to C terminal.
Oct 18, 2009 | Honeywell Electronic Programmable...
I have installed a Honeywell CT8775C, when I put it on the heat the A/C goes on!! I have checked my wiring and everything looks right? what should I do to correct it.
You should have a minimum of four thermostet wires. The red wire goes on the R terminal. White wire on the W terminal. Green wire on the G terminal. Place the yellow wire on the Y terminal. In most cases NO other terminals are used...... IF YOU DO NOT HAVE A YELLOW WIRE...... place the blue wire on the Y terminal. This should hopefully fix it. IF NOT....See if the thermostat has a RH and a RC terminal. If so I'll bet that you put the red wire on RC ternimal. this is for airconditioning ONLY. The RH terminal is for heating ONLY. Put a small jumper wire that will connect RH & RC. Then this should solve your problem.
Mar 03, 2009 | Honeywell CT87B ROUND HEATING&COOLING...
Replacing a non-programable thermostat for electric baseboard heater with model CT410B. This is a 4 wire thermostat replacement for a previous 2 wire. Directions indicate that I can do this. I connect...
If you take thermostrat back off and connect the wires together will baseboard heater get hot. If not you may have bad heater. If it gets hot your new tstat may be bad. The way you have it wired is correct. Most line voltage tstats have a ground screw. Your 's may not but will work without one .
Jan 23, 2009 | Heating & Cooling
Im changing an old honeywell thermostat with a new honeywell thermostat. the old on has wires 4 wires connected to 4 screws C,R,G,W but the new thermostat has a place where the wires go which are...
Yes, I believe that you will be fine. If the original wiring is correct then I have listed the basic wiring below. As always read the directions and make sure the wiring matches your system.
Red wire = Rh (24v power, should have an exsisting jumper to RC)
White wire = W (heat mode)
Yellow (or sometimes blue) wire = Y (A/C)
Green wire = G (Indoor Fan)
Jul 03, 2008 | Honeywell Heating & Cooling
Heating & Cooling Logo
20 people viewed this question
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen