I bought a new universal ac contactor relay to replaced the o.e.m. the new has l1 l2 t1 t2 . the old relay don't say l1 l2 t1 t2 or any indicatio.
  • Roger Jelinek Apr 05, 2011
    L1 L2 are line voltage connections. T1 T2 are thermostat connections. Does this help? If not, let me know. Roger
  • vannolan
    vannolan Oct 18, 2013
    I have 2 Black wires one end Colored wires other end what wire goes wear
    Problem Solver:
  • 5 Answers
The contactor should look alike. Just make sure the same wires are on the same side as the old contactor. Don't worry so much of the l1/t1 and l2/t2
Posted on Apr 05, 2011
I need help figuring out funky thermostat wiring on my 240v baseboard heaters.
sounds like your heater already has 120 going to it at all times. it doesn't heat because it needs 240. therefore your tstat breaks the black, when it calls for heat it closes the black therefore giving your heat the remaining 120 and begins to heat. I would think it would work just with the blacks going to l1 t1 but if l2 t2 needs the jumper you are not doing any harm. who knows what goes on inside your walls but if it ain't broke don't fix it
Oct 30, 2017 | Honeywell Heating & Cooling
I have an old air compressor that I have replaced the motor magstart and pressure switch on the motor is a 220 / 240 volt 5 horsepower motor it also has a low pressure oil cutoff switch does anybody have a...
Control: L1-SS-P-O-OL-OL-M-L2 In series, L1 is line 1, SS is start/stop switch, P is pressure switch, O is oil switch, OL is overload contact, M is magnetic coil (solenoid), L2 is line 2.
The voltage of M must be rated for the control voltage, across the line voltage (240V) or of a control transformer voltage, e.g. 240v/24v. A control voltage would be wired across the line, to L1 and L2.
Power: L1-T1-OL-M1, L2-T2-OL-M2. Line one to Line 1 on contactor, T1 on contactor jumpered to OL (overload heater) and out the overload heater terminal M1 to the motor terminal 1. Same for line 2, Line 2 to L2 on contactor, T2 on contactor jumpered to OL (overload heater) and out the heater overload terminal to M2 motor terminal.
The heater overload relays needs to be chosen by the motor full load current, a chart is given with a motor starter on selecting heater size. If no chart is available, go 115% of the motor FLA (full load amps) to select a heater size. E.G. 25 FLA motor at 115% is 28.75a. Sorry, no schematic available now, draw your own from this info. If using 3 phase, add the third line as duplicating one other line1 or line 2
Mar 10, 2015 | Air Tools & Compressors
Wiring diagram question power from house goes to the 2 top post and ac to the bottom post
assuming you are talking about the 'contactor' you are correct - but be sure the 'top' 2 posts are labeled L1 and L2.
Bottom posts should be labeled T1 and T2
L = Line in
T = load out (compressor/fan motor)
Jun 06, 2011 | Heating & Cooling
Fujitsu AST12LSACW - The green timer light is blinking on the indoor unit. The unit is in cooling mode but the compressor dosent come on and only the indoor fan operates. There is power to the outdoor unit...
Compressor contactor relay struck or relay not activated. Remove L1 and L2 wires and jumper with L1 with T1, L2 with T2 and check now. Be careful. It's only checking. When compressor starts, switch off and replace contactor relay.
Jan 27, 2011 | Refrigerators
How to install 25amp 3 pole relay
There should be 8 screws on the relay L1, L2, L3, T1, T2, T3 and two additional screws either at the top or bottom, or one on each side. The incomming, constant power in from the circuit breaker, should connect to L1, L2 & L3. The power out to the load should connect to T1, T2 & T3. The control wire from the switch or timer you will be using to close the contactor will connect to the remaining two screws. THE MOST IMPORTANT PART IS THAT THE CONTROL VOLTAGE MATCHES THE COIL VOLTAGE OF THE CONTACTOR. They will make 12vac, 12vdc, 24vac, 24vdc, 120v, 240v, 277v, etc. coils for the contactor.
Also keep in mind that when the contactor closes L1 & T1 make contact, L2 & T2, Etc.
Oct 08, 2009 | Eaton ARC FAULT CIRC BREAKER
I NEED TO RECONECT WIRES TO CONTACTER RELAY ON
Power leads L1 and L2 to top terminals of contactor.
Compressor leads T1 and T2 to bottom terminals of contactor
Side terminals get the low voltage leads from transformer.
May 18, 2009 | Continental Heating & Cooling
Carrier A/C units
Double check that the new contactor has the same electrical ratings on it. My guess is that the coil should be 24v while the relay should be able to carry the same amperage at 220v.
First shut off the breaker and disconnect switch for the furnace and outdoor condenser and call a licensed HVAC contractor:)
If you are determined to do it yourself, Then read the schematics first. Be aware, if you mis wire the system you may cause more damage than you have now. Not to mention your personal safety is at risk.
I am basing this on the most common style contactor found in my area.
The main relay side should be labeled. (eg. L1,L2-T1, T2). These should match exactly like the old one. L1 and L2 are the incoming power. T1 and T2 are the power leaving the contactor. All the 220v wires should correspond to one of these four terminals either by screwing them down or fitting the spade connectors together.
Usually the 24v wires will plug onto the coil (near the bottom, left and/or right sides of the contactor) silver spade connectors.
(STEP 1.) Leave all Wires Connected to your Old Contactor.
(STEP 2.) Remove the two mounting screws that hold the Old Contactor to the Air Conditioners casing.
(STEP 3.) Now Install the New Contactor to the old contactors existing location using the Same two Screws.
(STEP 4.) Now take Off one wire at a time from your old Contactor and Install each wire one at a time to the proper location on the new Contactor.
Jun 24, 2008 | Carrier 38CKC042 Air Conditioner
Coleman evcon moblehome ac question
I would replace them to the exact terminals that they used to be on. Technically speaking L1 and L2 stand for Line one and Line two. This would be the incoming power from the breaker or disconnect switch. T1 and T2 are the power leaving the contactor relay.
Jun 17, 2008 | Heating & Cooling
Heating & Cooling Logo
241 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen