Question about Intertherm Heating & Cooling
Intertherm heat pump: outside coils are frozen and it is 98 degrees outside. also, inside is not cooling.
  • 182 Answers
Check your filter....if its ok you are prolly low on freon
Posted on Aug 06, 2008
How do I maximize heat from the 14k ac/heat pump?
Heat pumps are designed to operate only with the heat strip if the outdoor temp drops below 50 to 53 degrees F. Heat pumps use the heat from the outside and transfer it to the inside, but if the temps outdoors do not hold enough heat, it ceases to function efficiently. Make sure the unit is always clean on the inside and on the outside coiling to make it as efficient as possible. I've been in the business for 17 years and around it my whole life and I've never recommended a heat pump for this very reason. They are only efficient in areas where the winter temps are more mild.
Jan 21, 2017 | Heating & Cooling
Ac unit keeps freezing up
what a heat pump is designed to do is reverse the evaporator inside coil and condensor outside coil. it trys to pick up heat from outside and transfer it inside. they work fairly well down to about 40 degrees ambient then not so good. that is why you have auxillary heat i.e. 15 kw. when it was shaking as you saw the compressor is trying to pump liquid instad of vapor as it's designed to. you either have a control issue or it's overcharged.
Feb 03, 2014 | Goodman Heating & Cooling
My heat pump is frozen up today and it is 60 degrees outside and I have my heat set to 66 degrees. Is this normal?
You post is not clear as to where the freeze-up is occurring. I'm going to assume the outdoor unit is frozen up.
Heat Pumps don't generally freeze up at 60 degrees. If the ice around the unit has an uneven pattern (for example a thick spot around the center or at the very bottom) could indicate a low refrigerant charge. If the ice is even throughout, it may be one of the following:
*Sticking Contactor*.....turn the system off at your thermostat and check to make sure the unit outside shut off. If it doesn't turn off, it is likely to be the contactor.
*Failed Defrost Thermostat*.....if the defrost thermostat fails "open", the system will never go into defrost.
*Failed Defrost Control Board*......this could also prevent the system from going into defrost
*Failed Reversing Valve*........put your system in COOL mode and check to see if it will blow cold air inside approx 16 - 22 degF lower than room temperature.
*Failed/Failing Condensor Fan Motor*.......ensure the condenser fan motor is running during heat and cool modes. The condensor fan motor will not run in OFF/Satisfied Mode or in Defrost Mode.
I hope this helps. Good Luck! :-)
Mar 05, 2010 | Heating & Cooling
Intertherm not cooling correctly
Sound like air flow problem to me, the inside and the outside. check the inside filter to see if it's clean and clean the outside condenser coils by washing it.
Aug 23, 2008 | Intertherm P3RA-048K Air Conditioner
Heat Pump
Your inside cooling coil in the air conditioning mode could be frozen over. Change the fan setting to on and operate it that way when in the cooling mode. Turn the air conditioning OFF with the fan ON to clear the coil of frost which should take about 1 hour.
The fact that you have sweat on the large line means that the temperature of the gas inside the line is below the due point of the moisture in the air. A good tech would measure the pressures and temperature of the system to get what is called superheat to determine proper system charge of refrigerant.
Jun 14, 2008 | Heating & Cooling
Amana heat/air conditioning pump
You are going to have to increase the amount of heat absorbed by the evaporator coil on the indoor section of your system. First change the filter. Second turn the power off to the outdoor section and leave the indoor fan running until all the ice on the evaporator coil has thawed this could take a few hours. Third you need to verify that you are getting adequate airflow across the indoor evaporator coil and the outdoor condenser coil both fans should be spinning at full speed and airflow should be unobstructed by dirty coil fins or debris Hopefully after you've done this you will have cold air blowing inside and the larger of the two lines entering the unit outside will be cool to the touch but not frozen or even frosted regardless of run time and the small one should be the slightly warm but not hot. If the larger line continues to freeze then it could indicate a number of problems but essentially your condensers cooling capacity is outrunning your evaporator coils ability to absorb heat from air stream circulating in your home.Hope it works out for you GL!
Jun 10, 2008 | Amana PTH123B25AJ Heat Pump Air...
We installed a 4 ton downflow coleman air handler with evap coil Model number 1854s2m we did not change out the outside unit. the outside unit is a 13 year old 3 1/2 ton intertherm condenser the system is...
you have a missmatched system, for it to work try removing the orfice on the high side txv it is not allowing the evaperator coil to fill with refrigerant properly coleman and intertherm dont like each other since they control a large market in the manufactured housing heating and cooling units electricaly connecting the componets together no issue prefromance sometimes is the issue hope this helps
May 06, 2008 | Heating & Cooling
FIRST YOUR OUTSIDE UNIT PROVIDES HEAT BY USING A REVERSING VALVE TO CHANGE THE REFRIGERANT FLOW.THERE IS NO HEAT STRIPS OUTSIDE SECOND YOUR EMERGENCY HEAT TURNS ON ELECTRIC ELEMENTS INSIDE YOUR AIRHANDLER UNIT.IT SOUNDS LIKE SOMEONE HAS WIRED YOUR UNIT WRONG OR HAS THE THERMOSTAT SET IMPROPERLY.WHEN THE HEAT PUMP CANNOT SATTISFY THE SETPOINT THE THERMOSTAT IS SUPPOSED TO TURN ON YOUR ELEC. HEAT UNTILL THE LOAD HAS BEEN REACHED AND THE HEAT PUMP CAN CONTINUE TO MAINTAIN IT.
Nov 28, 2007 | Heating & Cooling