Question about Ruud Heating & Cooling
Iam getting 24 to the board but not to the contactor
  • 182 Answers
Getting 24 from y to c?if not,prolly the tstat.....if so,your wire from the board to the ac is prolly broken.
Posted on Aug 05, 2008
Reset the contactor relay
the contactor does not have a reset button 24 volts will energize a magnet and pull the contactor in you can also manually push in the contactor for testing purposes the airhandler has the transformer which produces 24 volts this power then goes to the tstat then you select a mode which then goes to the contactor you most likely have a blown fuse on the circuit board or simular problem the contactor could have shorted causing this
Jun 27, 2012 | Goodman Heating & Cooling
Butters
Based on your description there should be 2 contactors. One is the contactor that controls power to the welder primary winding, this one should be quite large compared to the other one, the other controls the 24 volt (most common) supply to the wire feed speed control board and gas solenoid. If you do have 2 of these contactors, the 24 volt contactor may supply the control current to the larger contactor..
If blowing out the cabinet has not helped, and at this point it is not likely, the 24 volt contactor should be replaced. If a sealed one is available I would upgrade to that style. The ratings should be embossed on the contactor somewhere, otherwise your control voltage should be 24 volts, use a meter just make sure you are in that range, US, UK and Euro standard share some common specs. You may have a 2 pole or 3 pole type- it depends if the gas solenoid is powered off the same pole as the motor control board, or if it is powered by it's own pole. These would be the "N/O" contacts, and all would have current supplied by the 24 volt supply/control supply. The larger contact coil winding would be on it's own pole. Contacts should be rated at 15 Amps minimum
Replacing both contactors at the same time if so equipped is a cost effective bit of maintanence.
If you have only the single 24 volt contactor, the tip will be live at all times and it will only be the gas and the wire feed control board that would be switched by the contactor.
Again, based on description, I would replace the 24 volt contactor. Contacts should be rated at 15 Amps minimum
I would also just check the gas solenoid with a jumper wire to make sure it opened and closed as it should.
Feb 21, 2012 | Welding Tools
Outside AC unit not coming on but indoor fan is working, replaced the start/run 5/50 capacitor but still didnt fix it, let it set allday while came home tried it and it came on and worked great, but the...
Sounds like you are on the right track. The symptom of the contactor not pulling is your clue to the solution. When you turn the thermostat down lower than the room temperature and the thermostat calls for cooling, the outside unit should start immediately. There are a few exceptions to this but generally this is correct. So if you turn the system to cool and the thermostat is calling for cool then the contactor should pull in immediately. If it does not then check for 24 volts to the contactor. If you have 24 volts to the contactor then the contactor is the problem. If you do not have 24 volt power to the contactor coil then you will have to find where the break in voltage to the contactor is happening.
There are many reasons why you may not be getting 24 volts to the contactor, so check what i stated above before you go any further. Repost if this is the solution or you need further assistance.
Important tip....the yellow wire from the thermostat carries the 24 volt power from the thermostat to the contactor.
Sep 08, 2011 | Intertherm P3RA-036K Air Conditioner
My air conditioner will not run, the fan will not run in auto or in run mode, the compressor will not start. The thermostat clicks on but the air unit does not. this is a Goodman cplj18-1b unit.
Hello, if the outside unit is not running check tje power supply to make sure you are getting 240 volts, also make sure the contactor coil is receiving 24 volts, if you are not getting 24 volts at the contactor then it may be a bad thermostat, control board or the thermostat wiring is loose or perhaps cut somwhere. If you have 24 volts at the contactor and does not energize than replace the contactor coil.
May 12, 2011 | Goodman Heating & Cooling
Our ruud air conditioner will not go on no fan zero checked the breakers etc, what do i do?
Hello, if the outside unit is not running start at the outside disconnect box and verify if you are getting 240 volts, if you are continue to the contactor coil, check for 24 volts at the contactor coil if there is 24 volts and the contactor does not energize then it must be replaced. If you do not have 24 volts then the low voltage ( thermostat) wiring must be checked out for a short circuit, loose wiring, or the thermostat might be bad. Also, you can check for 24 volts at tjebcontrol board between the r and c terminal if no 24 volts then you have a bad transformer.
Apr 28, 2011 | Ruud UAMB Air Conditioner
Heil central a/c will not turn on, model is max performance 14 model # HAC442ACK4. checked circuit breakers
Apr 27, 2011 | Heating & Cooling
Contactor not engaging to start condenser unit . When setting the thermnostat, i hear the click from the unit starting inside the house. Fans start and air starts blowing inside the house, but the...
I would replace the contactor if you are getting 24 volts to the contactor and it isn't engaging therefore the magneto on the contactor is out and the contactor will need replacement. If you don't have 24 volts at the contactor then the transformer that sends the 24 volts is bad and will need replacing
Dave
Mar 11, 2010 | Heating & Cooling
Fan and compressor on outside unit not working.
If you read 24 volts at the contactor and it does not pull in, the contactor is bad. If you do not read 24 volts at the contactor the problem is with the thermostat, thermostat wire or a defrost board and pressure switches if so equipped.
Aug 09, 2009 | Heating & Cooling
The contactor well not pull in.
Also if it where the circuit board that had gone bad. Your furnace would not turn on at all not even the blower motor. You can test them both by looking for 24 volts to the board, and 120 volts per leg of the contactor
May 23, 2009 | Weather King 10AJA3001AH Air Conditioner
Goodman CPB 42 Heat/air packaged unit
did you turn off the air handler when you changed the contactor could have shorted and blown a fuse on the control board. did you get a 24v coil on your contactor. do you have 24v at the contactor when unit is calling. check your wire connections
Jan 31, 2009 | Heating & Cooling
Heating & Cooling Logo
Top Ruud Heating & Cooling Experts
Bill Long
Tim Whalen
Dennis Boxerman
Are you a Ruud Heating and Cooling Expert? Answer questions, earn points and help others