Question about APC Symmetra PX Power Module
We have a symmetra px , the ups showed failure of 10KW power module. We removed the failed module and tried to install a working module , the ups does not even sense the power module , fan in the power module does not turn on, nothing happen , it is just dead. what can be the problem ????
  • 42 Answers
Fuse blown on input. Check Fuse - confirm?
Posted on Feb 16, 2015
    Sergeant:
  • 318 Answers
Bridge failure
replace
Posted on Jun 26, 2011
Self test failed
This could mean that you have bad batteries in the UPS. Usually when it does this test its to test the batteries. So the UPS will start a battery test, Rectifier will lower it's voltage to a set point where the UPS tell it self to go on battery. If the UPS detects that, the battery % is lower than the allow set point to perform the the self test it will stop the test immediately. This way your load is not interrupted. Also could be that the intelligent modules or power modules have a issue which again the set point is to low or out of range due to the total of load the ups has on the output compared to the total power modules that might have a problem with. The UPS is smart enough to stop its test and sends a alarm to notify you. Hope this helps. Get the manual and go into the ups and do a diagnostics on the UPS, this should identify if you have bad batteries or power modules are bad. Doing a diagnostics should not drop the load.
Jan 17, 2014 | APC Symmetra PX SY64K160H UPS System
Apc symmetra px stuck on self test
Place UPS into internal Bypass (Static Bypass) via the display. Then place unit back to Normal from Internal Bypass(Static Bypass). See if that helps. Or shut the unit down completely by placing UPS into Static Bypass first and then place UPS into external bypass mode, switch is located on the bottom front of the UPS. Please follow the UPS Manual to help you understand the procedures. Also recommend doing this after hours, not during business hours.
Jan 15, 2014 | APC Symmetra PX (SYCF80KF) UPS System
Kindly recommend ups for 15kw load
I would get a APC Symmetra LX for single phase of Symmetra PX for 3 phase
Sep 21, 2013 | Computers & Internet
I have an Symmetra RM APC and there is an amber light showing and a beeping about every 30 seconds.
Hi Ewiesemann,
The amber light on the UPS usually means that the unit is 'on battery' -- meaning that input power is affected. Check to make sure that unit is plugged in and check to make sure that a breaker on a panel feeding the UPS power hasn't tripped.
Hope this helps.
Jul 28, 2011 | APC - UPS - Matix/Symmetra Enterprise UPS...
Our UPS is a symmetra Lx16000 which has 4 batteries one of which the diagnostic shows needs to be replaced immediately and the three show as bad. Is it possible replacing the one will solve the problem...
I would at least replace one battery module. There could be alot more going on there. Please call me at Gruber Power Services 800-658-5883 x256 and ask for Eric. I will give you all the free tech. support that you need.
Jul 21, 2011 | APC Symmetra Tune-UPS technical support -...
Not powering up
hold the power button for 25 secs
open the cover and ckeck the battery pack fuse
May 11, 2011 | APC Symmetra PX Power Module
I Have an 80KVA APC Symmetra PX and one of the power module is not working I already change position with other power module and still not working
Hello
Please clarify. If you change the suspected module position and the module is not working, then the problem is with the module. If you replaced a working module in the non working module position and it does not work then there is a problem with this particular slot. Normally you would replace the faulty module with a working one in its slot and things would be clearer. I do not understand well the way you describe the problem, however each module has a micro-switch on the side which activate the start up of the module. have a look at it. i hope this will help
May 09, 2011 | APC Symmetra 12kVA Basic System...
We get power module failure signal. however, when we check the status of that power modules , it say off and ok. what does it mean????
You may have a bad power module somewhere in that unit but not that one... and you will need to turn it on -- rotate the chrome knob on the right of the power module in order to turn it on. It should say 'ON AND OK' or 'ON, FAULT'.
Let me know what happens.
If you need UPS, Surge, or Power Related help contact:
Daniel with Power & Systems Innovations 800.260.2259 or go to our website: http://psihq.com/
•• If this helped - click YES :) ••
Apr 06, 2011 | APC Symmetra PX Power Module
Symmetra LX16000,5.93kva; Problem;Alarm indicating power module fault.
Hi Akortic,
Without knowing the full model number of your UPS I cannot go into specific details fully for you.. but a good test with any 'power module fault' is to re-seat the module and run a self test. This only applies if you have an extra/redundant power module to support the load. If the fault remains then you have a bad power module and you will need to replace it as soon as possible. This can all be done 'on-line' and you should not have any downtime... assuming there is a redundant power module in the UPS. This will clear the fault.
If you would like more information give me a call: 407.380.9200.