The suction line temp is 90 to 95 and drops down to about 68 on a residential unit checked the evap. it wasn't dirty flushed drain line wanted to know what could possibly be causing such a thing
    Problem Solver:
  • 7 Answers
Check the Liquid line drier. Make sure the temperature on either side of the drier is the SAME.
If there is no drier, and there is an expansion valve installed in the air handler, then it might be "hunting" or have some trash or non-condensibles in the lines. The Liquid line must be in the low to mid 200psi range. Is the condensor coil clean? It must be.
Also is the filter new and not too restirctive? Don't use one of those 3 month filters. Think about this, if it is so good, and lasts 3 months, then each month, it gets loaded more and more. Imagine the particulates collected over a 3 month period!
Hope this helps.
God Bless.
Erik
Posted on Aug 08, 2008
Why is suction and discharge lines of Goodman WMC24-1A split ac system freezing up.?
Low on freon, dirty evap, dirty filter or maybe restricted at the metering device
Jul 20, 2014 | Goodman Heating & Cooling
Freezes up not cooling like it should
Have you changed your filter? It could be a dirty evap coil. is your fan on the inside unit turning and turning in the right direction. If you have a filter dryer check to see if you have a temp drop across the filter dryer this will be found on the liquid line on the out side. It could also be low on charge of freon.
Its hard to tell you without seeing the unit. But I hope this helps. Let the unit thaw before you do anything. I would take off the evap cover on the inside unit this is the cover where your copper lines ar coming out and thaw this out by letting your indoor fan run. Then I would check to see how dirty this coil is.
Aug 02, 2011 | Heating & Cooling
TRIED TO GET SUPPER HEAT MEASSURMENT AFTER THAWING OUT THE EVAP. OUT SIDE TEMP WAS 95 THE SUCTION LINE TEMP 77 AND THE SUCTION PRESSURE WAS 42 AT THE GAUAGE. BUT THE SUCTION PRESSURE WOULD DROP PRESSURE...
You have to let the system run for a while for the suction pressure to stabilize, if the metering device is a TXV pressure will rise and fall as the valve opens and closes. If this is R22 you need to get the suction pressure up
Jun 23, 2011 | Heating & Cooling
1.5 ton straight cool condenser....head pressure good at 250 psig....suction pressure will not go higher than 55 psig....target superheat indicates target suction pressure at 68 psig....o/d coil clean,...
Hello take a evap coil split (return temp vs supply temp) 18*F would be great.If it is lousy the TXV valve is restricting the flow of freon or the filter drier is clogging.Adding freon will overcharge the system and the suction will NOT improve.
Sep 08, 2010 | Heating & Cooling
UNIT IS ONLY 4 YEARS OLD AND IS ON ITS SECOND COMPRESSOR SUCTION PRESSURE SLOW ABOUT GOING DOWN AND DISCHARGE PRESSURE GOES TO 210 THEN WILL DROP TO 200 .UNIT HAS 10 DEGREES SUBCOOLING BUT SUPERHEAT IS...
Hi, sounds as though for this to be its 2nd compressor for such a newer unit, the superheat was not right when the compressor was installed. I don't know what freon you are using the new R-410A or the regular R-22. There's a big difference in pressure, but now I see your pressure reading and its R-22 for these readings.For a 2 ton unit, you would use the superheat charging method for a unit that doesn't use a thermostatic expansion valve ( T X V ) and not the sub-cooling. A 23 degree super heat at that outdoor ambient temperature is way to high for that unit, you will loose the compressor again!!. Super heat killed the compressor is the saying and that's a fact. Suction pressure should pull down just as quick as the head pressure unless the valves are going and weak, or you have a scroll compressor that has a valve plate that is going, or you are low on charge. With a ambient of 95*, you should be at around 270p.s.i. on your head pressure as 210 to 200 is way low. Suction line temp should be around 68 to 70, with a suction line temperature of 50 to 51 degrees, which would give you a 10 to 12 degree F super heat. I don't know when the second compressor was installed, but it has to be low on charge to be such a low head, and high super heat and you will loose this compressor again, its only a matter of time before you have a burnout. It was either under charged when installed, or has a very small leak at one of the joints. I hope the liquid line drier was replaced also. It shows me you have some knowledge on a/c operation, so you need to get that superheat down to between 8 and 10 degrees for this unit to cool properly, and leak check it also. Did you buy a extended compressor warranty? Lets get the head pressure up and superheat down and you should be OK unless the valves or valve plate is weak. Once you loose the valves, you will have a lower than normal head pressure and a high suction pressure. Compressor just won't pull down anymore. I hope I have been of help to you and ask of you to be kind when rating me. I will be here for you if and when you need me for anything.
Sincerely,
Shastalaker7
A/C & Heating Contractor
Jul 02, 2010 | Weather King 10AJA6001AH Air Conditioner
What happens when the pipe freezes?
low freon charge or your inside evap coils are dirty,,,check yourevap filter and replace if its dirty..also check your evaporater coils to see if its dirty,,,,,,,if its dirty you will need to flush and clean it...with coil cleaner and water......if all is clean and evap has good air flow..........your freon charge might be low......check your pressures hi and low.........hi side should be around 220 to 250 psi and low side should be 68 to 74 depends on the outdoor temp and indoor temps............have a certified hvac tech check the pressures.............
high side line is the small copper line
low side line is the bigger copper line............
a feedback would be good if this helps anyone...
Apr 17, 2010 | Weather King 10AJA6001AH Air Conditioner
Have goodman unit, ac unit running 55 suction, 210 high side. cleaned condenser coils and charge to 10 degrees supercool. suction at 65, discharge 245, why did my discharge go so high
You should have liquid line filter/dryer that maybe restricted or there is a restriction in the orfice inside the evap coil normal operating pressures are 68/ 180
Oct 07, 2008 | Goodman Heating & Cooling
Extremely high head and suction pressures
disconnect the blower and turn on the ac.see if the coil frosts evenly.when you had the system open,you should have changed the liquid line drier.
Jul 29, 2008 | Heating & Cooling
Heating & Cooling Logo
181 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen