Unit works great on heat, but when set to cool the temperature display increases when it is actually cooling down. If i unplug the thermostat from the wall for a few minutes and plug it back in, it will sometimes reset itself to the correct temp, which is usually 6 to 10 degrees cooler than the original reading. Display also blinks "cool on" sometimes for several minutes before coming on.
  • 43,501 Answers
I would change the thermostat... it is running the heat anticipator in cooling when it should only run it in heating...
The heat anticipator is like a small heater inside the thermostat that fakes the thermostat into shutting down before the temperature is actually that warm so that the residual heat from the furnace just heats the room to the proper temp.
Pulling it off the wall temporarily fixes it but then it hangs up again later...
The flashing also is very normal....that means that the thermostat is in delay mode.....it will do that to let the pressures equalize in the A/C condenser so that it will start properly...nothing wrong there...
Make sure to mark each wire well before taking the old t-stat off of the wall...also make sure to read the directions and get the new stat set up properly for it to work correctly with your system.
heatman101
Posted on Apr 04, 2011
White-rodgers 1f80-261 thermostat: Set to heat, "flame icon" appears but no heat and no fan. Thermo doesn't click when adjusting temperature. Set to fan,there is no fan.?
There is a 3 amp fuse in the main circuit board. If this fuse is bad ,nothing will work but because of the batteries in the thermostat it will lead you to believe that the unit is working properly,however, it is only showing you what is supposed to be. Replace the fuse and everything will work.
Oct 17, 2015 | Thermostats White Rodgers 1F80-261...
Tip
Air Conditioners Cooling Tips
  • Whole-house fans help cool your home by pulling cool air through the house and exhausting warm air through the attic.
  • Set your thermostat as high as comfortably possible in the summer. The smaller the difference between the indoor and outdoor temperatures, the lower your overall cooling bill will be.
  • Avoid setting your thermostat at a colder setting than normal when you turn on your air conditioner. It will not cool your home any faster and could result in excessive cooling and, therefore, unnecessary expense.
  • Consider using an interior fan in conjunction with your window air conditioner to spread the cooled air more effectively through your home without greatly increasing your power use.
  • Avoid placing lamps or TV sets near your air-conditioning thermostat. The thermostat senses heat from these appliances, which can cause the air conditioner to run longer than necessary.
  • Plant trees or shrubs to shade air conditioning units but not to block the airflow. Place your room air conditioner on the north side of the house. A unit operating in the shade uses as much as 10% less electricity than the same one operating in the sun.
  • on Sep 21, 2010 | Heating & Cooling
    Tip
    Lux Thermostat 500
    The Lux 500 Thermostat is an affordable programmable thermostat that gives you a very easy way to customize your heating and cooling temperatures to your schedule. The programming of this thermostat is easily the simplest that I have found in a programmable t-stat.
    The Lux 500 series thermostats are a great economical way to reduce energy and utility expenses by raising or lowering your temperature settings a the times you set. The installation is so easy that most any DIY’er can install this thermostat. It has an easy to read display and the rotary dial makes the programming very user friendly.
    A few of the other great features of this unit are, a keyboard lockout, and an air filter reminder.
    This thermostat can be used on any 24v AC or 750mV single stage conventional heating/cooling system. Single stage heat pumps without auxiliary heat will also work with this thermostat.
    Here is a summary of the features of this thermostat
    Normal 0 MicrosoftInternetExplorer4 st1\:*{behavior:url(#ieooui) } /* Style Definitions */ table.MsoNormalTable {mso-style-name:"Table Normal"; mso-tstyle-rowband-size:0; mso-tstyle-colband-size:0; mso-style-noshow:yes; mso-style-parent:""; mso-padding-alt:0in 5.4pt 0in 5.4pt; mso-para-margin:0in; mso-para-margin-bottom:.0001pt; mso-pagination:widow-orphan; font-size:10.0pt; font-family:"Times New Roman";}
    • 5 - 2 Day programming
    • 4 Periods per day
    • Large easy-to-read display
    • LUX patented user-friendly Speed Dial®
    • Filter usage monitor and alert
    • Default Energy Star approved program
    • Temporary Temperature Override
    • Temperature Hold
    • Keyboard Lockout
    • Temperature Calibration
    • Swing Settings #1 - #9
    • Fahrenheit or Celsius temperature Scale
    • 12/24 Time Format
    • Low Battery Warning Indicator
    • Mercury Free
    As you can see this thermostat will give you a lot of great features at an affordable price.
    on Jan 16, 2010 | Heating & Cooling
    Ice on the back wall; temperature went from 58 degrees to 34 degrees; had to shut off regrigerator
    hi,
    Wine cabinets work off of cycle defrost, so in order to built frost your temperature sensors are not working properly. I would look for corrosion on or in connections to be the fault or problem. Sensors report information to control unit and thats there only job. Its the control unit that dictates function. Look for corrosion to be the problem, clean connection and seal with RTV when connection a corrected.
    Good Luck
    Sep 10, 2011 | Transtherm Ermitage Wine Cooler
    We have the white and rodgers thermostat model 1F81-261. The problem is that the ac unit will not work. We have reset and changed the batteries and set the point 4 degrees less than the actual room...
    Set System Switch to Cool and lower setpoint below room temperature.
    Verify thermostat and system wires are securely attached.
    Diagonistic: Set System Switch to Cool and lower the setpoint below the room temperature. Within a few seconds the thermostat should make a soft click sound. This sound usually indicates the thermostat is operating properly. If the thermostat does not click, try the reset operation ( . If the thermostat does not click after being reset contact your heating and cooling service person or place of purchase for a replacement. If the thermostat clicks, contact the furnace manufacturer or a service person to verify the heating system is operating correctly.
    Reset the thermostat by pressing , UP,DOWN and TIME at the same time.
    Jun 28, 2010 | White Rodgers White-Rodgers 1F85RF-275...
    Tip
    The Honeywell TH811U1003 thermostat is a universal programmable thermostat that...
    The Honeywell TH811U1003 thermostat is a universal programmable thermostat that gives you electronic control of 24V AC heating and cooling systems. It also has the capability to be used on 750mV heating systems
    One of the best features of this thermostat is it’s big clear backlit display. The current temperature, the set temperature and the time of day are displayed at all times. Simply touching the screen also activates the back light feature.
    This thermostat has a menu programming guide the helps you through the process of setting up your schedule. You are able to select multiple days and customize the thermostat for any kind of unique schedule you may have. This thermostat also let’s you take it off the wall and still be able to program it. This lets you watch TV and program it at the same time.
    There are built in backups that will hold the time for you if the power goes out. This t-stat will also update for daylight savings time. There are HOLD features that allow you to modify your program and hold it and then go back to the original.
    Change reminders that are built in include the air filter, UV light, humidifier service and of course the batteries of the thermostat. The blower of you furnace can also be programmed to run extra to help increase the air quality in your home.
    If you decide you want to know the outdoor temperature you can purchase an additional sensor and then hook it to you thermostat. The outdoor temperature will then be displayed on you thermostat. This feature also gives you the capability of using the sensor to monitor indoor temperatures remotely.
    This thermostat will keep you very comfortable as the variation typically in temperature from set point is less than 1 degree F. The thermostat after a period of time learns the characterizes of the way the house or building heats and cools and then adjusts to get the most efficient operation of the heating or cooling system while maintaining a very close temperature tolerance.
    By changing a few of the parameters in the thermostat this can be can be configured for either single stage conventional heat/cool systems or any single stage heat pump system.
    Specifications of the Honeywell TH8110U1003 Thermostat
    • Description: VisionPRO Touchscreen 7-Day Programmable 1 Heat/1 Cool
    • Conventional and Heat Pump Thermostat
    • Application: Gas, Oil or Electric; Heat Pump; Millivolt
    • Programmability: Universal Programming from 7 Day to Non-Programmable
    • Changeover: Auto or Manual
    • Color: Premier White
    • User Interface: Touchscreen
    • Switch Positions (System): HEAT-OFF-COOL-AUTO
    • Switch Positions (Fan): AUTO-ON
    • Power Method: Battery or Hardwired
    • Terminal Designations: R, RC, C, W (O/B), Y, G, S1, S2
    • Dimensions (in.): 4 9/16 in. high x 6 in. wide x 1 1/4 in. deep
    • Mounting: Horizontal
    • Electrical Ratings: 20 to 30 Vac
    • Frequency: 60 Hz. 50 Hz
    • Setting Temperature Range (F): Heat: 40ª F to 90ª F. Cool: 50ª F to 99ª F
    • Setting Temperature Range (C): Heat: 4.5ª C to 32ª C. Cool: 10ª C to 37ª C
    • Differential Temperature (F): 1ª F
    • Differential Temperature (C): 0.5ª C
    • Stages: Up to 1 Heat/1 Cool
    • Outdoor Sensor: Yes, optional outdoor or indoor remote
    • Remote Sensor: Yes, optional outdoor or indoor remote
    • Sensor Element: Thermistor
    • Currents (Heating): 1.0 A running
    • Currents (Cooling): 1.0 A running
    • Currents (Fan): 0.6A running
    • Operating Humidity Range (% RH): 5 to 90% RH, non-condensing
    • Comments: Selectable to and Heat Only or Cool Only
    • Features: Screen lock
    on Jan 15, 2010 | Hardware & Accessories
    Tip
    Th811u1003
    Normal 0 MicrosoftInternetExplorer4 /* Style Definitions */ table.MsoNormalTable {mso-style-name:"Table Normal"; mso-tstyle-rowband-size:0; mso-tstyle-colband-size:0; mso-style-noshow:yes; mso-style-parent:""; mso-padding-alt:0in 5.4pt 0in 5.4pt; mso-para-margin:0in; mso-para-margin-bottom:.0001pt; mso-pagination:widow-orphan; font-size:10.0pt; font-family:"Times New Roman";} Specifications of the Honeywell TH8110U1003 Thermostat
    on Jan 15, 2010 | Heating & Cooling
    Frigidare window air conditioner with remote control about 3 yrs old. All controls seem to be working except when the energy saver mode is suppose to shut down the unit / the display goes dark but the...
    Hello, I can assist you.
    If the unit is supposed to turn off and it doesn't, it will be necessary to check several things.
    • First, is the unit cooling properly? See the section entitled "The air is cool but doesn't seem cold enough."
    • Next, is the temperature of the room adequately cool? If the room temperature is cold enough try setting the thermostat to a higher temperature. If the unit then seems to work properly leave the thermostat set to the higher temperature.
    • If the unit is cooling properly when it is turned on and the room is not cool enough the problem is probably that the unit is trying to cool an area that is too large for its capacity. Use the following chart to find the appropriate size air conditioner to use:
    AREA TO BE COOLED / CAPACITY (BTU/HR)
    100 to 150 square feet = 5,000
    150 to 250 square feet = 6,000
    250 to 300 square feet = 7,000
    300 to 350 square feet = 8,000
    350 to 400 square feet = 9,000
    400 to 450 square feet = 10,000
    450 to 550 square feet = 12,000
    550 to 700 square feet = 14,000
    700 to 1000 square feet = 18,000
    If the room is heavily shaded, reduce needed capacity by 10%
    If the room receives a lot of direct sun, increase needed capacity by 10%
    Add 600 Btu/Hr for each person in the room if there are more than two people
    If the unit is for a kitchen, increase the capacity by 4,000-6,000 Btu/Hr.
    If the room size is too big for the air conditioner you have two possible choices. Either decrease the room size by shutting some doors or partitioning off an area of the room. Or, increase the BTU of the air conditioner for that room by installing a different air conditioner with a higher BTU rating.
    Aug 02, 2009 | Heating & Cooling
    My appartment does not have cenral AC/heat, it has a GE cooling/heater unit in each room. You can set up low heat or high heat but it continues runing on until you manually stop it when is to hot. Is there...
    the unit runs all the time because of the fan (ventilation motor)-but it is not working on cooling or heating all the time - The ventilation motor pushes the air from the room through the machine and when the termostat is reading that you set it up for cooler air or warm air it will turn on the air conditioning part or the heating part of the machine-it is very good system actually
    Oct 04, 2008 | Heating & Cooling
    Tip
    Becoming more efficient with your heating and cooling
    Here are some ways to become more efficient with your heating and cooling. Obviously you do not have to do them in order but try to complete as many as you can! = )
    · Buy a laser thermometer! You can use this to detect air leaks (or at least areas with “minor” temperature differences) so you know where to put seals
    · Keep blinds shut on hot days and open on cold days----helps reduce temperature extremities
    · If the temperature is can be negated by using a t-shirt or a jacket, use that clothing! You will save temperature control costs and still be able to keep warm or cool
    · Do not use those old lightbulbs on hot days---they make extra heat increasing cooling bills (but you can use them on cold days to help warm your house)
    · Utilize energy star products to increase efficiency comfortably
    · Set your thermostat as low as is comfortable in the winter and as high as is comfortable in the summer.
    · If you are on vacation, turn of that air conditioning/heating! No one will be in the house if everyone is away and it shouldn’t be too uncomfortable to wait like one hour for the house to cool/heat
    · Don’t turn your thermostat up/down just to heat/cool faster---all temperature control changes the house temp at the same rate and if you forget to turn it off, you just wasted some energy there!
    · Don’t block heating/cooling vents so that your rooms can be controlled quickly and so that your air actually gets controlled, not your furniture
    · Check up your air conditioning and heating systems regularly (not once a month but maybe once every year) so that the systems stay running the best they can
    source:
    http://www.savingsnut.com/heatingcooling.html
    on Dec 07, 2009 | Heating & Cooling
    Heating & Cooling Logo
    22 people viewed this question
    Top Heating & Cooling Experts
    Paul Carew
    Dan Webster
    Dan Webster
    Tim Whalen