Question about Carrier 52PQ307 Wall/Window Air Conditioner
Under the window heat pumps, do they have a reset on the compressor,, I replaced the capasitor , the fan starts but the compressor doesnt?
  • bruced94 Apr 05, 2011
    The over load device sat on the top of the heat punp AC compressor... I have a voltage meter it tells you if you have voltage in the line and I have a contaneuity tester. Their are wirers from the capacitor to the top of the compressor. one to the run the terminal ,one to start terminal and one to common. The common line went to the over load then to the terminal for the common line on the compressor .. one post on the capacitor is for fan. one post for Herm and one post has 3 wires to compressor. the common wire was burned off in side the OL . that line can be made hot so that one is ok but sciece its burned off the OL its not hooked to compressor, it can be jumped to compressor, but i thought that would be unsafe. to test the compressor that way and try to start it.
    Scholar:
  • 133 Answers
The compressor is hermetically sealed. They have overload protection for temperature but it is not manually resettable. Check for proper voltage at the contactor going to the compressor.
Posted on Apr 05, 2011
  • 2 more comments
    Can a weak or failing capacatior cause the compressor to overheat and burn up the over load device? is the compressor cooked too?
  • Roger Jelinek Apr 05, 2011
    The capacitor is probably associated with the fan. Compressors don't normally have one. If it does have one and it went bad, the windings in the compressor would definitely overheat. if the over load over heats too many times, it will burn also. The thermal over load in the compressor should have opened and prevented all this. Where is the over load that burned located? Do you have a meter you can use to test the compressor for a short to ground?
  • Roger Jelinek Apr 06, 2011
    Now that was a description !!!! The overload is not an overload. If it wires in rather than pushing onto the studs of the compressor, it is a "Potential Relay". Its purpose is to engage the start winding for a second to help the compressor start and then remove power from the start winding once the compressor has started. If the compressor is going tight or has been short cycling a lot, that relay will fry. The other type that pushes onto the studs is called a "Current Relay". They both do the same thing but the Potential Relay operates by Voltage differential and the Current Relay by Amperage differential between starting and running of the compressor. From the way its wired, you have an "electrolytic Run Capacitor". They are normally metal and oval or round shaped. If it is not swollen out of shape, there's a good chance its OK. Disconnect the compressor completely and test each terminal to ground. Lets hope it is not grounded. Disconnect the capacitor, short the terminals together to be sure it is dry, (drained of voltage) then attach your ohm meter. One lead to Common and the other to either terminal and watch the numbers. The capacitor should start charging. Reverse the leads and it should start discharging. Test the other side the same way. If it won't charge and discharge from each terminal to its common, replace it as well as the relay. You will need to go to an HVAC supplier or Grainger for the new relay. It is unique to compressors, so most general supply stores won't carry it. Thanks for writing. Roger
  • Roger Jelinek Apr 07, 2011
    Wow! No thumbs for me on this. One would have been too many. I am sorry for misunderstanding. Some of the small (really small) scroll compressors do have a "Klixon" OVER LOAD. The start relay probably doesn't apply to a compressor that small. Both feet are in my mouth for that. Roger
I have a trane XR12 Heat Pump. The cooling fan on the outdoor unit does not run nor does the compressor. The fan motor heats up and hums. I am guessing that the problem is the start capacitor on the fan...
Hello Rich,NO you have a dual capasitor that runs both fan & compressor motors.Shut it down and let it cool off.You need the uf rate numbers & the volt rating of the existing cap (printed on the side)to get EXACT replacement.The wires plug in to the top termanls C, HERM &FAN.Worth fixing good luck.
Jul 29, 2010 | Heating & Cooling
Rheem heat pump,have to keep pushing red reset button for fan
Either the fan motor is going out OR the compressor may need a boost of power from a quick start.
When the compressor gets old, sometimes it requires a little extra power to get it going.
Your unit should be under work warranty if they installed it.
Jan 06, 2010 | Heating & Cooling
On a coleman heat pump DRHS0421CB when the thermostat call for heat the heat pump compressor and fan start for an instant and then they stop and a failure message shows up on the thermostat. This works the...
If both the fan and compressor are going off the problem would be in the low voltage side a safety is opening. Probably low on refrigerant. You need to check refrigerant pressure when the unit is starting, if the pressure drops below 60 psig the low pressure switch will open and shut the compressor and fan off.
You really need to have a service technician check the system out for you.
Nov 22, 2009 | Dehumidifiers
ACE184XD1 will not heat or cool. Fan works fine.
If your fan is working this is a good thing. So we know we have good power to the unit.
Your going to need to remove the cover from the unit, remove several screws to get access.
Make sure power is off and where the compressor is, on top remove the cover where the power connects inside and make sure there is no wires burnt, if all is well, move onto the capacitor.
Its usually the cause of compressor failure. Write down where the wires are located on the capacitor (read the top of capasitor) and take the capacitor to a local appliance supplier and have them test it and if bad then purchase a new one and replace in your unit.
Also make sure to verify no wires are burnt in the unit or melted together, and it never hurts to clean it while you have it out.
Good Luck!
Nov 14, 2009 | Heating & Cooling
Fan runs, cooling and heating do not.
sounds like capasitor blew, or bug or snake or someyhing got into compressor area if outdoor heatpump or unit, could be snails also. if so might have killed compressor or something else electrical
Jun 14, 2009 | Heating & Cooling
Home unit 3 ton won't run
The small capacitor is for the fan motor the other for thecompresor .You can try conecting a booster (or hot start) in paralel to the comp.capacitor .If this doesnt work you have to replace the compresor.
Mar 29, 2009 | Heating & Cooling
Heat Pump hums, clicks and does not come on sometimes
yes the start capasitor starts the fan motor and the contactor pulls together when the t-stat tells it to start and it has a spring in it that gets week , some brands of units have a delay in the outside units board to stop it from starting at the exact same time as the airhandler
Jan 08, 2009 | Heating & Cooling
Intertherm 3 ton ac unit I took the capasitor off to get a new one and forgot how to wire it it is not on the cover three wire fan and compressor three prong 55-5 capasitor help
The 55 terminal is marked "herm" it goes to the start winding of the compressor. The 5 terminal is marked "fan" it goes to a wire from the fan motor. The common terminal goes to one side of the power line...The side that is NOT going directly to the compressor.
Jul 27, 2008 | Intertherm Heating & Cooling
Ge ptac
Hello Tom ,   I'm sure i can help you with this.... I work on these units everyday. unfortuneately im not there to put my hands on it but i will explain as clearly as possible.    The most common problem I tend to find with these units is that the control board  and indoor fan motor tends to go bad in these quite often.  If you put the unit in A/C MODE  and/or Fan mode and set it to high if it will not speed up from low , then your problem could be in a couple different places.   1st.  The bearings in the fan motor could be wearing down ,  2nd  The Control board could be bad  in that its not telling the fan motor to speed up.
And when you tell me that the compressor doesnt run in that mode at any given time..... which the electric heat and heat pump itself works together so that when the load is really tough  that the heat pump doesnt over work and in general saves life on your compressor.
Solution is this.
Take your indoor fan motor off and and drill out the rivits  and it pulls apart easy, and replace the bearings and grease them.
ALIGNMENT OF THE FAN IS A MUST.   doesnt cost much at all the fix this. Just a little time and bearings
Replace the Board in the control box
This my friend will definetly solve your problem.    These problems i see everyday with these same units.
Oct 10, 2007 | GE Zoneline Deluxe Series Cooling &...
Fan not working
some fan motors have a start capasitor, some have a run capasitor and some have both. if you take out the capasitors (normally in the junction box) take note of which wires go where and head to a refrigeration spare parts wholesalers they should be able to give you the right ones then replace them. this shouldnt cost any more than $20 if that doesnt work you will need to replace the motor.
Aug 06, 2007 | Friedrich SL24J30 Air Conditioner
Carrier 52PQ307 Wall/Window Air Conditioner Logo
60 people viewed this question
Top Carrier Heating & Cooling Experts
Dan Webster
Dan Webster
Donni Steen
Bill Long
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others