Question about Goodman Heating & Cooling
I have a GMP075-3 Rev B. The Thermostat calls for heat, inducer motor comes and the ignitor never lights? The inducer motor continues to run until you shut off the main power supply switch on the wall. The Control Board Blinks 4 times. The info on the back of the removable door discribes a Limit switch problem. The circut layout shows a Limit Switch and Aux. Limit. Should I try to jumb across these switches to see if this corrects the problem? Do these Limit switches have a reset button? Can these switches be purchased at a supply house locally here in Denver?
  • 2 more comments
  • scjellis Apr 05, 2011
    Thanks, Where should I look for this switch? Will it be on the circut board? Should I trace it using the circut layout on the back of the front panel board? Aux or Limit switch or both? Thanks again for the much needed help!
  • scjellis Apr 06, 2011
    It was the limit switch! We are warm again, thanks to your wisdom!
    Thanks a bunch Heatman 101
    Excellent help. A little guidance can go a long way to help the little guy's. Thanks.
  • Goodman Master
  • 43,501 Answers
Yes you have a limit switch problem and most do have a reset button.
There will be a little red button between the wires that you will have to push in to reset it.
If the switc h keep skicking then find out why it is doing that. It have have kicked because of a power failure though...
Those switches also are very common and any Goodman dealer near you will have the part...there should be no problem finding a dealer in the denver area.
heatman101
Posted on Apr 05, 2011
  • D. Floyd Kolb
    D. Floyd Kolb Apr 05, 2011
    The limit switches will be separate from the circuit board....you can find them by following the wiring on the back of the panel...
    The one that probably needs reset is the Aux. limit....
    It could be that the regular high limit is stuck open also...
    heatman101
  • D. Floyd Kolb
    D. Floyd Kolb Apr 06, 2011
    You very welcome!!!
    Please accept my answer... your feedback is much appreciated!!
My heater isn't blowing any heat. I hear the fan come in, and i think i hear the gas come on, but nothing comes out of the vents. The fan only comes on for a couple of minutes and then goes off.
Ok so here is a sequence of the heater lighting and the solution for your problem...
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks.Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning. Please see the pictures below to help you identify a flame sensor.
Thanks and I hope this helps. Feedback apprec.
Jan 28, 2011 | Honeywell Electronic Programmable...
I have a ng furnace downstairs that started this a couple of days aga....It comes on like it is suppose to and runs until it shuts off. Once the blower cuts off it stays off for about 1 second and then...
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Dec 06, 2010 | Heating & Cooling
Induction fan motor cycles on and off , with no call for heat
Problem: Your furnace will not ignite the gas to produce heat for your home. When a furnace has a bad ignitor what I see most of the time is the following sequence of operation:
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution: You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks. Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning.
Nov 26, 2010 | Heating & Cooling
Goodman GS9 propane furnace inducer motor runs continuously
it sounds like the low temp limit switch, the one that cools the furnace down with the burner off and the thermostat open, when it cools to a point the fan stops, the other switch in burner area turns burner off/on, hope this helps
Jan 31, 2010 | Goodman GMS90703BXA Heater
HEIL 80% furnace T-STAT calls for heat, Inducer runs and nothing else happens, Ohm meter reads 4.9 on ignitor. MDL#NTGM100EHA2....Any help with this?
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Nov 03, 2009 | Heating & Cooling
My problem is with the central heat. The thermostat will click, but the heater doesnt come on. What will cause that?
On a call for heat, the 24 volt thermostat2.gif sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the ignitor does not energize (bad control, bad ignitor), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not lite (dirty pilot), the burner does not lite (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Most newer furnaces will have a diagnostic center or control built into the control module. You may be able to view it as it is running thru a small viewing port. Some models will require the removal of an access panel prior to finding it. On the reverse of the access panel, there will be a diagnostic chart that will aide you in understanding any error code recorded (usually a blinking light).
Oct 18, 2009 | Heating & Cooling
Funace gag goes on than off right away
Oct 18, 2009 | Honeywell Electronic Programmable...
I have a Goodman air heat unit that will not come on.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the ignitor. The ignitor will glow and you will be able to see it if viewed thru the small inspection port. Once the ignitor gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
Jan 27, 2009 | Goodman GMS90703BXA Heater
Janitrol/Goodman GMP075-3 Draft Inducer Fan Won't come on
most forced draft fans are powered by 120 volts . close to the fan is usually a plug that unsnaps. create a call for heat after turning off to clear safetys and see if your getting 120 to fan on initial call for heat. if you are then fan draft motor is bad, usually sold as an entire assembly replace exact as it came out. sequence of operation is..... stat calls for heat via common and white wire to furnace , 24 volts. ......board sences call and sends 120 volts to forced draft ........ motor runs and creates pressure on proofing switch,....... switch closes 24 to board and tells it draft fan is on......... board then energizes ignitor,....... after ignitior glows gas valve is opened and burner lights ........ either ignitor or seperate sensor rod tells board the burner lit........ and a few minutes later the fan comes on and hot air is blown out. if a step is missed or doesn't proof the furnace either trys up to three times to light or locks out. turning off power usually resets safetys and it will resume attempts to lite normally.
Oct 25, 2008 | Heating & Cooling
Heating & Cooling Logo
155 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
paulcarew
Brandon Berry
Brandon Berry
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others