Mitsubishi ms12tn mini split

It will run fine for a few minutes and then the suction pressure will drop into a vacum and the head pressure drops 50 p.s.i. . The compressor gets so hot you cant touch it in a very short time.

Posted by on

1 Answer

  • Level 2:

    An expert who has achieved level 2 by getting 100 points

    MVP:

    An expert that gotĀ 5 achievements.

    Governor:

    An expert whose answer gotĀ voted for 20 times.

    Scholar:

    An expert who has written 20 answers of more than 400 characters.

  • Expert
  • 67 Answers

Heya Harmlhs,
If the system is going into a vaccum that shows the compressor is working I would say it is either short of gas or it is a problem with the RCD. If the compressor is getting really hot i would say that it would short of gas and it is not best to use it untill a licenced person comes and looks at it before the compressor is seriously damaged.

Posted on Apr 04, 2009

Add Your Answer

Uploading: 0%

my-video-file.mp4

Complete. Click "Add" to insert your video. Add

×

Loading...
Loading...

Related Questions:

1 Answer

My Panasonic mid wall split short cycles. the indoor pcb relay makes and breaks too often. suction pressure drops to 100kpa at startup. when attempting to charge it cycles of then comes on after a few...


You will need to check the head pressure, condensing temperature, sub cooling and superheat to determine this, but yes sounds as so or restricted.

Oct 09, 2013 | Air Conditioners

1 Answer

TRIED TO GET SUPPER HEAT MEASSURMENT AFTER THAWING OUT THE EVAP. OUT SIDE TEMP WAS 95 THE SUCTION LINE TEMP 77 AND THE SUCTION PRESSURE WAS 42 AT THE GAUAGE. BUT THE SUCTION PRESSURE WOULD DROP PRESSURE...


You have to let the system run for a while for the suction pressure to stabilize, if the metering device is a TXV pressure will rise and fall as the valve opens and closes. If this is R22 you need to get the suction pressure up

Jun 23, 2011 | Air Conditioners

1 Answer

Pressure readings


the metering device is in the outside unit on mini splits that is why the liquid line sweats. pressure reading depend on load high load high readings i would shoot for arount a 40f suction saturation temp

Jun 26, 2010 | Mitsubishi Mr. Slim MXZ30TN Air...

1 Answer

Water flowing inside the room thru indoor unit


blocked drain
low gas charge
cracked drain pan in head unit

Apr 21, 2010 | LG LS-K1830CL Cool Mini Split Air...

1 Answer

Head pressure good low pressure good, but not cooling


r we talking about a split system? begin pump down by closing the high side then watch as the suction drops to zero or very close u should here the compressor loading. turn off the compressor open low pressure port and see if the refrig. is being held by the valves. if the refrig flows back to air handler thru suction in a/c mode most lkely compressor needs to b replaced due to bad valves. also whats the twmp drop across the coil

Jan 28, 2010 | Carrier 38CKC036 Air Conditioner

1 Answer

Hi,mitsubishi ms12tn mini split ,when i put on the


There is small PCB in the AC, this PCB is malfuctioning also there is automatic ON /OFF switch Check whether ti is working properly or not.

Oct 02, 2009 | Mitsubishi MS12TN Air Conditioner

1 Answer

Bon-Air mini split 1.5 ton, suction and discharge pressures are equal. discharge valve has ice on it. and the suction and compressor are very hot.


Sorry to sat but the tech has no idea what he is doing. The metering device is in the discharge valve, making that line a low pressure, not high. If the "suction" line is hotthen it is running in heat mode.

Jun 25, 2009 | LG LS-L1210CL Mini Split Air Conditioner

1 Answer

Sharp split system, cutting out


If this is running in A/C mode, then I bet you have a low refrigerant charge. The compressor is dropping out on low suction pressure if it's cutting in and out every 5-10 minutes or so. If it takes hours, then it's likely a different problem.

Reply back and I can help you (been in that business for over 30 years.).

Feb 01, 2009 | Air Conditioners

1 Answer

Extremely high head and suction pressures


disconnect the blower and turn on the ac.see if the coil frosts evenly.when you had the system open,you should have changed the liquid line drier.

Jul 29, 2008 | Air Conditioners

2 Answers

No cooling, suction pressure reads vacuum Split AC


The unit is restricted, reprocess the system, flush and vacuum it thoroughly.

Mar 24, 2008 | Sanyo 24KS62R Cool Mini Split Air...

Not finding what you are looking for?
Mitsubishi MS12TN Air Conditioner Logo

Related Topics:

165 people viewed this question

Ask a Question

Usually answered in minutes!

Top Mitsubishi Air Conditioners Experts

D. E. Hev

Level 3 Expert

1059 Answers

yadayada
yadayada

Level 3 Expert

61249 Answers

MightyMikeJr

Level 3 Expert

347 Answers

Are you a Mitsubishi Air Conditioner Expert? Answer questions, earn points and help others

Answer questions

Manuals & User Guides

Loading...