Using a fluke multi meter how do I find low voltage problem between furnace blower and condenser
  • cocodulce_74 Apr 04, 2011
    Very helpful..thanks a bunch...
    Scholar:
  • 133 Answers
Go to the low voltage terminal board in your furnace. Follow the thermostat wires ti find it. Set your meter above 30 volt A/C. Hook one lead to one side of the transformer. Touch the other to the RED wire on the terminal strip. If you don't read 24 volts, switch terminals on the transformer and touch the red wire again. If OK then touch your lead to the YELLOW wire or the terminal marked Y on the terminal strip with the thermostat set to cool. you should have 24 volt now between the lead on the transformer and the one on the Y terminal. Go to the condensing unit outside and test the 2 18 gauge wires there. the 2 readings should be the same. If you have any trouble with anything, please write me back.
Roger
Posted on Apr 03, 2011
  • cocodulce_74 Apr 03, 2011
    Well after finding a bad 120/24 40va transformer I replaced it and I shud haved fused it but I didn't any ways I hooked up the new one and tryed jsut the fan in the on position and all was ok the fan came on so I put the doors back on when I put the tstat to the cooling there was a small delay when the cooling came on the transformer sparked and smelled burned so I'm fixin to put fused transformer with a built in fuse reset button.sonow I know my problem is between my condenser and my blower what's the easiest way to find the short ground...thanks C.
  • Roger Jelinek Apr 04, 2011
    Sorry I'm late getting back. The fan runs fine so you are probably OK in the furnace. Just be sure the wires from the terminal board in the furnace to the condensing unit are not shorted. With all power off, tie one lead to the furnace cabinet and test all the wires on the terminal board. If any are grounded and its not the transformer common, trace it out. If the "Y" terminal is shorted (Yellow to AC), look at the contactor in the condensing unit. If the contactor LOOKS OK, disconnect the 2 low voltage wires from it and test each separately to the unit cabinet. Test the leads on the contactor last. The contactor is most likely the culprit but its a good idea to test every thing. I'll be back and forth on here for a couple hours. Let me know how its going before tying in the new transformer. Thank you for writing and please grade, OK?
    Roger
Hello, I have an a/c unit that is not turning on. I have tried to shut the breaker off for an hour and still nothing. The furnace blower turns on just the actual a/c unit doesn't kick on.
with a meter verify 24 volts entering the condenser via the tstat wire. if voltage present but still no contactor pulled in you likely are low on refrigerant. you can manually press the contactor in and if the machine then runs it's almost guaranteed it's a refrigerant issue and the machine is of on safety. Keep us posted.
May 03, 2018 | Heating & Cooling
Coleman presidential furnace
bad fan control switch or bad fan motor
Nov 28, 2017 | Coleman Heating & Cooling
Ipod wont charge
first check the charger by using a FLUKE OR SIMILAR multi-meter to check the output voltage, if there is voltage then clean the contacts using an old tooth brush with non corrosive alcohol or methylated spirit
Jul 02, 2014 | Audio Players & Recorders
Hi I have an goodman model capf036a2a furnace and I have replaced the capacitor and blower motor. When I turn on the heat the furnance lights and runs but the blower motor doesent start which trips its...
Verify if you have 120 volts from the control board. Easy way to check is to bypass the board, you can do this by using a small wire and jump the L1 wire with the low speed motor wire, if the motor starts up the board is bad and will need to be replaced. You can also use a meter and check voltage between the low speed motor wire and the Common wire which is typically white in color. If you do not have voltage the board is bad.
Nov 28, 2012 | Heating & Cooling
Electrnic hand growler to test electrical armature with green and red indicator
Go on E-bay for electrical test equipment and look for growler.or go google and type in armature growler test equipment and see what you get.
Sep 05, 2011 | Hand Tools
Weather King Acclaim II gas furnace will kick on but the blower won't work. It will try and run for about 5 minutes and then the furnace shuts down.
Hello, First thing is verify if you are getting voltage to the motor at the low speed motor terminal tat he control board and neutral. if you have voltage, next step is to check the capacitor, Discharge it and use a meter to verify the microfarad rating, if it is too low replace the capacitor. If that checks out good then the motors windings are either open or shorted to ground and must be replaced. If you don't have voltage at the control board then the board must be replaced.
Mar 05, 2011 | Heating & Cooling
No spark
An Ignition system check is required to see if there is voltage going to the Ignition coil. Use a fluke meter or multi meter and check the connector from the coil pack. Or, ohm check each spark plug wire individually and one by one.
Nov 05, 2010 | 1998 Mercury Mountaineer
Have three wires on my air handler blower motor and need to know what order they go in?
Chances are that you have a low speed, high speed, and common lead (wire). One of the three wires should be white, this is your common, or neutral. If you ohm the other two wires, one at a time with the white wire, you can determine which speed is which. The higher the resistance the slower the speed. High speed should go to cool, and low speed should go to heat. Hope this helps.
May 04, 2010 | Fluke Networks Fluke 902 True Rms Hvac...
I have a Carrier 58SX060 Furnace with air. I turned the thermostat to heat and the exhaust comes on and runs and the pilot comes on but the burner never light s and the blower never comes on. If I turn the...
carrier gas furnaces will try to light three times then will usually go on a lockout for one hour you can bypass the lock out by resetting the power, turn furnace on, remove wires from gas valve, you will need a multi meter to check for voltage to valve, if control board sends a call to the gas valve the valve is bad, if voltage is never present during the lighting cycle your control board is bad
Sep 30, 2009 | Heating & Cooling
Heating & Cooling Logo
46 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen