Question about Honeywell Heating & Cooling
I have a Honeywell 8124A,B,C. model aquastat. The diagram does not show zone valves connecting to this model. It only shows additional circulators. I currently have 2 zones. Can I use zone valves on the 8124A,B,C model aquastat? Do I need to purchase another control box?
  • 17 Answers
SOURCE: I get the error code E2 It only shows 2 zones on my 4 zone syst
I reset the circuit breaker to the panel and everything is good now.
Posted on Jun 25, 2009
senor8
  • 73 Answers
SOURCE: need to wire a zone control for a closed system with a circulator
Tankless water heaters for domestic use fire whenever there is water flow. As long as the pump flow rate exceeds the minimum flow rate of the appliance, the heaters hould fire (the return temperature needs to be less than the set temperature as well). Boiler systems will typically require a thermostatic signal (call for heat) and water flow before they will fire. Tankless heaters are designed for residential use and only require pump flow to fire.
Posted on Aug 18, 2009
rylee_smith
  • 8619 Answers
SOURCE: My Honeywell EMM-3 zone controller
Hi
Thanks for using FixYa. Perofrm this test--
Connect DATS Sensor to EMM-3 (optional).
a. Reconnect power to EMM-3.
b. If system is in Purge mode, press PURGE OVERRIDE on EMM3.
c. Verify SYSTEM LED is no longer flashing. This confirms proper DATS operation. (Flashing occurs in Idle and Fan modes only.)
Also see page# 9 & 10 from this link--
Please do accept the solution if the issue is resolved or else revert for further assistance.
Thanks
Rylee
Posted on Aug 28, 2009
ryanmalin
  • 40 Answers
SOURCE: lennox electric furnace wont cool house. model
check the outside unit (condenser) see if the fan and compressor are running. the compressor humms and you should be able to hear it. if it is running check the inside unit's coil to see if it is frozen or dirty. if it is frozen or extremely dirty then you have restricted airflow to the inside unit. Sometimes checking the coil is near impossible, i use an inspection mirror and headlight flashlight, then i wedge a chisel under the front of the drainpan (CAREFULLY! its plastic usually) so i can get my mirror in there and see whats up. On a furnace the coil will be on the very top and have 2 copper pipes running into it with one of them being insulated. hey also a dirty filter or prefilter can cause freezing.
Posted on Oct 10, 2009
  • 118 Answers
SOURCE: I want to output blu ray dvd output in zone 2. Denon AV 4308
correct. in order to enjoy your digital sources in any zone2 configuration, an additional connection has to be made to the analog input from and for each of these devices.
some receivers wont allow internal xm, sirius and ipods to work in zone2 because they are input to the digital board and thats what your stuck with.
Posted on Nov 03, 2009
I have installed honeywell aquastat relay per instruction manual on my dunkirk xeb-4 lp boiler furance with honeywwell ignition unit s8610u but it wont ever start the exhaust fan checked everything several...
If aquastat wirings are ok, and control module had been set up properly, the the furnace should start.
Check if bypassing the control the furnace starts, if it starts then check aquastat wirings.
If it depends on the furnace, check the valve, the safety sensor and the ignitor.
Here is the guide to set up the Aquastat control:
Guide to Setting & Wiring Heating System Boiler Aquastat Controls
Sep 13, 2008 | Honeywell Heating & Cooling
I have a Weil mcLain Gold gas furnace and the Amtrol WH-7L hot water maker. I heat alot with an indoor woodstove and if the furnace is not being used I cannot get any hot water. However, when the furnace...
You should download & review the manual for Amtrol Boilermate products here.
Page 12 of the manual begins examples of wiring between the Boilermate and aquastat (also gas valve and multi-zone relay), that is usually mounted on the boiler. In order to use it correctly, you'll need to determine which aquastat (or other device) your furnace has. You should be able to locate this info on the inside of the aquastat cover. The Honeywell Triple Acting aquastat is very common and looks like this:
The cover is held by a single screw on the top, bottom or front (depending on the model you have). The inside should have wiring information along with the model number. Compare the model number with the wiring diagram for it in the Boilermate manual.
Make sure power is OFF before continuing.
Check that all wires are terminated and undamaged. Make sure terminal screws are not loose. Tighten any found to be loose.
The orange wires are connected to a switch that is normally OPEN but CLOSES to start the boiler when the hot water has cooled. It is also used to operate a "power vent" for a minute or two both before ignition and after flame out for safe pre and post purging of the combustion chamber of furnaces that lack a chimney.
Blue wires are connected to a switch that is also normally OPEN but CLOSES to start the boiler when the hot water has cooled. When the switch connected to these wires is CLOSED, ignition happens instantly. There is no delay for purge so when these wires are used to start a furnace, it should be one with a chimney - not a power vent.
For additional help with your particular installation, you will need to provide information concerning the wiring diagram in the manual that applies. Otherwise, there are simply too many variations to walk through.
I suspect that the switch(es) that are connected to the orange (or blue) wires - or the device (aquastat or multi-zone relay box) is not operating as expected to start the furnace.
The troubleshooting section of the manual that seems to apply best is the section: Boiler will not operate when calling for hot water on page 27 (if you want to try some of their suggestions while waiting for additional replies).
I hope this helps..
Nov 29, 2012 | Heating & Cooling
Solid fuel stove linked to oilsystem with two zone
Put a temperature operated control (aquastat) on the piping of the wood stove so that if it is on, it will interupt the circuit wired to the oil burner at the X&X terminals of the boiler control.As the wood stove cools off, it will close the connection allowing the oil system to fire.
Mar 04, 2010 | Honeywell Electronic Programmable...
Looking for simple wiring diagram to wire ******** aquastat
What are you fanning??? the fire?
Do you have a circulator that circulates when the water is up? Many controls have a AUX connection ... wire the AUX to your fan --- alaternatively, wire directly fron your circulator connection to the fan.
I hope I understood your question ...
Let me know what happens.
a
Oct 16, 2009 | Honeywell International Honeywell&...
How do i install a zone valve in my hot water heater. I need the schematic from boiler controller to the valve. if I tie the first floor to one valve , the rooms (2) will be on the last section before the...
The two zones have seperate supply and returns, correct? If not zoning will not be possible without piping the system in that way. Assuming the piping is correct, for two zones, you will need two zone valves, one cut into each zone. The wiring will vary, but for a 3 wire zone valve, (Taco), power from the transfomer goes through the thermostat, into terminal 1 on the Zone Valve, Terminal 2 on the zone valve goes back to the transformer, (24v common), and also to one "T" terminal on the aquastat (boiler control), and Terminal 3 on the zone valve goes to the other "T" terminal on the aquastat.
For a Honeywell, or other motorized Zone Valve, power again goes from the transformer, through the thermostat and into one side of the motor contacts/wires (depending on brand), the other motor wire goes back to the transformer, (24v common) Then the two end switch contact/wires go back to the T T terminals on the aquastat.
If you are using motorized zone valves, and only 2 of them, the transformer in the aquastat will be strong enough to power them.
Hope this helps
Jul 04, 2009 | Kenmore 75944 Gas Dryer
I want to increase the boiler temp by using the your aquastat
Warning! Can cause electrical shock! Here is the instruction manual
for L7248c
http://customer.honeywell.com/techlit/pdf/PackedLit/68-0281.pdf
Jan 12, 2009 | Water Heaters
Heating & Cooling Logo
111 people viewed this question
Top Honeywell Heating & Cooling Experts
Bill Long
Paul Carew
vance jones
Are you a Honeywell Heating and Cooling Expert? Answer questions, earn points and help others