I have a Goodman GMS9 Furnace that ignites and runs perfect for about 5minutes and then I will here a woosh of air and the flame goes out and inducer motor stops for about 3 seconds, then it re-lites and runs good for about 30seconds and kicks backoff, then relites again and runs for 30secs and so on..... I had a HVAC person look at it and he cleaned the flame sensor, blew out the exhaust and intake tubes, checked the condensate trap, and changed the pressure switch thinking that would fix it. It is still doing the same thing?
  • 27 Answers
This is a common problem with this brand and can even often fool HVAC contractors! There is a control module/circuit board inside the furnace that needs to be replaced for proper operation. The circuit board controls multiple functions and switches and relays inside the equipment and it begins developing a mind of it's own and starts turning certain things on and off at improper sequences. Most of Goodmans furnaces come with a 10 year parts warranty, so try exhausting that resource first before buying one.
Hope this helps James
Posted on Apr 06, 2011
Induction motor runs/no ignition/red light on
If inducer run and igniter is not come on. 1) check igniter for any damage. 2) check pressure switch to make it close as soon as the inducer run. if it not close check the small tube that connect to it for any restriction( mostly inside the inducer compartment) clear it and restart the unit.
Feb 22, 2015 | Goodman Manufacturing Goodman GMS81005CN...
I have a Goodman GMS9 furnace. When the furnace starts the induction fan runs for about 15 seconds, the ignitor turns on but thats as far as it goes. The burners do not light and I don't think the gas...
The igniter heats a thermocouple to turn on the gas valve. From your description, the thermocouple may have failed. The noisy stack blower probably needs to be replaced but its controller may be in need of replacement as well.
Nov 01, 2013 | Goodman GMS90703BXA Heater
Goodman furnace-inducer motor comes on then igniter turns on then gas comes on and then flame comes on then flame goes out, it semms like a draft issue. Then it starts all over again. Any ideas?
Check air filter is clean , see if flame sencor is clean , jump ou tpressure switch and see if it lights, some times you can fool it in to lighting , it sounds like its the pressure witch
Nov 17, 2011 | Heating & Cooling
Good morninng, My Goodman furnace inducer stops and starts at various intervals. At times it runs fine but starts the same issue. Everything starts up accordingly, runs and then the inducer stops for...
Replacing the board, flame sensor, and pressure switch, and cleaning out the induction motor was definitely a good start. Other things to check would be a blocked or restricted flue pipe, I have ran into a few bird nest before!, and you also want to check or replace the hose that runs from the inducer to the pressure switch if you haven't already. To be honest, most of the time I clear out the nipple on the inducer where the hose goes with a small piece of wire and it works. The last thing I would suggest is making sure the new pressure switch is rated for what you need. Alot of the revisions on furnaces actually call for less than the original pressure just for this problem. Hope this helps and good luck!
Feb 15, 2011 | Goodman GMS90703BXA Heater
Our furnace keeps shutting down soon after burner ignites inducer motor stays running wont heat until reset switch behind inducer motor is pushed
Sometimes a "Flame Sensor" gets carboned up and does not detect that the furnace has ignited, so it shuts down the fuel source. Might try cleaning that if so equipped.
Dec 05, 2010 | Goodman GPG152407041 15 SEER Packaged...
My goodman furnace keeps lighting for about 10 seconds than goes out lots of clicking sounds
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad igniter what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat.
2. Draft inducer motor starts.
3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes.
4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas.
Solution: You probably need to purchase and install a new igniter. I would suggest that you inspect your igniter closely for cracks. Make sure you do not touch the igniter with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, roll-out switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
NATE, NCCER, PHCC,HVAC Certified Instructor
Oct 25, 2010 | Heating & Cooling
I have a goodman furnace model#GMT045-3A. when I turn it on the electronic pilot works fine and the furnace will start and run about 30-45seconds then shut off. I followed the insructions for restart but...
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Jan 26, 2010 | Goodman Heating & Cooling
Furnace won't stay running
1 FLASH
Furnace fails to operate.
• Integrated control module
diagnostic LED is
flashing ONE (1) flash.
• Furnace lockout due
to an excessive
number of ignition
“retries” (3 total)1.
• Failure to establish flame.
Cause may be no gas to
burners, front cover
pressure switch stuck open,
bad igniter or igniter
alignment, improper orifices,
or coated/oxidized or
improperly connected flame
sensor.
• Loss of flame after establishment.
Cause may be
interrupted gas supply, lazy
burner flames (improper gas
pressure or restriction in flue
and/or combustion air
piping), front cover pressure
switch opening, or improper
induced draft blower
performance.
• Locate and correct gas
interruption.
• Check front cover
pressure switch
operation (hose, wiring,
contact operation).
Correct if necessary.
• Replace or realign
igniter.
• Check flame sense
signal. Sand sensor if
coated and/or oxidized.
• Check flue piping for
blockage, proper
length, elbows, and
termination.
• Verify proper induced
draft blower performance.
Nov 23, 2008 | Goodman GMS90703BXA Heater
Ignition failure after three attempts then sits for an hour.
try cleaning the burners and or adjust the distance the igniter is from the actual burner .
Oct 01, 2008 | Goodman GDS80904BNA Open Flame Heater
Goodman GMS90703BXA Heater Logo
133 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
paulcarew
Brandon Berry
Brandon Berry
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others